Furnace not working. Error LED code 1 short 2. 4 years - no.

Customer Question
Bryant Furnace not working...

Bryant Furnace not working. Error LED code 1 short 2 long

Contractor's Assistant: How old is the appliance? Have you gotten error messages before?

4 years - no

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

Model lnumber 912SB48080S17

Submitted: 4 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 8 minutes by:
3/10/2018
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 4 months ago
Brian HVAC Guy
Brian HVAC Guy, HVAC Technician
Category: HVAC
Satisfied Customers: 1,024
Experience: I have been an HVAC/R mechanic/technician for 30+ years.
Verified

Hi I'm Brian and I'll be happy to help with this!

How long of a period of time did you notice the furnace flashing this code? Did you have a power failure before or during any of the noted times this code was flashing?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Furnace quit working overnight. Discovered code an hour ago troubleshooting. No power failure.
Customer reply replied 4 months ago
You don't have a clue I can tell. Never mind
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 4 months ago

Thanks for clarifying. The reason I ask is on that model furnace the flash code 1-2 is a blower run for 90 seconds after an interruption in power if there is a call for heat at that time. Could the filter panel possibly have come loose tripping the power safety panel interlock?

Ask Your Own HVAC Question
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 4 months ago

I assure you after nearly 40 years in HVAC that I am well versed in furnace diagnosis and repair. I just need to gather a little more information to be able to zero in on what the issue may be.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Brian HVAC Guy Your Own Question
Brian HVAC Guy
Brian HVAC Guy
Brian HVAC Guy, HVAC Technician
Category: HVAC
Satisfied Customers: 1,024
1,024 Satisfied Customers
Experience: I have been an HVAC/R mechanic/technician for 30+ years.

Brian HVAC Guy is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have an older furnace. It only has 1 LED indicator. It's
Hi, I have an older Bryant furnace. It only has 1 LED indicator. It's flashing 1 short and 2 long. … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
My 90 Plus furnace is not heating. The exhaust fan comes on
my Bryant 90 Plus furnace is not heating. The exhaust fan comes on and goes off but the furnace does not ignite and heat … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,948 satisfied customers
Ryant furnace led flashes 2 slow then 4 fast flashes
ryant furnace led flashes 2 slow then 4 fast flashes … read more
Charles Bodenheimer
Charles Bodenheimer
Owner
Associate Degree
78 satisfied customers
I'm trying to figure out how to light the pilot on my
Hi. I'm trying to figure out how to light the pilot on my bryant furnace. Seems it went off. … read more
Rick
Rick
Supervisor
24,242 satisfied customers
I have a furnace, model #350AAV that will not initiate the
I have a Bryant furnace, model #350AAV that will not initiate the heating sequence. The LED is Green and is currently ON. I ran the Component Test sequence and the code that came up wast 12 (1 short a… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
Gh Efficiency Furnace will not turn on. After power cycling,
Bryant High Efficiency Furnace will not turn on. After power cycling, blower goes on for a short time. LED flashing 5 X. Model 395CAV048090 … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,349 satisfied customers
My furnace doesn't turn on. It igniter doesn't glow. I check
Hi, My furnace doesn't turn on. It igniter doesn't glow. I check the resistance and it reads 65 ohm. The interesting part is that my 24VAC reads 27.20. When I turn it on, the fan blows for short perio… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Model 350MAV0360FHKA induced draft motor not coming on. At
Bryant Model 350MAV0360FHKA induced draft motor not coming on. At first I was thinking it was the motor, because it was hot to the touch, yet not turning, but when I tried another motor it too did not… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
We have a bryant 340 AAV furnace. The blower runs but there
We have a bryant 340 AAV furnace. The blower runs but there is no heat. We don't see the burner light on.… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Carrier furnace model 58MVP080. It is displaying
I have a Carrier furnace model 58MVP080. It is displaying LED code 2-4 (Secondary Fuse is Open). When I turn off the thermostat (system off), the LED code is a steady light (Control has 24VAC power). … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Bryant Plus 80 Series, Model 3395CAV042091AGJA, Series G, S/N
Bryant Plus 80 Series, Model 3395CAV042091AGJA, Series G, S/N #1696A05280 Getting an intermittent LED Code 12. What is the normal diagnosis and repair? Powered down the furnace and re-powered after th… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
i have a bryant 340aav a have a 3-1 led flash. the furance
i have a bryant 340aav a have a 3-1 led flash. the furance runs but NO heat. blower working but NO ignition. I tryed buying a new thermostat… read more
BillyHvac
BillyHvac
Journeyman Service Technician
State Licensed Mechanical Contractor
13,790 satisfied customers
I have a Bryant Plus 90 Propane furnace. The system will not
I have a Bryant Plus 90 Propane furnace. The system will not start at all. There is a repeating LED blink code: 2 short / 4 long. What does this indicate?… read more
BillyHvac
BillyHvac
Journeyman Service Technician
State Licensed Mechanical Contractor
13,790 satisfied customers
My furnace will not ignite. I set the thermostate for heat
My bryant furnace will not ignite. I set the thermostate for heat and the blower starts, but no heat comes from the registers. I looked at the troubleshooting section of the manual for th floashing LE… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,038 satisfied customers
I have a Bryant furnace Series G, 56,000 BTU Model 376CAV024070
I have a Bryant furnace Series G, 56,000 BTU Model 376CAV024070 not working properly (blower going on and off intermittently) and displays a code of red blinking light of 1 short followed by 2 longs. … read more
BillyHvac
BillyHvac
Journeyman Service Technician
State Licensed Mechanical Contractor
13,790 satisfied customers
I have a Bryant Plus80v furnace and the burners do not ignite.
I have a Bryant Plus80v furnace and the burners do not ignite. When the call for heat happens, the LED is solid orange, then there is a click, it flashes green for a second, then begins flashing orang… read more
BillyHvac
BillyHvac
Journeyman Service Technician
State Licensed Mechanical Contractor
13,790 satisfied customers
I have a Bryant plus 80 with an error code of 3 short blinks
I have a Bryant plus 80 with an error code of 3 short blinks and 1 long blink (31?) Blower comes on and does not ignite, blower runs about 10 minutes and then shuts off. What could be thee issue?… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,038 satisfied customers
I have Bryant Model 355MAV060100ADKA furnace. I am getting
I have Bryant Model 355MAV060100ADKA furnace. I am getting the error code of 4 Amber LED flashes followed by 4 Green LED flashes. I cleaned the filter & cannot get the error code to clear.… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,349 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x