My Nest is showing wiring error. I have no idea. Just moved…

My Nest is showing...

My Nest is showing wiring error.

Contractor's Assistant: How old is the appliance? Have you gotten error messages before?

I have no idea. Just moved in. Apparently it is the Y1 wire. I do not see a Yellow wire though.

Contractor's Assistant: Do you plan on doing the work yourself?

Yes, if I can.

Contractor's Assistant: Anything else we should know to help you best?

What information can I provide for you to tell me how to fix this?

Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 minute by:
3/18/2018
Daniel Plourde
Daniel Plourde, HVAC Technician
Category: HVAC
Satisfied Customers: 451
Experience: I've been in the HVAC buisness since 2008 working on residential, commercial, and industrial buildings
Verified

hi i am dan i can help you with this. first i will need to know what type of system you have and what wires you have connected to the thermostat

Ask Your Own HVAC Question
Customer reply replied 1 month ago
I just moved into this house and there was a Nest installed. There are 4 wires, White, Red, Green and Blue.

ok there are hundreds of different types of systems without knowing what type you have i cannot tell you how the thermostat should be wired or what your possible problem can be. if you do not know what system you have you will have to have a technichian come out to fix the problem.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
how do I proceed?
Customer reply replied 1 month ago
Oh, OK! So, there is nothing I can do at this time?
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,001
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

Hello,

My name is Billy.

I can help you wrap this up if you wish to continue?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
please.

What did not help you is your wiring does not have the "code" wires. You have no yellow...so in the event there is no yellow the blue wire takes it's place.

So red to r

white to w

green to g

blue to y

Can you try this now?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
Thank you! I will try it and let you know in couple of mins.

If the code is missing power to Rh...then we want to check the furnace for power...we can work through that also.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
It is already connect that way. Mine is connected as: Red to Rh, Green to G, White to W1, Blue to Y1. Is this right?

That is correct. if no power is the code we need to move to the furnace if you are ok with that

Ask Your Own HVAC Question
Customer reply replied 1 month ago
I get the code e103.
Customer reply replied 1 month ago
it says there is a problem with the Y1 wire.

Is this a zoned system with more than one thermostat in the home? Or just one furnace and one thermostat?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
Just one furnace and one thermostat.

Thank you.

Now lets go to the furnace...we want to see the same wiring at other end of the thermostat wire. Do you mind removing the furnace doors?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
1min, let me go to the furnace and open it.

thx....any pics you want to post of the wiring is great

Ask Your Own HVAC Question
Customer reply replied 1 month ago
That is the current wiring on Nest.
Customer reply replied 1 month ago
I don't have any tools to open the furnace.
Customer reply replied 1 month ago
OK, I got it open but can't see the wires. What do I do now?
Customer reply replied 1 month ago
It was working yesterday, but today morning it gave me that error. It seems to be working now again, but now sure if that error will pop up again.
Customer reply replied 1 month ago
Now it stopped and getting the same error code.

do you have a condensate pump next to furnace?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
I have no idea what a condensate pump is. I am not very knowledgeable when it comes to furnace or electrical work. But I don't see any device next to the furnace, if that helps.

Ok, how about pics of the furnace with the door off ?

Are you currently in ac mode or heating season?

A ac safety blocked drain switch can do this if the ac drain is slow..

Ask Your Own HVAC Question

excellent pic....now can I see with the door to the right off and any drain pipe you see from the duct,ac,furnace?

Ask Your Own HVAC Question

see here

are heating or cooling recently?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
Cooling.
Customer reply replied 1 month ago
Let me check that area. 1min.

standing by

Ask Your Own HVAC Question

kind of hard to tell in the pic....is there a switch in the pan under ac coil (the safety catch pan) and is there any water present?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
No, I couldn't find a switch (as far as I looked) and there is no water in the pan.

ok, put right hand door back on furnace.

It appears there is no water safety switch (which by code there is 99% of the time).

This safety protects the home from water damage if pipe gets plugged...it stops the Y circuit by opening it and shutting off access to ac. Is there a spare wire in the thermostat wire cable not being used?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
OK, good to know!
All the wires are already connected. 4 wires and all 4 are connected.

