Phil I'm a electrical engineer can HVAC engineer I have a…

Customer Question
Hi Phil I'm a...

Hi Phil I'm a electrical engineer can HVAC engineer I have a problem with a carrier furnace that's an 80% the model number is ***** 110. The fan was bad in this furnace and I used a new fan that will go into any furnace but now this furnace is looking for feedback that the fan is running. There is a 4-pin connector on this 1 pin has 24 volts and I need to be able to bypass this feature in order to have the furnace run

Contractor's Assistant: Are you an HVAC professional?

Yes I am

Contractor's Assistant: Do you plan on doing the work yourself?

Yes everything is done I just have to bypass this feature using that 4 pin connector

Contractor's Assistant: Anything else we should know to help you best?

No I just need a quick answer on how to bypass this

Submitted: 3 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 3 months ago
Need an answer please.
Customer reply replied 3 months ago
Posted by JustAnswer at customer's request) Hello. I would like to request the following Expert Service(s) from you: Live Phone Call.
Customer reply replied 3 months ago
Let me know if you need more information, or send me the service offer(s) so we can proceed.
Answered in 1 hour by:
3/9/2018
HVAC Technician: Phil, Mechanical Engineer replied 3 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello. I need to know if the new fan motor you bought is 3 or 4 speed motor that uses a *run capacitor, OR a variable speed motor costing $600 to $900 and does not use a run capacitor.

I need to know how many wires connected to the old motor and how many connect to the new motor in order to determine the type, so far it sounds like you might have gotten an incorrect type of motor

.

Take close up, exceedingly well focused photo's of the wiring diagram glued inside the furnace/air handler door, and the printed circuit board mounted on the blower, , that shows where the thermostat wires connect, and I will mark them up with trouble shooting instructions.

Use the 'add files' link next to your send button to get the photo(s) to me.

.

We can go from there with training, coaching and diagnosis.... without a time limit, In depth with as much detail as needed .

.

When we finally get the situation solved, please select the 'finish and rate your expert link' near the top of your page and click on it.

.
My goal is to give you the best experience possible!
I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today.

If you need more assistance, please use the reply box and let me know.

Ask Your Own HVAC Question
Customer reply replied 3 months ago
I like using Mars Motors which are far more efficient then PSC Motors. They are five speed have 5 wires all operate from 120 volts they are a DC motor so no run capacitor and I have the fan running properly
Customer reply replied 3 months ago
The Mars Motors I use will work with any furnace. This Carrier Furnace is an older one and the fan for it is not available. There were four wires going to coming from the old fan motor that we're not power ground and neutral. Those wires go back to the computer to tell it that the fan is running I need to bypass this feature until I can put a new furnace in for them
HVAC Technician: Phil, Mechanical Engineer replied 3 months ago

I might be missing something here,

A bit about myself, I am 77 years old with 58 years in the business, the first 35 years running my own HVAC contracting company with 27 staff, the last 25 years or so consulting nationally, mostly large scale projects for the US Dept of Energy, IBM etc, and about 9,200 questions answered here since 2010. (1.7 percent failure rate)

.

I need the model number of the Mars motor you have in order to coach you on the install or any modifications needed.

What you have in place is a 3 phase DC motor, speed controlled by pulsing a 0 to 10v signal to the end bell of the motor that controls the pulse rate from the capacitors in the end bell, that pulse rate determines the speed of the motor (to be clear the 120 or 230vac power to the motor is converted to 3 phase DC inside the motors end bell.)

There are various other motors that can be wired to replace that variable speed motor, I need to see its wiring diagram to coach you on that transition

Lacking that, let me know and I can opt out. there are other very well qualified experts here who can look at your question and possibly answer without those details

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Phil the new fan is running fine. I have it hooked up and it works great. The computer on the board for the carrier furnace is looking for a signal that the fan is running. This signal used to come from the old fan motor that had for extra wires besides 120 volts ground and neutral. I want to bypass this feature on the furnace so it will run everything else is done here.
Customer reply replied 3 months ago
The furnace will run properly for a minute or two and then believes there is no fan running so it shuts down. If then tries again in 30 seconds and runs again for a few minutes and the same thing happens the error code says the fan isn't running. I want to bypass this feature with a dip switches or with configuring the wires that went to the old fan motor so that it believes that the fan is running
HVAC Technician: Phil, Mechanical Engineer replied 3 months ago

