How do you properly install and configure a Nest thermostat…

How do you properly install...
How do you properly install and configure a Nest thermostat for a dual fuel system?For reference, the current thermostat (Braeburn 2220NC) uses the following wiring terminals:
Rc (with jumper to Rh)
Y1
G
W1/E
W2
O
C
Show More
Show Less
Ask Your Own HVAC Question
Answered in 21 minutes by:
3/17/2018
Bill
Bill, HVAC Technician
Category: HVAC
Satisfied Customers: 111
Experience: Service Mgr
Verified

Hello,

Do you have the new Nest thermostat mounted and some wires already in?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
it was mounted about an hour ago. Still need to connect the wires to the terminals though.

Ok just a moment.

Ask Your Own HVAC Question

Old.....................New

Rc (with jumper to Rh) to Rh (red)
Y1 to Y1 (yellow)
G to G (green)
W1/E to W1 (black)
W2 to aux (white)
O to O/B (orange)
C to C (Blue)

Then the Nest will step through set up with you

Ask Your Own HVAC Question

For clarity, AUX is not the " * " terminal, but the W2/AUX terminal as shown on the attached image, correct?

That is correct..W2/Aux

FYI, this is the 3rd generation Nest if that matters at all. The Nest series all wire the same for your particular situation

Bill
Bill, HVAC Technician
Category: HVAC
Satisfied Customers: 111
Experience: Service Mgr
Verified
Bill and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 4 months ago
Working through step-by-step setup for the Nest. One question it is asking is what outdoor temp. should be considered to use the alternate heating. Is there optimal temp. this should be set at?
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Bill Your Own Question
Bill
Bill
Bill, HVAC Technician
Category: HVAC
Satisfied Customers: 111
111 Satisfied Customers
Experience: Service Mgr

Bill is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Can you help me wire this system? It's is a heat pump
Can you help me wire this system? It's is a heat pump without a fossil fuel kit. (The thermostat is supposed to replace the fossil fuel kit) Thermostat is a White Rogers/Emerson 1F85U-42NP RC-RH. O/B.… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I am trying to replace a Braeburn 2200 with a NEST
Hi, I am trying to replace a Braeburn 2200 with a NEST thermostat. The details are: … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Was wondering if someone can help with thermostat wiring. I
was wondering if someone can help with thermostat wiring. I am trying to put a Honeywell RTH7600 RET97 Series thermostat on a 12 year old Trane system with heat pump and gas furnace. The old system ha… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I am going from a Braeburn thermostat to a Honeywell
I am going from a Braeburn thermostat to a Honeywell RTH6450. The wires on the Braeburn were: R O (B) C Y1 E/W1 G W2 (with a jumper between E/W1 & W2) The book doesn't show a comparable transfer. Can … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I'm trying to replace my current thermostat with the Nest
Hello - I'm trying to replace my current thermostat with the Nest (3rd generation). I'm not sure how to connect 1 of the wires. Should the existing (brown) wire go into the W1 or E terminal in the Nes… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have an Amana (installation date 2009) heat pump (2-stage)
I have an Amana (installation date 2009) heat pump (2-stage) and I'm trying to determine if a Honeywell Lyric thermostat is compatible. The thermostat wires I have configured to digital thermostat are… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
old thermostat is TA32H01 on a water furnace it is using C
old thermostat is TA32H01 on a water furnace it is using C R L G O W Y1 my new tstat is a nest it has different hookups wondering which one to use? on the nest it has Y1 Y2 G ob Rc W1 W2aux C * Rh… read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
Have a 1996 carrier all electric furnace/heatpump attempting
Have a 1996 carrier all electric furnace/heatpump attempting to install second gen nest thermostat. Original stat has wires labeled as such: orange wire on O terminal White wire on W2 terminal brown w… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I am looking to replace my old thermostat with Nest
Hello. I am looking to replace my old thermostat with my new generation 2 Nest. I have 6 wires: R, O, Y, G, B, W1, and X2. My system is a dual stage heating/cooling with auxiliary heat. I'm unsure how… read more
joeydelia
joeydelia
HVAC-R Tech
High School or GED
81 satisfied customers
I have been trying to install the nest thermostat and and trane
I have been trying to install the nest thermostat and and trane x14. I have a unknown brand thermostat on now, wiring that currently is in place on this thermostat is jumper between Y2and W2= white, G… read more
SWFLHVAC
SWFLHVAC
67 satisfied customers
Installing a Hunter thermostat with a Goodman heat pump
I have a Goodman CPKE24-1AB, I'm attempting to install a Hunter 44132 Thermostat. This was the wiring indicated when I removed the Addison 3AAT80A5B11 Thermostat that was present before: R - Red X - R… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a new lennox Elite Series heat pump (newly constructed
I have a new lennox Elite Series heat pump (newly constructed house) and it is currently connected to a non-programmable Braeburn Model 1200 thermostat. I want to replace the Model 1200 with Honeywell… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Im replacing a Braeburn thermostat (with an emergency heat
I'm replacing a Braeburn thermostat (with an emergency heat switch) with Honeywell RTH6350/6450. I'm having trouble figuring out the wiring configuration. The Braeburn configuration is as follows: R O… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have a tempstar 2000. Installing a Braeburn 5300 Tstat.
I have a tempstar 2000. Installing a Braeburn 5300 Tstat. How do I figure out if Tempstar is a single stage HP, 2 stage or 3 stage. Inside blower has aux electric. Old White Rodger Tstat just has a W … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Im replacing a Trane Weathertron with a new Hunter 44860.
I'm replacing a Trane Weathertron with a new Hunter 44860. The Weathertron is configured as follows: R - Red O - Orange G - Green Y - Yellow X2 - Black B - Blue U - Light Green (U and W are jumped tog… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I am converting from a Weathertron thermostat to a Hunter model
I am converting from a Weathertron thermostat to a Hunter model 44860. The Weathertro was wired as follows: X2- Black O - Orange G - Green Y - Yellow W - White R - Red B - Blue the Brown wire was not … read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Hello Presently I have a heat pump furnace and Im trying
Hello XXXXX have a heat pump furnace and I'm trying to change a "Water Furnace" thermostat with a Honeywell RTH8500. Presently the Water Furnace has this configuration R Y/Y2 G C W/W1 O/W2 Y1 L The Ho… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I currently have a Honeywell programmable themostat, model
I currently have a Honeywell programmable themostat, model number T8611G2002 which we want to replace with a Honeywell model TH8320U1008. We have a heat pump with aux electric heat and air conditionin… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x