Furnace runs when cycle complete wont come back on unless power is turned off then back on

Contractor's Assistant: Did you check the furnace's filters?

Yes clean

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Submitted: 6 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 hour by:
3/9/2018
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,879
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, it is most likely the case that the furnace is tripping its *high limit safety cut out switch* about the same time that the thermostat is satisfied. That will cause this problem.

.

Cause is usually a dirty air filter, OR on older furnaces a clogged blower wheel and cooling coil...OR a bad high limit switch. Or anything that limits air flow through the furnace

.

We can go from here without a time limit.

.

My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today.

If you need more assistance, please use the reply box and let me know.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,879
9,879 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,879 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Goodman furnace light flashing four times. Fan kicks on but
Goodman furnace light flashing four times. Fan kicks on but wont ignite … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
The Trane V 80 will only run 1 cycle then shut off, a 3
The Trane V 80 will only run 1 cycle then shut off, a 3 blink code comes on and it will not restart unless the power is turned off and on again. On restart I can hear the relays close, the igniter glo… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My furnace is not coming back on after it cycles sometimes.
My furnace is not coming back on after it cycles sometimes. I checked the thermostat, it is good. I cycle off the power off and on and it comes back on. I am thinking furnace control board? What do yo… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My Bryant MAV360 has stopped working. Have had problems with
My Bryant MAV360 has stopped working. Have had problems with iceblocked air intake in the past. same today. Cleared it, but the furnace won't restart. Turned main power off/on. The red light for error… read more
theplumber717
theplumber717
Plumber
Vocational, Technical or Trade Scho
792 satisfied customers
Consolidated Industries furnace MBA080NH3R. Furnace would not
Consolidated Industries furnace MBA080NH3R. Furnace would not start. Found draft inducer motor locked-up (bearings) and over heating. Replaced draft inducer assy. Furnace now runs through normal ignit… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Thermostat shows heat on but will not start the furnace unless
Thermostat shows heat on but will not start the furnace unless I pull the thermostat out, taking all electricity away and then reinstalling. This will start the furnace and the furnace will shut off w… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
Howdy Kent. I have a Bryant 383KAV (made in 97) and I am getting
Howdy Kent. I have a Bryant 383KAV (made in 97) and I am getting the error code 12 which reads: Blower on after power up (115v or 24v) - Blower runs for 90 seconds, if unit is powered up during a call… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a goodman95 furnace, I have just went through a cleaning
I have a goodman95 furnace, I have just went through a cleaning it is 6 years old, now the furnace draft motor is running all the time - no blink codes… read more
Heath.M
Heath.M
Refrigeration Mechanic
Vocational, Technical or Trade School
223 satisfied customers
my dukane furnace wont start. the ventilation blower starts,
my dukane furnace wont start. the ventilation blower starts, then goes off. only once in a while will the furnace light and run. If i turn off power , then turn it back on, it cycles again. But it won… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Hello, I have a lennox 21 pulse furnace. It was installed
Hello, I have a lennox 21 pulse furnace. It was installed in 1999 and was just maintenanced last fall. In the last few weeks, the furnace is not turning on and I notice the green sensor light is off. … read more
gmac2905
gmac2905
hvac tech
Vocational, Technical or Trade Scho
18 satisfied customers
Heater promblem on a Lennox g 23. Got back from honeymoon
Heater promblem on a Lennox g 23. Got back from honeymoon turned it on and all smoke detectors went off. Came down stairs and it wont light. Any suggestions?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My carrier furnace will come on and run when you turn the thermostat
I need help with my carrier furnace. It will come on and run when you turn the thermostat switch on, It will run for a while then shuts off, but it will not turn back on unless I turn thermostat switc… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
armstrong air furnace blower turns on and off during heat cycle
armstrong air furnace blower turns on and off during heat cycle burners stay on then after thermostat shuts it down it may or may not come back on i heat thermostat click but nothing happens… read more
Mike
Mike
Service Tech/ Installer
High School or GED
149 satisfied customers
I cannot get my furnace to turn on. The pilot light wont come
I cannot get my furnace to turn on. The pilot light wont come on The thermostat is set to heat, the electrical switch on the box coming from the furnace is set to on, but nothing is happening. The cir… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a train XE 78. It has been acting up for a couple weeks.
I have a train XE 78. It has been acting up for a couple weeks. Last night it quit. The fan initially comes on to blow itself out but then it wont light. It continuasly goes through this cycle. What d… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
My coleman/evcon mobile home propane gas furnace runs about
My coleman/evcon mobile home propane gas furnace runs about 5 minutes,turns off, then back on (short cycles?).… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I own a carrier gas Furnace. it is a 1992 model. Model 585XA08066. The
I own a carrier gas Furnace. it is a 1992 model. Model:585XA08066. The problem is when it starts up it will run for a few minutes, then turn off. The thermastat (which I have replaced) shows its still… read more
Charles
Charles
HVAC Technician
Associate Degree
91 satisfied customers
when i turn my gas furnace it stays on until reaches the desired
when i turn my gas furnace it stays on until reaches the desired temperature but after that all the flames turn off and they wont turn back on when the house gets cold, what could it be?… read more
Robert
Robert
Associate Degree
161 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x