Customer Question
Need help wiring a...

Need help wiring a honeywell r7284u from a r7184b primary control. I attached the wires from the 7184 exactly to the 7284 (burner to burner, igniter to igniter, valve to valve, L1 to L1, the 4 L2's to the 4 L2's, 2 cad's to cad) there is not limit wire connection on the 7184, so i dont have a wire from that to hook up. the r7284u sets on standby and nothing is happening. I seen in the forums that it must be used?

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

Just got the new primary today (R7284U) and just installed it about 30 minutes ago. I had major tripping going on with old 7184 controller after a power issue (transformer at nearby power station caught on fire and left us in the dark for hours til it got replaced, in late january). system tripped intemittently since then til last week, it couldn't be reset and run. Replaced pump (solenoid type), coupler, igniters, nozzle yesterday and it ran for 10 cycles and started tripping again. cad cell is testing okay, transformer is fine too. Noticed the led on the old primary stayed on, solid, after burner shut down and about 2 minutes after fan stopped, then would trip in 3 seconds when a call for heat happened. it was also very warm, not hot, to the touch. So, i decided to change it up to the universal model with the troubleshooting display to get a better handle on any problems. Its the wiring up the new one that I need help with so I can get some heat as its 30 outside now and all i got otherwise is 2 space heaters

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Thermostat and filters are fine no dirt in line

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

I just need to know how to wire up the new primary (honeywell R7284U) from the old primary (honeywell R7184B) so the furnace runs

Submitted: 4 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 9 hours by:
3/12/2018
HVAC Technician: Rick, HVAC Supervisor replied 4 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,398
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. If my initial response doesn’t answer your question then let me know and we can continue our conversation.

You need to run a new 120 volt hot lead to L1 and move the lead on L1 (most likely from the furnace limit) to LIMIT.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Indicator light on my Interrupted Electronic Oil Primary
Indicator light on my Interrupted Electronic Oil Primary Control (Honeywell R7184B) does not go on and reset button will not restart burner. I have power going to the control. Installed a new primary … read more
Rick
Rick
HVAC Supervisor
24,398 satisfied customers
Ihave a thermoflo oil furnace model OL11=105FDA.It
Ihave a thermoflo oil furnace model OL11=105FDA.It originally had Honeywell R7184B burner control I changed it due to malfunction with Honeywell R7284U. every thing is the same except for the old cont… read more
Rick
Rick
HVAC Supervisor
24,398 satisfied customers
Trying to wire my honeywell 7284 oil primary and can't get
trying to wire my honeywell 7284 oil primary and can't get it to work … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Just put in a honeyell r7284u on a warm air furnace. Its
Just put in a honeyell r7284u on a warm air furnace. Its showing me tt limit opend what does that mean and do I have to install a jumper … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Rick. My name is ***** *****. I have an Olsen Furnace with a
Customer: Hello Rick. My name is ***** *****. I have an Olsen Furnace with a Beckett R7184B Primary Control. Plenty of fuel, new air filter, new oil filter cartridge. When it reaches the set temperatu… read more
Rick
Rick
HVAC Supervisor
24,398 satisfied customers
I have a honeywell R8184g 1302 intermittent ignition oil
I have a honeywell R8184g 1302 intermittent ignition oil primary that has failed. I am replacing it will the recomended replacement honeywell r7284 primary. I have hooked all of the wires up as the di… read more
Rick
Rick
HVAC Supervisor
24,398 satisfied customers
Rick, ***** ***** here. i have an issue with a tripped reset
Customer: Hi Rick, ***** ***** here. i have an issue with a tripped reset on the primary control for an oil burner. … read more
Phil
Phil
Mechanical Engineer
7,426 satisfied customers
Hello- I have a Beckett model AFG oil burning furnace with
Hello- I have a Beckett model AFG oil burning furnace with (I think) a bad ignition primary. The old ignition is a Honeywell R8184G1427, and the new replacement is the digital replacement R7284U. I ju… read more
Rick
Rick
HVAC Supervisor
24,398 satisfied customers
I want to replace the R8182D with a L7224 but what happens
I want to replace the R8182D with a L7224 but what happens to the cad wires? I have the new unit in and the house is getting cold. I need to fire this up.… read more
Rick
Rick
HVAC Supervisor
24,398 satisfied customers
im trying to install an new beckett oil burner genysis in my
im trying to install an new beckett oil burner genysis in my furnace and cant seem to figure out the wiring to a honeywell circuit board can u help??… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have in my hand a Honeywell Oil primary R7284 to replace
I have in my hand a Honeywell Oil primary R7284 to replace a Honeywell R8184G1427 which I believe is original on the Ultimate oil fired boiler I have. I see the orange motor, black and white coming in… read more
Rick
Rick
HVAC Supervisor
24,398 satisfied customers
Hello there, I have a Miller 75,000 BTU oil Furnace Model
Hello there, I have a Miller 75,000 BTU oil Furnace Model CMF 80-PO CONU I bought a new Honeywell R7284U they said it replaced my old one. I have been working on it for a few days and just had a frien… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
becket honeywell r7184b have to start furnace by pushing red
becket honeywell r7184b have to start furnace by pushing red button.it will run then shut off again with light flashing half second intervals.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
billy r7284u no limit on previous controler ran limit to l1
billy r7284u no limit on previous controler ran limit to l1 black furnanc worked but thermostat did not… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Beckett burner with a honeywell R7184B controller.
I have a Beckett burner with a honeywell R7184B controller. The controller needed to be reset about a month or so ago and has needed increasing resets up until today and now the burner only runs for a… read more
Rick
Rick
HVAC Supervisor
24,398 satisfied customers
I would like to know the proper way of wiring up a White Rodgers
I would like to know the proper way of wiring up a White Rodgers 50E47-843 Furnace Control Box. I had a WR 50E47-140 and it was bad. I wired up the 843 but it isn't working. Here is how I had it wired… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I bought a Honeywell YTH6320R1015 wirelees thermostat kit for
I bought a Honeywell YTH6320R1015 wirelees thermostat kit for my Armstrong Ultra 80 oil fired furnace with a Beckett burner w/Honeywell R7184B. When I wired the interface module the burner went into l… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have a oil water heater with a R7184B on it, the AC power
I have a oil water heater with a R7184B on it, the AC power was off for about a day while some work was done. The unit now is in recycle mode, the burner runs and fires for about 10 seconds (the LED f… read more
Robert
Robert
Associate Degree
161 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x