HVAC

Have HVAC questions? Ask an HVAC Expert for answers

Ask an Expert,
Get an Answer ASAP!

I'm getting an error on my Nest Thermostat, No Power to RH…

Customer Question
I'm getting an error...

I'm getting an error on my Nest Thermostat, No Power to RH wire, E24. The heat will not turn on and now the fan is running and I cannot shut it off. Wondering how to get it to shut off.

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

It won't let me go to any settings, just the error tech info. Did not check filters.

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Submitted: 1 month ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 minute by:
3/18/2018
HVAC Technician: Daniel Plourde, HVAC Technician replied 1 month ago
Daniel Plourde
Daniel Plourde, HVAC Technician
Category: HVAC
Satisfied Customers: 451
Experience: I've been in the HVAC buisness since 2008 working on residential, commercial, and industrial buildings
Verified

hi i am dan i can help you with this. is the thermostat newly installed or has it been working and now it has stoped working?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
It has been working for about a year now, and just stopped this morning.
Customer reply replied 1 month ago
I went through the troubleshooting on Nest site, but still not working. I removed the AC wire, but the fan is still running and the thermostat has the same error.
HVAC Technician: Daniel Plourde, HVAC Technician replied 1 month ago

ok if you a voltmeter the next step will be to remove the thermostat from the sub-base and test for voltage at the wires on the wall. then the next step will be to troubleshoot the equipment it is connected to. i would need to know what unit you have and the model number to give you specific instructions.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
No I do not have that. Will I need to call someone out to fix this?
HVAC Technician: Daniel Plourde, HVAC Technician replied 1 month ago

what is the model number of your furnace?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
CK68BXT048021AAAA
HVAC Technician: Daniel Plourde, HVAC Technician replied 1 month ago

what is the brand? is it oil or gas?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
Bryant Gas
HVAC Technician: Daniel Plourde, HVAC Technician replied 1 month ago

that number is ***** a model number for a bryant furnace. it should begin with 2 numbers. since the fan on it is running all the time that means a safety limit in the furnace has tripped. or there is a problem with the thermostat. to rule out the thermostat remove it from the sub base if the fan is still running then the problem is in the furnace.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
310JAV048090ACJA
Customer reply replied 1 month ago
I removed the thermostat, and the fan still stays on. I turned off the furnace at breaker and the fan has shut off
HVAC Technician: Daniel Plourde, HVAC Technician replied 1 month ago

ok the next step will be to remove the front cover of the furnace and then in the lower compartment is a circuit board with an led light. if there is an error that light will be flashing a code. count how many times it flashes fast and slow

Ask Your Own HVAC Question
Customer reply replied 1 month ago
I do not see a light
Customer reply replied 1 month ago
I tried to send a pic but it will not allow. Can I email it to you?
Was this answer helpful?
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,938
6,938 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a 116B and wondering if the nest thermostat is
Hello, I have a Bryant 116B and wondering if the nest thermostat is compatible? … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,712 satisfied customers
Would like to connect a nest thermostat. the trane
Would like to connect a nest thermostat. the trane thermostat has three wires connected. d=green, r=red, b=blue. any help is good … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,712 satisfied customers
I am troubleshooting a nest thermostat that is blowing
Hi, I am troubleshooting a nest thermostat that is blowing cool/cold air when it's supposed to be heating. Not sure the wires are in the right spot, but not 100% sure... … read more
Bill
Bill
Service Mgr
85 satisfied customers
I'm trying to figure out if I can install a nest thermostat
Hello, I'm trying to figure out if I can install a nest thermostat with my Lenox system … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
Replace a carrier edge thermostat with a nest thermostat.
replace a carrier edge thermostat with a nest thermostat. New system and just want a nest … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
How do you properly install and configure a Nest thermostat
How do you properly install and configure a Nest thermostat for a dual fuel system?For reference, the current thermostat (Braeburn 2220NC) uses the following wiring terminals: Rc (with jumper to Rh) Y… read more
Bill
Bill
Service Mgr
85 satisfied customers
Nest thermostat is giving error 74, no power to the RH
Nest thermostat is giving error 74, no power to the RH cord... we've done all the troubleshooting suggested by Nest... how can we fix it?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My Nest thermostat is giving me e23 error. I believe it is
I believe it is specific to the thermostat because the Nest in another part of the house is operating … read more
Daniel Plourde
Daniel Plourde
HVAC Technician
451 satisfied customers
I have a nest thermostat showing e24 error no power to rh
I have a nest thermostat showing e24 error no power to rh wire in thermostat . I have checked the fuse is good breaker is good. Before that my power wire that connects to th actual a/c burned from con… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I'm trying to install a nest thermostat e. I currently have
I'm trying to install a nest thermostat e. I currently have a honeywell h3z11 and wanted to make sure it was compatible. I installed the nest on the main level and it is currently not working. … read more
Daniel Plourde
Daniel Plourde
HVAC Technician
451 satisfied customers
OB Terminal on Nest Thermostat has gone out twice in the
OB Terminal on Nest Thermostat has gone out twice in the last month. … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My Nest thermostat says no power and no HVAC connected. But
My Nest thermostat says no power and no HVAC connected. But it was all working yesterday … read more
Daniel Plourde
Daniel Plourde
HVAC Technician
451 satisfied customers
We just installed a Nest thermostat. It was working fine,
We just installed a Nest thermostat. It was working fine, but we woke up to smell exhaust and found that the fan is not blowing. We re-checkes the wiring and think it's right, and we looked at the fus… read more
Daniel Plourde
Daniel Plourde
HVAC Technician
451 satisfied customers
Hollo, my nest thermostat stopped work this morning and the
Hollo, I'm Aaron my nest thermostat stopped work this morning and the message reads RH wire not connected. What should I do. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Are you familiar with a NEST thermostat? I have a old
Are you familiar with a NEST thermostat? I have a old Honewell CChromotherm {{{ and want to convert to the NEST … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
I. Am trying to install a nest thermostat it is saying to
I. Am trying to install a nest thermostat it is saying to check certain wires it was labeled with 2 letters I was told I had a heat pump is that dual fuel then and if so is it forced air? … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Weil mclain boiler, and a nest thermostat. the
I have a Weil mclain boiler, and a nest thermostat. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a NEST thermostat and for some reason it is not
Hi! I have a NEST thermostat and for some reason it is not turning on our air conditioner. I was trying to figure out if the problem is with the NEST or with the AC. … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x