Thanks, ***** ***** opt out so that others here can see your question and get involved if they have that answer

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a carrier furnace with the LED light blinking 2-4, I
Hello,I have a carrier furnace with the LED light blinking 2-4, I have isolated the problem to the condenser but need help going forward … read more
Phil
Phil
Mechanical Engineer
7,426 satisfied customers
I have a new carrier furnace and a probabaly 20 year old
I have a new carrier furnace and a probabaly 20 year old conditioner. My air conditionar will not start with the the new thermostat and I have reset the circuit breaker and furnace. I'm wondering if t… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,892 satisfied customers
Carrier furnace is blinking 2 fast then 4 slow and the
carrier furnace is blinking 2 fast then 4 slow and the blower will not turn on … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Have a carrier furnace, the pilot light is on. The burners
Hi, have a carrier furnace, the pilot light is on. The burners used to come on & off on their own (not in response to the Thermostat). Then they stopped responding all together. … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,019 satisfied customers
Carrier furnace igniter doesn't spark. It was working but
It was working but today the electronic igniter doesn't spark … read more
Phil
Phil
Mechanical Engineer
7,426 satisfied customers
My carrier furnace model 395baw036060. There is a clicking
there is a clicking sound and the flame comes on but goes off and it keeps clicking… read more
Bill
Bill
Service Mgr
105 satisfied customers
I just replaced a 10 year old Carrier Furnace with a Lennox.
I just replaced a 10 year old Carrier Furnace with a Lennox. It is a 2 zone system (Carrier again). At the install we had to change out the zone control board and thermostats to be compatible with Len… read more
Bill
Bill
Service Mgr
105 satisfied customers
I have a Carrier furnace funace, and it's not blowing warm
Hi I have a Carrier furnace funace, and it's not blowing warm air … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Carrier furnace that is having issues. The t-stat
I have a Carrier furnace that is having issues. The t-stat calls for heat, inducer motor runs, for approx 30-60 seconds, then the surface igniter heats up and gas ignites. Then sometimes the last few … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Carrier furnace. Igniter comes on, but no flame. There was
Carrier furnace. Igniter comes on, but no flame. There was an electrical issue earlier today on the electric company's side of the meter. It has been repaired. Furnace was OK prior to that. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Carrier furnace rated at 1865 cfm was recently installed in
carrier furnace rated at 1865 cfm was recently installed in Jan 2018. Total cfm for all vents is 1056 cfm. heat distrbution for 16 vents ranges from 69 to 95 cfm. what could be the problem? Please adv… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Carrier furnace model 58CTA090-12114 that was
I have a Carrier furnace model 58CTA090-12114 that was installed in 2005,I am currently having an issue with it when it is called upon for heat, it will start the burner sequence with the ignitor glow… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
The ignitor to my Carrier furnace will not trigger so no
Hi Pearl. The ignitor to my Carrier furnace will not trigger so no heat can enter the house. I've manually reset the limit switch and cleaned the flame sensor and was looking for suggestions on what t… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My carrier furnace is not turning on. Thermidistat is blank.
My carrier furnace is not turning on. Thermidistat is blank. Error codes is 33. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My carrier furnace is not igniting, no error code. Last
My carrier furnace is not igniting, no error code. Last night it was glowing like it was trying to ignit, but it's not glowing anymore. … read more
Phil
Phil
Mechanical Engineer
7,426 satisfied customers
I have a 1983 Carrier furnace 294gaw00100. There is not
I have a 1983 Carrier furnace 294gaw00100. There is not pilot ignition. I've checked blower, theromstat, … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Getting a code 33 on my carrier furnace intermittently. And
getting a code 33 on my carrier furnace intermittently … read more
Phil
Phil
Mechanical Engineer
7,426 satisfied customers
My Carrier Furnace Model CNPVP4324ATAACAA says humidifier
My Carrier Furnace Model CNPVP4324ATAACAA says humidifier pad needs to be changed. Is that something easy to do? … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,892 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x