Now that you see how the wiring is done...check the blue wire connection and then the wire it connects with in Y.....looks like white wire that runs outside....check all the connections...It is possible the thermostat is to blame but I like ruling out other options.

BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,001
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
BillyHvac and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 1 month ago
I checked all the connections and everything looks like you said it should. Maybe it is the Nest thermostat that is malfunctioning. Thank you so much for your help!
Was this answer helpful?
Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,001
23,001 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a 116B and wondering if the nest thermostat is
Hello, I have a Bryant 116B and wondering if the nest thermostat is compatible? … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,700 satisfied customers
Would like to connect a nest thermostat. the trane
Would like to connect a nest thermostat. the trane thermostat has three wires connected. d=green, r=red, b=blue. any help is good … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,700 satisfied customers
I am troubleshooting a nest thermostat that is blowing
Hi, I am troubleshooting a nest thermostat that is blowing cool/cold air when it's supposed to be heating. Not sure the wires are in the right spot, but not 100% sure... … read more
Bill
Bill
Service Mgr
83 satisfied customers
I'm trying to figure out if I can install a nest thermostat
Hello, I'm trying to figure out if I can install a nest thermostat with my Lenox system … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Replace a carrier edge thermostat with a nest thermostat.
replace a carrier edge thermostat with a nest thermostat. New system and just want a nest … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I'm getting an error on my Nest Thermostat, No Power to RH
I'm getting an error on my Nest Thermostat, No Power to RH wire, E24. The heat will not turn on and now the fan is running and I cannot shut it off. Wondering how to get it to shut off. … read more
Daniel Plourde
Daniel Plourde
HVAC Technician
451 satisfied customers
How do you properly install and configure a Nest thermostat
How do you properly install and configure a Nest thermostat for a dual fuel system?For reference, the current thermostat (Braeburn 2220NC) uses the following wiring terminals: Rc (with jumper to Rh) Y… read more
Bill
Bill
Service Mgr
83 satisfied customers
Nest thermostat is giving error 74, no power to the RH
Nest thermostat is giving error 74, no power to the RH cord... we've done all the troubleshooting suggested by Nest... how can we fix it?… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,001 satisfied customers
My Nest thermostat is giving me e23 error. I believe it is
I believe it is specific to the thermostat because the Nest in another part of the house is operating … read more
Daniel Plourde
Daniel Plourde
HVAC Technician
451 satisfied customers
I have a nest thermostat showing e24 error no power to rh
I have a nest thermostat showing e24 error no power to rh wire in thermostat . I have checked the fuse is good breaker is good. Before that my power wire that connects to th actual a/c burned from con… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I'm trying to install a nest thermostat e. I currently have
I'm trying to install a nest thermostat e. I currently have a honeywell h3z11 and wanted to make sure it was compatible. I installed the nest on the main level and it is currently not working. … read more
Daniel Plourde
Daniel Plourde
HVAC Technician
451 satisfied customers
OB Terminal on Nest Thermostat has gone out twice in the
OB Terminal on Nest Thermostat has gone out twice in the last month. … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My Nest thermostat says no power and no HVAC connected. But
My Nest thermostat says no power and no HVAC connected. But it was all working yesterday … read more
Daniel Plourde
Daniel Plourde
HVAC Technician
451 satisfied customers
We just installed a Nest thermostat. It was working fine,
We just installed a Nest thermostat. It was working fine, but we woke up to smell exhaust and found that the fan is not blowing. We re-checkes the wiring and think it's right, and we looked at the fus… read more
Daniel Plourde
Daniel Plourde
HVAC Technician
451 satisfied customers
Hollo, my nest thermostat stopped work this morning and the
Hollo, I'm Aaron my nest thermostat stopped work this morning and the message reads RH wire not connected. What should I do. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Are you familiar with a NEST thermostat? I have a old
Are you familiar with a NEST thermostat? I have a old Honewell CChromotherm {{{ and want to convert to the NEST … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have a Weil mclain boiler, and a nest thermostat. the
I have a Weil mclain boiler, and a nest thermostat. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a NEST thermostat and for some reason it is not
Hi! I have a NEST thermostat and for some reason it is not turning on our air conditioner. I was trying to figure out if the problem is with the NEST or with the AC. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x