I gotta warn you, my current HVAC vendor is stumped...

I gotta warn you...

I gotta warn you, my current HVAC vendor is stumped...

Contractor's Assistant: Are you an HVAC professional?

No.

Contractor's Assistant: Do you plan on doing the work yourself?

Possibly, but hopefully now. er now->not

Contractor's Assistant: Anything else we should know to help you best?

I think that's all before asking the question... :)

Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 1 month ago
I have a conventional oil furnace and just had a heat pump/AC installed. The intent was to use a single smart thermostat to control both ("Dual fuel", shut off the heat pump at 35F, or so and run the oil burner when it's very cold). Installer finished but now says that due to the "backup" electric heat on the heat pump that this isn't possible (and I need to put the oil burner on a second thermostat). How do I wire both systems to one thermostat? I was looking at p141 of this:https://forwardthinking.honeywell.com/related_links/thermostats/prestige/68-0311.pdfand it seems to be just what I'm looking for...? Am I right? And if so what do I tell the installer to get them to understand? And if I'm wrong, is there anything that I can do (besides having two thermostats?)
Customer reply replied 1 month ago
Failing the Honeywell... which DOES seem to me like it would work... It seems like this https://jacksonsystems.com/products/dual-fuel-kit-outdoor-thermostat.html would do the job. The thing the installer claims is the problem is that the airhandler will be running when the furnace is running (dumping cold air out the vents while the oil heat is heating the baseboards)
Answered in 3 hours by:
3/14/2018
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,977
Experience: Furnace, A/C and heat pump specialist.
Verified

If you had an electric sir handler installed with the heat pump, you will need two separate thermostats as the oil furnace and heat pump have independant transformers.

If you had a heat pump outdoor unit installed using the oil furnace as would be the proper way to do, then a single dual fuel thermostat will work.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
Electric air handler in the attic. Condenser outside. Not sure what you mean by "heat pump outdoor unit installed using the oil furnace"?I'd thought that fig 324 on p141 (link above) would use the two independent transformers?

No that will not work.Figure 324 is used when you have a transformer in the air handler for heat only and a separate transformer in outdoor unit to control contactor in outdoor.

What you are trying to do if you have an electric air handler is to control two entirely different systems with a single thermostat.

The problem is the air handler has its own transformer which control blower,heat strips, outdoor unit and everything and then the oil furnace also has a transformer that controls the blower, heat controls etc.

The proper way to do this would be to use the oil furnace as the blower for both the heat pump and oil furnace with a heat pump coil installed with the oil furnace.

Otherwise you have a stand alone oil furnace and a stand alone heat pump.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
Ok. I think I get why fig 324 doesn't work for me. Only remaining Q is whether my second link:https://jacksonsystems.com/products/dual-fuel-kit-outdoor-thermostat.htmlwould allow me to dual-fuel across the two systems.

Unfortunately NO.

Again the reason we can't control two separate blowers with one thermostat is that the thermostat has to have a 24v hot wire from transformer in the air handling unit and a 24v common from same unit.

You can have a separate transformer for outdoor which can go to RC.

The problem is we can't control two blowers that use two different transformers with a single thermostat

Ask Your Own HVAC Question
Customer reply replied 1 month ago
Only 1 blower (oil furnace is forced hot water) but I think I follow your line of thought. I gave the Jackson/iohvaccontrols guys a call and spoke to an engineer. They think that with an isolating relay on the oil furnace I can get what I want.Thanks for the assistance. I think I'm all set for now.

I gotcha.Good luck and hope that works.

airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,977
Experience: Furnace, A/C and heat pump specialist.
Verified
airheatman and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,977
8,977 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
OIL BURNER STOPPED RESET BUTTON NEVER POPPED IS THIS MY
OIL BURNER STOPPED RESET BUTTON NEVER POPPED IS THIS MY PROBLEM … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Oil furnace blower comes on, no flame or ignition. I buy the
oil furnace blower comes on, no flame or ignition JA: Did you check the furnace's filters? Customer: yes JA: Do you plan on doing the work yourself? Customer: I buy the parts JA: Anything else we shou… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My old oil furnace needs rest=ettiung in the mornings, but
My old oil furnace needs rest=ettiung in the mornings, but OK in the day. does the bi metal actuator itself ever need changing as the scavenge time is opnly 45 seconds … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Oil furnace not hot just added fuel today. Flashing light
oil furnace not hot just added fuel today JA: Did you check the furnace's filters? Customer: flashing light says lockout mode JA: Do you plan on doing the work yourself? Customer: no JA: Anything else… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a columbia emerald em-100 steel oil burner with a
hi mark i have a columbia emerald em-100 steel oil burner with a tankless approx 20 yrs old. Presently the circulator has to cycle at least 3 times on a call for heat to let the boiler cath up to the … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
First time heating oil furnace owner. Ran out of oil a week
First time heating oil furnace owner. Ran out of oil a week and a half ago, just got more delivered today, but cant get the furnace to kick on. it is blinking green, have tried holding the restart but… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Buderus G115WS/5 boiler with a Riello oil burner.
I have a Buderus G115WS/5 boiler with a Riello oil burner. Direct vent. I am wondering whether I can successfully convert this system to natural gas by installing a new burner designed for the purpose… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
When I run out of oil in my Lenox oil burner, the reset
HI when I run out of oil in my Lenox oil burner, the reset button turns red. One quick push and the burner fires up. This morning, no heat. I have oil and the reset button is blinking green, which I'v… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a wei-mclain gold oil burner that stopped firing up.
I have a wei-mclain gold oil burner that stopped firing up. the blinking green indicator light is flashing. the blinking green light goes off while I press the reset button for 45 seconds until I get … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Trane XV90 Oil Furnace. My furnace made some extra noise and
My furnace made some extra noise and then cut off... the red light on the oiled burner unit is flashing … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have an oil furnace... after running out of oil, then oil
I have an oil furnace... after running out of oil, then oil delivery today, I need to restart it. I have a Riello 40 burner. I've hit reset twice... sounds like it fires up but still blowing cold air.… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Oil furnace will not turn on message says standby but it
Oil furnace will not turn on message says standby but it doesn't do anything can anyone help… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Oil furnace will run if reset but will on run to degree,
oil furnace will run if reset but will on run to 69 degree, even if you have is set thermostat set on 80 degrees. Nozzle has been replaced, oil filter was changed.… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My reillo burner on my oil furnace wont fire it wont do
Hi, my reillo burner on my oil furnace wont fire it wont do anything when you push the reset button any advice … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Oil burner Aquastat possible problems. Two days. I have in
The stat is fairly new I think the igniter transformer might be bad or going bad. Which may have led to my problem.… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My patriot 80 fuel oil furnace ran out of fuel and now it
My patriot 80 fuel oil furnace ran out of fuel and now it wont blow hot air … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a oil burner assembly off a Shenandoah waste oil
I have a oil burner assembly off a Shenandoah waste oil furnace I have no spark I do have 120 volts at board for the transformer assembly that sits a top the spark electrodes is there a way to test th… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have an oil burner question, One week, Yes, Please connect
Please connect me with someone who deals with oil burner questions… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x