My question is about HVAC. The contractor prematurely

My question is about HVAC...
My question is about HVAC. The contractor prematurely installed air handlers from Comfort AIr, 11 units of VFH model.
The house is not done and the models are now discontinued, yet I need 3 condensers for outdoor. The manufacturer says I can install new model condensers and it is compatible with the old air handlers. However, the contractor insists that the new condensers will not work with old units and that I either get old discontinued condensers which are available in the warehouse or get all new mini-splits ( at a cost) and new condensers.
He insists, in spite of the manufacturer's reassurance, that the old and the new will not work together.
Obviously, the distributor is interested in getting rid of all discontinued condensers, so i am not sure who to trust.
Irina
Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 4 months ago
Posted by JustAnswer at customer's request) Hello. I would like to request the following Expert Service(s) from you: Live Phone Call.
Customer reply replied 4 months ago
Let me know if you need more information, or send me the service offer(s) so we can proceed.
Customer reply replied 4 months ago
model numbers:
condensers: A- VFH 42PA, 36QA; 24TA;
air handlers: B -VFH 09 MA-1;12 MA-1, 18 MA-1
Answered in 20 hours by:
3/18/2018
Bill
Bill, HVAC Technician
Category: HVAC
Satisfied Customers: 111
Experience: Service Mgr
Verified

Hello,

Actually I fail to see where any of this is your responsibility.

The installing contractor should be the one to make this right regardless of cost.

Lets say you get a quote to install the units, then at build time the units cost $5,000.. more than when quoted.

This is not your fault and you should not pay the additional 5K. It is not your fault units are discontinued or cost of new units are more.

In my opinion the contractor is protecting themselves and making you responsible. I would be embarrassed to ask my customer to make up the the difference in this exact situation.

Why wasnt the equipment alll ordered at same time?

We NEVER buy partial sets...always a full set, never indoor only.

As far as the discussion of if they will work or not......I see the indoor units will work with the upgraded units.

Now "discontinued" is not a bad thing. It simply means like everything else they are making a different version.

This is like saying the 2017 Car is discontinued. Yes they no longer make it, but that means nothing in the world of heating and cooling. If you buy "current" units at an extra cost - they will be discontinued in 6-12 months.

I would drop this right back in the contractors lap and give them a choice. Get the correct units even though "discontinued", or buy all new at no additional cost.

If the roof were half done and the roofer came back that the color shingles were no longer available and you needed to buy all new....the answer is no.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Thank you. It is not my responsibility, correct.
The supply store has the discontinued outdoor condensers, we can install them, yes.
However, I had to check all the information I was getting from my contractor because I did not trust his assertion that it is "better" to change all indoor units and install new condensers as well.
According to the manufacturer the efficiency will be slightly better with new condensers, - and this is what he is opposed to: ***** ***** and new, so that it is either all old or all new. He is saying that the computer part in the new condenser will not recognize the old indoor unit and will not work. It sounds like nonsense to me. He also says that the parts will not be available in a couple of years,- again, not true according to the manufacturer.
I see that you agree with the manufacturer.
Thank you for your response.

You are very welcome and I wish you the best.

I hope all works out well for you.

Just arte service to close thread and return back here for any follow up needed

Bill
Bill, HVAC Technician
Category: HVAC
Satisfied Customers: 111
Experience: Service Mgr
Verified
Bill and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Bill Your Own Question
Bill
Bill
Bill, HVAC Technician
Category: HVAC
Satisfied Customers: 111
111 Satisfied Customers
Experience: Service Mgr

