I have a Carrier 58sxc060 gg hot air furnace and it short…

I have a Carrier...

I have a Carrier 58sxc060 gg hot air furnace and it short cycles and won't satisfy the thermostat I replaced the limit switch it is a little better but still won't satisfy the thermostat if I plug the old limit switch in and not install it just let it hang by the wires it will satisfy thermostat

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

The thermostat works fine like I said if I plug the old limit switch in and don't install it let it dangle by the wires the furnace will satisfy the thermostat I don't have a filter I have a Trion electronic air cleaner

Contractor's Assistant: Do you plan on doing the work yourself?

I have been so far I diagnosed the old limit switch bad because there was 24 volts on one side of the switch and the furnace wouldn't turn on I put a jumper wire across the 2 terminals for a test and the furnace would run so I replaced the limit switch with the same hi & low rating and the furnace runs but won't cycle long enough to satisfy the thermostat it keeps short cycling and won't bring the house up to temperature it is 18 degrees out the thermostat is set at 70 and it is 64 degrees in the house

Contractor's Assistant: Anything else we should know to help you best?

That is it

Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 minutes by:
3/18/2018
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,154
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

hello,

does the Trion have a 1/2" prefilter?

Ask Your Own HVAC Question
Customer reply replied 5 months ago
no

Ok we may have an issue then as most all electronic filters come with a prefilter screen to catch larger particulate. If you leave the bottom door off and the safety switch taped down does it satisfy or short cycle?

Ask Your Own HVAC Question
Customer reply replied 5 months ago
I took the electronic filters out of the Trion and turned it off it does the same thing I don't believe it has anything to do with the Trion air cleaner

That very well could be but I do not see what you do.

The limit trips due to excessive heat.

That means air restriction or too little air from blower.

Have you sped the blower up in heat mode yet?

Ask Your Own HVAC Question
Customer reply replied 5 months ago
When the thermostat calls for heat the blower comes on then shuts off then the inducer motor comes on then the pilot lights shouldn't the furnace continue to run until the thermostat is satisfied as long as the blower is running shouldn't the heat exchanger stay cool enough to continue to run

Yes....IF...

If the blower is at proper speed

There are restrictions

All vents and returns open

Unit set up properly at start up.

Did you see my response about whether you changed blower speed for heat?

Ask Your Own HVAC Question
Customer reply replied 5 months ago
I did not see the response about blower speed that has never been changed

Would you like to change it?

Whether the blower has slowed

or other restriction, the temp is high in the furnace due to airflow ratio.

To get more airflow we find restriction or speed the blower up...which the furnace is capable of.

Ask Your Own HVAC Question
Customer reply replied 5 months ago
if the speed is to fast or to slow what happens I know this is gong to sound stupid but the furnace sounds like it is moving the same amount of air it always has If it was laboring I would hear it why all of a sudden the air flow it was never a problem before

Because it is mechanical...things can change at anytime.

It appears airflow has not changed - yet you are cycling on limit which means overheat.

So regardless of what it sounds like...we are running too hot. The reason of too hot is the ratio of heat vs the air flow has changed.

If you want to fix the cycling issue you will need to increase airflow...providing, as mentioned, there are no filter issues, closed vents, blocked returns etc.

Ask Your Own HVAC Question
Customer reply replied 5 months ago
you say to speed the blower up I have checked all the vents and returns so I know there are 2 or 3 wires or positions to change motor speed how do I speed motor up

on the circuit board...follow the wires from blower motor to where they attach to board.

You see terminals HEAT....COOL.....PARK

Ask Your Own HVAC Question

then tell me what color wire is on HEAT

Ask Your Own HVAC Question
Customer reply replied 5 months ago
I also know where they are plugged in but have never touched them I had compressor replaced and I think it wasn't matched correctly and when it is real hot out it never brings the house down as cool as it did before I was going to speed the motor up but I was told the a coil would freeze so I never did

actually for cooling we want as much air as possible...it is too little air that freezes a coil.

If you see what is on heat we can change...it ships with red wire, which is lowest speed.

Ask Your Own HVAC Question
Customer reply replied 5 months ago
red is on low black is high white is on common

great...do you see a blue and yellow on PARK from blower motor?

Ask Your Own HVAC Question
Customer reply replied 5 months ago
It looks like the motor has been changed there is a junction block marked c1234 on the motor side in the same order is white black yellow blue red on the circuit board side is white c black 1 red 4 then someone wrote with magic marker on the squirell cage white c red 2 black3

so the red wire from HEAT on the circuit board....goes to motor where a 4 pole plug is and the red is currently on 2 and black on 3?

Was the ac put in smaller than prior?

Ask Your Own HVAC Question
Customer reply replied 5 months ago
it wasn't suppose to be smaller but never worked like the carrier unit that was installed with the furnace the red wire coming from the board marked low is currently on 4 and is red from motor black coming from the board is marked high is currently on 1 and is black from motor

move the red to 2 and try system

Ask Your Own HVAC Question
Customer reply replied 5 months ago
motor doesn' run
Customer reply replied 5 months ago
doesn't

then someones has rigged a motor in that was not spec'd for the furnace.

Can you post a pic of the blower motor wires and the plug they go to.

