Three bits of data requested on heat pump. Ruud upla-031jaz.

What is the lowest temperature...
Three bits of data requested on heat pump. Ruud upla-031jaz. What is the lowest temperature it is designed to operate in? 35, 40 or 45 degrees?Can it run concurrently with emergency heat?Is the reversing valve energized on heat or cooling?Thank you.
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 minute by:
3/13/2018
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,213
Experience: Furnace, A/C and heat pump specialist.
Verified

My name is ***** ***** I am happy to be able to work with you on this today.Please be patient as I respond as sometimes it takes me a few moments to gather proper manuals and specifications on your equipment in order to provide accurate answers.Please wait until we are finished to rate my answer.Just to let you know, the website will be offering a live phone call for an additional fee. Due to my current work load and responsibilities I may not be available for the live phone call .Please note that there is an additional cost for the service and if a technician calls it may be a different technician. However we can continue here as long as needed .

Ask Your Own HVAC Question

1.You can actually use the heat pump down to about 5 degrees,it just loses efficiencey below about 25 degrees.

2.You can run the heat pump along with the heat strips but that would be considered using the heat pump and heat strips as auxillary heat. If you select EMERGENCY heat on thermostat the elements will work alone without the heat pump

3.Ruud energizes the reversing valve in HEAT mode.

If you have further questions, please let me know.
Thanks for letting me work with you.When we are finished if my answer has been polite, professional,and thorough, please click one of the ratings before you go. If you still need help let me know!.Expert is not paid for assisting you until you rate answer.Feel free to follow up for 30 days at no additional cost. Bonus always appreciated if you feel justified.
To rate answer, please select one of the stars on the page.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Thank you. Installing an ecobee smart stat right now.

Let me know if you have further questsions and I will be happy to help.

Ask Your Own HVAC Question

If you just installed,give it several minutes to acclimate to actual room temp

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Yeah. It’s been three hours since I put it on the wall.
Customer reply replied 4 months ago
Wires are warm to touch.

Wires should not be warm. Ny heat source near thermostat or wiring?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Yeah. It was weird. I pulled stat off the wall and put palm of hand on top of wiring base with all of the wires bent around to fit in the cavity between the stat and the base. It felt warm. I unmounted the base and pulled the slack out and pushed it back into the wall. Now it reads 81. Two degrees cooler.

That is strange.Not sure where the heat would get in the wall

Ask Your Own HVAC Question
Customer reply replied 4 months ago
I think the heat is generated from the stat itself. Put a nest on and it reads proper temp.
Customer reply replied 4 months ago
I’m going to stick with the Nest. But during testing I did emergency heat test that should have had the blower running. No blower. And I could smell burning elements.

THat should be controlled by a sequencer in the air handler.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
I should wait longer to see if the blower turns on, huh?

No fan should come on immediately with first heat strip.Was this working normally before you messed with stat or is this a new installation?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
It was working before I changed stat. I work two hours away from here. And I’ve always used a nest. When I moved into this new house the furnace wasn’t working. My goal was to get it to a known working state. And we did that yesterday and this morning. Now I’m trying to see if I can use a smart stat. Either Nest or Ecobee3 Lite. Both of which need to know the three questions I asked for setup.
Customer reply replied 4 months ago
sir. But, I’m recalling something from last night. I went to bed late. It was cold. The heat pump wasn’t turning on. I decided to give up for the night. I turned heat to emergency heat and blower turned on. I went to bed and fell asleep fast. Two hours later I woke up to a burning electric/hair smell. The blower wasn’t running. I turned everything off.

Will blower come on now n any mode? Heat cool or FAN ON?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
I then went to the heat pump and realized I hooked up wrong color wire (green instead of brown) while using flashlight last night. Got the right wire hooked up and heat pump worked. Never checked emergency heat again.
Customer reply replied 4 months ago
Blower will work in heat, cool and fan.

You may have a burned sequencer.IN emergency mode the sequencer tells motor to come on

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Wouldn’t surprise me. My luck these days. Do you know the part number for sequencer? I’ll get one tomorrow.

Which air handler do you have?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Ubha-17j11nfaa

Give me a second

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Take your time. Thank you.
Customer reply replied 4 months ago
Thank you. All other tests pass. I appreciate your help. It was in the nick of time before snow came down today. I’ll get the sequencer tomorrow and replace it. Have a great night Tim.