Bill is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
HVAC air condition question here. I live in Northeast
Hello. HVAC air condition question here. I live in Northeast Florida and have a 1930 old home fully renovated about 6000 sq feet and we are doing a replacement of four old R22 units. The question is i… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Will Friedrich Model MR24DY3F outdoor unit be compatable
Second opinion] Will Friedrich Model MR24DY3F outdoor unit be compatable with Luxaire 24000 btuh horizontal coil in forced air residental system. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I had a Lennox Elite 10 system which was 15 years old and
I had a Lennox Elite 10 system which was 15 years old and had to replace the air handler last October. It was replaced with a Lennox Merit air handler CBX25UH(-10) unit by my Home Warranty Insurance. … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,942 satisfied customers
I have old carrier system model #40AQ024300BU, serial
HI, I have old carrier system model #40AQ024300BU, serial #5288A14497 Need to replace a coil, can I order that coil? or where can I get it I live in Danvers, MA… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I just had an older Goodman mini-split installed. 20CR air
Hi, I just had an older Goodman mini-split installed. 20CR air handler & HDP 18-1A condenser (R22). Works fine in both heating & cooling but the fan runs continuously. Is this normal? Tkxxx Bob Miller… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a 36,000 BTU Pioneer AC system. The air handler is
I have a 36,000 BTU Pioneer AC system. The air handler is working fine and is relatively new. However the compressor unit and fan are shot. Can a 2 ton (24,000 BTU equivalent) work with the 36,000BTU … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
454 satisfied customers
I have a this Rheem combo about 10 years old: RAKA-060JAZ
Hi. I have a this Rheem combo about 10 years old: RAKA-060JAZ Condenser RBHA-24J11NFBAI Air Handler Evaporator The compressor is fine, but the evaporator is so gunked up it's leaking an inch of conden… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Hi replacing an 2.5 ton attic Trane air handler (hydro air)and Trane 2ton condenser for u
Hi replacing an 2.5 ton attic Trane air handler (hydro air)and Trane 2ton condenser for upstairs in my house. Contractor quote $17,500 3 ton American standard 13 seer FirstCompany 36,000 BTU variable … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have a Rheem gas fired home furnace about 23 years old. It
I have a Rheem gas fired home furnace about 23 years old. It is now making a lot of noise; I assume it is from the bearings in the blower. I need to get rid of that noise; it is driving the wife nuts … read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I am a Heating & A/C contractor with a question about a GE
I am a Heating & A/C contractor with a question about a GE direct drive blower motor for a ceiling mount gas fired, forced air furnace. I could find no manufacturer tag on the unit. The motor is a GE … read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
The tech install an new american standard heat pump indoor
The tech install an new american standard heat pump indoor unit in Jan of 08 He said my indoor unit was old and not efficient. I have never been able to get the electric heat to work. I keep calling t… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I had an Amana 2 stage ASZ160361 Condenser #0804097789 and
I had an Amana 2 stage ASZ160361 Condenser #0804097789 and Evaporator CHPF36426A S# XXXXX Blower/coil MBE1600AA installed on 6/9/08 by Braatz Heating in Madison, WI, which is now out of business. I al… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have an existing Trane 2.5 ton air handler that is 3 years
I have an existing Trane 2.5 ton air handler that is 3 years old. The model no. is 2TEC3F30. Is the Ruud 2.5 ton heat pump, model no. 13PJA30A01 compatible with that Trane air handler? How can I find … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We have a relatively new heat pump(8/06) Carrier 2 ton/3seer.
We have a relatively new heat pump(8/06) Carrier 2 ton/3seer. Our air handler Trane(TWV024814Fa1) is old and rusting with multiple repairs over the past 2 years.....currently were quoted $225.00 plus … read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
I have two York single speed fan handlers that are 2 years
I have two York single speed fan handlers that are 2 years old. Model # XXXXX and AHP42C3XH21A. Back up elec coils. I need to replace 20 year old Trane XE1000 and XE800 heat pumps. Can I use the newer… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Heil Furnace H8ENL100F14B2 S/N A074544237 which I
I have a Heil Furnace H8ENL100F14B2 S/N A074544237 which I want to now get an A/C unit to go with this new furnace. Can you tell me what unit would be compatible and where is a distributor (not dealer… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have a 5 year old air handler (national comfort model epb
I have a 5 year old air handler (national comfort model epb 2400 a) and a very old condenser unit..it is 1.5 ton. I want to buy 2 ton and have it prof. installed..how do I know what condenser is compa… read more
Mario
Mario
Owner Of At Your Service Plumbing & Heat
High School or GED
672 satisfied customers
Air Handler B5VM-X49K-C Serial Number B5D090403255 Condenser
Air Handler B5VM-X49K-C Serial Number B5D090403255 Condenser Model FT4BE-042 Serial Number FTD090501825 There are 8 switches in the air handler cabinet what should each switch be set on for this confi… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.