The schematic I have from the unit will no longer pertain

Ask Your Own HVAC Question
Customer reply replied 5 months ago
I can't post a picture I think it is time to bail I will have to call someone to look at the blower motor In the meantime as long as i am at home can I let the blower run to satisfy the theromstat with the old limit switch hooked up and not installed without putting the heat exchanger in danger

No, do not let the limit hang free as that totally circumvents the safety feature and purpose of the limit.

Lets say the limit is keep the furnace less than 220 degrees....we remove it and let the furnace get to 300+...this is not good or safe.

Letting it cycle is a pain, but at least is safe.

I wish you the best

Billy

Ask Your Own HVAC Question
Customer reply replied 5 months ago
how do we end this

you just rate service with a star system visible on your end. Once rated it moves off the active list.

Thank you

BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,154
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
BillyHvac and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,154
23,154 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Our new model Goodman furnace does not reach the set
Our new model Goodman furnace does not reach the set thermostat temp before shutting down. Ex...We have the thermostat set for 70 degrees. The furnace shuts down at 64 degrees with a 4 count diagnosti… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,154 satisfied customers
I have a CARRIER CONDENSING GAS FURNACE MODEL 59SC5A. (new
Hello, I have a CARRIER CONDENSING GAS FURNACE MODEL 59SC5A. (new home 5months old), as of this morning, it will not blow warm air. I have thermostat set at 70 and internal house is currently 64 degre… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
My furnace won't heat the house past 64degrees. Problem
Customer: ***** *****, my furnace won't heat the house past 64degrees. Problem solving I have the thermostat set at 70. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
hello, my furnace runs all the time yet does not get to temp
hello, my furnace runs all the time yet does not get to temp setting. maintaining a constant 64 degrees when set at 70, always running. if i turn it down to 64 it will kick on and off. old unit [ late… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
my weatherking furnace isnt blowing warm air. I already tried
my weatherking furnace isn't blowing warm air. I already tried powercycling it a couple of times. both thermostats are on and set to auto heat. it doesn't appear to have a filter because I see a Trion… read more
Expert
Expert
We have a Honeywell thermostat and last night it started the
We have a Honeywell thermostat and last night it started the heat just fine. But, it won't turn it off. We have it set to "hold" at 64 degrees. The furnace kicked in when temp got down to 64 but it ne… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Hi, We have a 12 yr old Carrier 58PAVNNN-NN-NNNNfurnace that
Hi, We have a 12 yr old Carrier 58PAVNNN-NN-NNNNfurnace that the flame roll out switch keeps buring out. We have had it checked, inspected and serviced and things look okay. That being said it burned … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,154 satisfied customers
I have a high efficiency Ruud furnace. A week ago, it was
I have a high efficiency Ruud furnace. A week ago, it was not maintaing the heat temperature. It was set for 70 and the heat was 66. I called a service guy who replaced a part (Ruud pressure switch) a… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
this is a coleman gas furnace that runs on lpg gas, insalled
this is a coleman gas furnace that runs on lpg gas, insalled new blower unit, but when calling for heat the burner lites but no fan, installed new fan switch and still no fan I jumpered the fan switch… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
I have a Trane XC90 that keeps setting intermittently the Open
I have a Trane XC90 that keeps setting intermittently the "Open High Limit Device" error code (4 Flashes). This furnace is about 10 years old. I have changed the filter and cleaned the evaporator to r… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Gas Furnace SA Series 80+ High Efficiency Upflow/Horizontal. The
I have a Gas Furnace SA Series 80+ High Efficiency Upflow/Horizontal. The furnace was installed during the summer and I don't know if they tested anything more than the furnace kicking on. I have redu… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,154 satisfied customers
payne gas furnace keep cycling flu clean heat exchanger ok
payne gas furnace keep cycling flu clean heat exchanger ok filter clean i jumped high limit switch and seem to corect the problem i replaced high limit switch and furnace is cyling i checked the motor… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,154 satisfied customers
I have a Lennox warm air furnace Model 61MPV-60C with matching
I have a Lennox warm air furnace Model 61MPV-60C with matching evaporator coil, and media air cleaner model PMAC-12C. It is connected to a Lennox 49M55, or 49M56, or 49M57 programmable thermostat.It w… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
Ive had issues the past few years of the firebox getting too
I've had issues the past few years of the firebox getting too hot causing very short cycles. The furnace could not run long enough to heat the house to the desired temperature of 70 degrees. The heat … read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Good Morning - I have a Carrier Furnace Model 58CTA090---13114 My
Good Morning - I have a Carrier Furnace Model 58CTA090---13114 My thermostat is set to 70 but the furnace will only run enough to keep the house at 64. I removed the cover on the furnace and there is … read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
hello. I have seen this question a few other times but maybe
hello. I have seen this question a few other times but maybe I wont have to pay a professional this time. I have a Ruud 90 plus Gas furnace that is 6 years old. Once in awhile it will just stop blowin… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
Hello, hope you are having a good day. We have carrier programmable
Hello, hope you are having a good day. We have carrier programmable thermostats and have two questions: First, when you program in a heat number, say 70 , this means that the room will heat TO 70 when… read more
The Home Smithy
The Home Smithy
Home Improvement Repair Consultant
1,890 satisfied customers
I posed a question/problem to your sight earlier. I have another
I posed a question/problem to your sight earlier. I have another problem/simptom to add. The furnace in question now fires immediatly however the blower never turns on to circulate the air.The furnace… read more
Al
Al
Master Service Technician
Votec, College, Master Electrical S
24 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x