I installed a new thermostat but all that comes on is the…

Customer Question
I installed a new...

I installed a new thermostat but all that comes on is the fan no heat

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

What settings and what filters

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

I don't think so

Submitted: 6 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 minute by:
3/13/2018
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,178
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

Hello,

My name is Billy.

Please disregard computer generated phone offers as that option is not currently available.

Is the blower running nonstop? Was furnace power turned off before swapping?

Ask Your Own HVAC Question
Customer reply replied 6 months ago
No turned the power off
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago

Ok what color wire did you put on what terminal?

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Blue on b ...green on g ...white on w and red on r
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago

Thank you.

I am betting the blue actually goes on Y. You dont have a yellow wire and in the absence of yellow, blue is used.

Move the blue to Y terminal and test.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Switched but just the fan still with cold air
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago

is this a gas furnace with ac?

Ask Your Own HVAC Question
Customer reply replied 6 months ago
It's gas no a forced hot air
Customer reply replied 6 months ago
No ac
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago

furnace only?

Ask Your Own HVAC Question
Customer reply replied 6 months ago
it sounds like it kicked in but still cold air
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago

What is the new thermostat model number?

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Rth221b
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago

for heat only (gas furnace) this thermostat only needs 2 wires...R terminal and W terminal. The G and Y are for ac if you had it.

If you take the red wire and the white wire and just twist direct together...do you get heat?

Ask Your Own HVAC Question
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago

Then put red on R and white on W.

Try again as a test and let me know result

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Actually it's still blowing cold air
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago

ok if red is twisted to white directly...it is not a thermostat issue. Red to white direct bypasses the thermostat.

Can you go to furnace and tell me if flame on

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Where's the flame
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago

can you post a pic of your furnace?

Ask Your Own HVAC Question
Customer reply replied 6 months ago
There they are
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago

downloading now just a moment

Ask Your Own HVAC Question
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago
Ask Your Own HVAC Question
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago

was furnace working properly before the change?

In old thermostat what color was on what terminal?

Ask Your Own HVAC Question
Customer reply replied 6 months ago
it was calling for heat then shutting off in like a min.....red on rh .... Blue on b..g on green and white on w
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago

do you mind removing the doors off the furnace ?

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Ok they are off
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago

thank you, ***** ***** you post a picture of the circuit board in bottom?

Ask Your Own HVAC Question
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago

is that a piece of plastic on the wiring?

Ask Your Own HVAC Question
Customer reply replied 6 months ago
It was just removed it
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago

is there anything like that inside the blower wheel?

Ask Your Own HVAC Question
Customer reply replied 6 months ago
No
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago

ok,

on that circuit board....there are terminals like at the thermostat....can you see the thermostat wire and it attaches?

Ask Your Own HVAC Question
Customer reply replied 6 months ago
In not sure what I'm looking for
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago

I would circle but the board pic does not show me the left edge or bottom.

Ask Your Own HVAC Question
HVAC Technician: Regan Land, HVAC Technician replied 6 months ago
Regan Land
Regan Land, HVAC Technician
Category: HVAC
Satisfied Customers: 768
Experience: Over 20 years of experience, NATE Certified, Licensed HVAC Contractor, Certified IAQ Specialist
Verified

Hello, my name is ***** ***** It looks like Billy had to log off, so he opened this up to me. I'd like to revisit something you did before... you say that when you connect red and white wires together at thermostat that the heat comes on, correct? What brand was the old thermostat?

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I tried installing a new thermostat, now my compressor won't
Hi, I tried installing a new thermostat, now my compressor won't turn on. I feel air from the vents but they are weaker than normal and not cold. I installed the old unit with thesame issue … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,178 satisfied customers
Blower motor runs in heat but ac wont come on also fan
Blower motor runs in heat but ac wont come on also fan doesn't come on when you turn fan to on … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Amanda PTAC PTC093G35A 9000 BTU. (Background)-This
I have a Amanda PTAC PTC093G35A 9000 BTU. (Background)-This is my 2nd unit. My previous one was 8 years old and I have a wireless thermostat that's is being used with the new unit. The new unit works … read more
Bill
Bill
Service Mgr
114 satisfied customers
I'm trying to install a 7560e programmable thermostat to
I'm trying to install a 7560e programmable thermostat to replace an old (mercury) unit. I wired up everything based on current configuration, but the heat (electric) won'the come on. … read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
I had Honeywell RTH9580 thermostats installed in my Florida
I had Honeywell RTH9580 thermostats installed in my Florida vacation home last fall. This summer, the Lennox air handlers have been sweating in the a/c closet and dripping. A fan blowing on the units … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
How do i switch to the cooling function of my system
how do i switch to the cooling function of my bryant system preferred 2 stage; installed jan 2017; can't find manual … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Installed a 4 ton straight cool electric heat 20 kw had to
installed a 4 ton straight cool electric heat 20 kw had to add power the old unit was a 3 ton. only had one power supply line when I turn heat on it pops the 3 amp fuse a/c works fine . The 3 amp fuse… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
New 6000series installed. worked nicely for a week now temp
new 6000series installed. worked nicely for a week now temp stays at74 . ihear the auto go on but no heat no natter what I enter. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Have honeywell stat that fan does not work in auto but it
Have honeywell stat that fan does not work in auto but it does in on … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,178 satisfied customers
I have a Carrier Weathermaker 8000. Heat comes on but fan
I have a Carrier Weathermaker 8000. Heat comes on but fan isn't blowing. The LED light is solid, so no error codes. The fan spins freely by hand. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Trane TWN024-060C heat pump & have changed out the
I have a Trane TWN024-060C heat pump & have changed out the old (OLD!) manual thermostat to a digital one; Honeywell RTH2300/RTH221. There are R, G, B, Y & W wires coming out of the wall. the old ther… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,178 satisfied customers
Heater / heat pump stopped working, thermostat found broken,
heater / heat pump stopped working, thermostat found broken, replaced but no change...no heat … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,178 satisfied customers
I have Honeywell TH8000 Series programmable thermostats
hi I have Honeywell TH8000 Series programmable thermostats that the fan only blows out hot air. I have tried new batteries, changing the settings and unplugging it still does the same things. I am lea… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Im having an issue in which my furnace fan will not
Im having an issue in which my furnace fan will not start/run when the thermostat fan setting is on AUTO with HEAT ONLY. The fan works just fine when set to AUTO with the AC but not with the heat. The… read more
Jason Whatley
Jason Whatley
60 satisfied customers
I have a W8835 envirazone panel system with four zones, with
I have a W8835 envirazone panel system with four zones, with TrueSteam humidifier system. Then I have Visionpro IAQ thermostats. In both cooling and heating settings, my furnace fan will come on for n… read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
HI, I have an xr11 trane with a honewell electrostatic filter
HI, I have an xr11 trane with a honewell electrostatic filter and the wiring connection goes straight down across where a regular filter would have been installed. so one cannot be installed. Does thi… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
We had a new Payne heat pump installed in the fall of 2009,
We had a new Payne heat pump installed in the fall of 2009, as well as the Totaline Smart thermostat. We have had a problem with the heat pump turning on and off and won't maintain the set temperature… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
I have a Bryant 90 plus approximately 11 years old. We turn
I have a Bryant 90 plus approximately 11 years old. We turn on the heat, the blower motor comes on with code 12, runs for about 90 seconds and then furnance starts and no heat. There is no flame. The … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x