THanks and good luck

airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,213
Experience: Furnace, A/C and heat pump specialist.
Verified
airheatman and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 4 months ago
All good now. Thank you.
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,213
9,213 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have an HVAC system that does not seem to be functioning.
I have an HVAC system that does not seem to be functioning. The compressor, fan, and blower all seem to be working. The pipes coming from the compressor are hot. I just had the system looked at and th… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,948 satisfied customers
I am replacing an old GE WeatherTron model # 3AAT80A1A1 with
Hello, I am replacing an old GE WeatherTron model # 3AAT80A1A1 with a new Bosch BCC100 thermostat which is supposed to be compatible with a Heat Pump which I have. The way the wires were hooked up to … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I'm ***** *****. I have a Honeywell model RTH6580WF. I' m
Hi, I'm ***** *****. I have a Honeywell model RTH6580WF. … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,019 satisfied customers
I bought a honeywell programmable thermostat to replace my
I bought a honeywell programmable thermostat to replace my mercury style thermostat. I have a heat pump, and electric furnace. I followed the instructions but have not had success. It it cold outside,… read more
airheatman
airheatman
HVAC Technician
6 years college
9,213 satisfied customers
I have a York CHPO36-6a and have taken the inside unit out
I have a York CHPO36-6a and have taken the inside unit out when I converted to gas heat. I use only the air conditioning on the outside unit. My question is if the reversing solenoid that must be ener… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
It would be helpful to have the functions of all the letters
It would be helpful to have the functions of all the letters on all the the PC cards from compressor air handler to thermostat example what function does the Orange connection do---- what function doe… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
If the unit is freezing in heat mode and the reversing valve
If the unit is freezing in heat mode and the reversing valve didn't make it's usual hiss. Could it be the valve is bad . Unit doesnt freeze in cooling ..ruud heat pump… read more
airheatman
airheatman
HVAC Technician
6 years college
9,213 satisfied customers
i have a 2 ton package uniy heat pump and the suction line
i have a 2 ton package uniy heat pump and the suction line is cold like when i run a/c when i turn on the heat switch, i've check the defrost board and i think the reversing valve was working? is ther… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
I have a Ruud heat pump model #UPKA-013JAZ (serial# M120307891).
I have a Ruud heat pump model #UPKA-013JAZ (serial# XXXXX). I need to know 2 bits of information 1. What type of system is it? (ie. Heat pump w/backup heating system, Heat/Cool multiple stages(with 1 … read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
My mother has a rheem unit Model # RGRA-12ERAJS, Serial # EH5D707F289706009.
My mother has a rheem unit Model # XXXXX Serial # XXXXX Two Heating and Cooling guys have worked on the unit and have not been able to get any heat using the heat pump. It works cooling the house and … read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I just recently purchased and installed a Honeywell RTH6350
I just recently purchased and installed a Honeywell RTH6350 Thermostat. The issue I am having is that when the heat kicks on, the auxillary heat kicks on immediately. The temperature inside the house … read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
Why would my Rheem heat pump blow cold air when set to heat?
Why would my Rheem heat pump blow cold air when set to heat but blow hot when the aux heat kicks in?… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,349 satisfied customers
Trying to connect White Rodgers 1F58-34 thermostat to RUUD
Trying to connect White Rodgers 1F58-34 thermostat to RUUD Model RQMPA030JK Package-Unit heat pump. Heat pump is single-phase, 208/230v, 60 Hz and has 10 kw aux heating strips installed. The low-volta… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I have a heat pump and a gas furnace. The thermostat has a
I have a heat pump and a gas furnace. The thermostat has a Y terminal to call for the compressor and an O terminal to call for the reversing valve. It also has terminals to call for auxiliary and emer… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
My Luxaire heat pump unit is running emergency heat due to
My Luxaire heat pump unit is running emergency heat due to outside unit not running. Have power to unit. If system is in off mode for a hour or so then turn heat on the fan and compressor run for 15 t… read more
freon
freon
Owner
High School or GED
214 satisfied customers
I have lennox HPX-A19-038 heat pump with an indoor electric
I have lennox HPX-A19-038 heat pump with an indoor electric backup blower coil. When the stat calls for hest the outside unit does not come on and the emergency heat designation comes on the stat. We … read more
DuWayne
DuWayne
Sales/ Service
Vocational, Technical or Trade Scho
126 satisfied customers
My Ruud Heat Pump model UPMC-036JAZ, serial 6306-m1501 12862,
My Ruud Heat Pump model UPMC-036JAZ, serial 6306-m1501 12862, mfd 04/01, keeps icing up. I have two friends who have been in the A/C business for the last 35~40 years. They came over and checked the c… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
Im replacing my Carrier programmable thermostat with a new
I'm replacing my Carrier programmable thermostat with a new Honeywell RTH7500 series thermostat. I have a heat pump with aux gas furnace. My problem is, I have two wires, labled S1 and S2, that dont m… read more
Rick or Nick in Texas
Rick or Nick in Texas
General Manager-Lead Tech
Own and run HVAC business 29yrs
44 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x