Would having an open window in a Canadian winter causing the heater to run almost constantly cause a furnace to open the Primary or secondary limit switch?
Show More
Show Less
Ask Your Own HVAC Question
Answered in 4 minutes by:
3/8/2018
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,122
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

Hello,

The issue here is the room gets infiltrated with cool air which makes the furnace run longer, but the cool air should also keep the discharge temp under control. Commonly plugged filters, too dense of the newer filters, blocked registers, restricted return air are the things that lead to overheat.

I have not found windows open leading to limit fail but to extended run.

Billy

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Ok. The filter isn't very dirty but it is pretty dense. I'll try a less dense one and check the rooms for blocked vents and see if that helps

In order for the limit to be tripped the discharge air from furnace would need to rise. Commonly only air blockages or lack of air can do this.

Many of the newer filters mimic a plugged filter as they are so dense.

Just rate service to move off the active list.

Thank you

BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,122
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
BillyHvac and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,122
23,122 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My furnace start wont turn on it says primary secondary
my furnace start wont turn on it says primary secondary limit switch open its a lennox … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,349 satisfied customers
I have a primary/secondary switch open code after about 30
I have a primary/secondary switch open code after about 30 min on Lenox SureLight G26Q3 furnace … read more
Rick
Rick
Supervisor
24,233 satisfied customers
What causes the condensate water to leak from inside the
What causes the condensate water to leak from inside the furnace? I cleaned the condensate trap.… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,948 satisfied customers
I have a lennox elite series furnace and the blinking light
I have a lennox elite series furnace and the blinking light indicators are saying: primary/secondary limit switch open. It will come on and run for about 1 or 2 minutes then shut off. I went to school… read more
Kcrand36
Kcrand36
Technician/Owner
Vocational, Technical or Trade School
72 satisfied customers
I have a Lennox G60UHV, the furnace will light and run for
I have a Lennox G60UHV, the furnace will light and run for a short time and kick off. It gives the fault Primary/secondary limit switch open Primary secondary or rollout switch open. Any help would be… read more
Rick
Rick
Supervisor
24,233 satisfied customers
Diagnostic lights are telling me primary/secondary limit switch
Diagnostic lights are telling me primary/secondary limit switch is open. Changed very dirty filter, turned power to furnace off for >1 hour. Turned everything back on, same code. Neither rollout sw… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
not getting heat. indicator light on left is slowly blinking
not getting heat. indicator light on left is slowly blinking and right light is on constantly. the diagnostic code says the primary/secondary limit switch open and then on (2stage models) primary or s… read more
warmneighbor
warmneighbor
owner
Vocational, Technical or Trade Scho
9 satisfied customers
I have a Lennov G40UH Furnace. The temperature in the house
I have a Lennov G40UH Furnace. The temperature in the house will not exceed 19 deg celcius with the thermostat set to 22 deg or even higher All the cycles run properly except for a point after about 4… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,122 satisfied customers
The primary/secondary limit switch open indicator light is
The primary/secondary limit switch open indicator light is blinking on my lennox furnace. Is there anything I can do to fix this problem or do should i call a repairman tomorrow?… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,216 satisfied customers
I have a Lennox G2603-75-3 that the blower is running constantly
I have a Lennox G2603-75-3 that the blower is running constantly but will not ignite. The Diag lights show that the Primary/ Secondary Limit Switch is open. How do I find the limit switch so I can res… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,122 satisfied customers
The furnance shows a slow flash (1) slow flash on (2) primary
The furnance shows a slow flash (1) slow flash on (2) primary secondary limit switch on..what or how can this be corrected..… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
Hello, The faul indication in my furnace indicates primary/Secondary
Hello, The faul indication in my furnace indicates primary/Secondary limit switch. In order to test those switches, can I just jump across the switches to test them and run the furnace without causing… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,038 satisfied customers
a customer of mine has an ancient, gigantic, natural gas furnace,
a customer of mine has an ancient, gigantic, natural gas furnace, it has no central air running through it just heat, so there are only two thermostat wires, and of course it has an old transformer 11… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,027 satisfied customers
I have a lennox G26 furnace. The fan runs and blows cold air.
I have a lennox G26 furnace. The fan runs and blows cold air. The LED indicator was the left light flashing slow and the right light was solid, this indication based on the info on the cover of the fu… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,349 satisfied customers
I have a Lennox G50UH-48C-110-02 furnace that is not making
I have a Lennox G50UH-48C-110-02 furnace that is not making heat this evening. LEDs are slow flash/ON meaning primary/secondary limit switch open. What do I do to fix this… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,349 satisfied customers
My Lennox furnace will kick on and run for a while but then
My Lennox furnace will kick on and run for a while but then shuts off. The signaling LEDs say that the primary/secondary limit switch is open. What can cause this? I see it shut off, the fan keeps run… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,349 satisfied customers
My furnace is indicating that the primary/secondary limit switch
My furnace is indicating that the primary/secondary limit switch is open. As a result, it is not blowing warm air during it's cycle and the ignition switch has not automatically lit the burner. Is the… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,216 satisfied customers
Why is the indoor blower and the inducer motor on my gas pack
Why is the indoor blower and the inducer motor on my gas pack running all the time? I've unhooked the wires coming from the thermostat and put power back on the unit and the blower and the inducer mot… read more
Jim Eastwood
Jim Eastwood
Lead service
High School or GED
100 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x