I have a rheem 80 super quiet furnace and noticed that there…

I have a rheem...

I have a rheem 80 super quiet furnace and noticed that there was no heat this morning .this has happened before and they replaced the flame sensor.

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

I cleaned the flame sensor with steel wool, but it shut down again. Also there are 2 green lights when the furnace is properly working. now the left one blinks and you have to turn off and on again for it to run. I believe there is another type sensor on the left side of this furnace they cleaned?? Can you help.

Contractor's Assistant: Do you plan on doing the work yourself?

Yes I do. I am not happy with the company that sold me this unit.

Contractor's Assistant: Anything else we should know to help you best?

Can it be I did not clean the flame sensor properly?? I think I did . I do have a spare that looks clean, but I can not remember the name of that other sensor that I saw the repair man take out.

Show More
Show Less
Ask Your Own HVAC Question
Answered in 42 minutes by:
3/8/2018
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,408
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your

issue. First I’ll need some more info so I have a more complete picture of your situation.

How many times does the LED blink before it pauses and repeats?

Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,408
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified
Rick and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 4 months ago
right now the unit is not running the right led is on, but the one next to it is constantly blinking. when this furnace is running properly bot lights stay solid green all the time. if i shut the unit off the unit will kick on and there will be heat for a shoirt time before it shuts down again.
Phone call session started
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Rick Your Own Question
Rick
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,408
24,408 Satisfied Customers
Experience: 40+ yrs. experience as a licensed oil & gas technician.

Rick is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Rheem super quiet 80, and the igniter flames don't
I have a Rheem super quiet 80, and the igniter flames don't stay lit … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have Rheem Classic Services Super Quiet 80 that is cycling
I have Rheem Classic Services Super Quiet 80 that is cycling on and off. I have two green lights on. The third light is yellow or amber. It comes on briefly and I have flame for a few seconds. The lig… read more
Rick
Rick
HVAC Supervisor
24,408 satisfied customers
Having a problem with my unit not blowing hot air. All
Having a problem with my unit not blowing hot air JA: Did you double-check the thermostat's settings? And what about the filters? Customer: all checked JA: Do you plan on doing the work yourself? Cust… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Furnace draft blower comes on, the ignition happens, then
Furnace draft blower comes on, the ignition happens, then full flame for about 2-3 seconds then goes out. Immediately after the burned hoes out the circulation fan comes on even though there is no hea… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Rheem super quiet 80 furnace, burner lights and then goes
Rheem super quiet 80 furnace, burner lights and then goes out within A FEW SECONDS. pROBLEM … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I'm having a problem with my Rheem criterion furnace
Hello, I'm having a problem with my Rheem criterion furnace again. I looked for the flashing light indicator, this time when I turn it on, every time the burners ignite, there is a flashing orange lig… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
I'm having the same issue with my furnace it lights up for
I'm having the same issue with my furnace it lights up for 15 seconds and then when the fan comes on the flame goes out… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Hi guys. I have a Rheem Classic Series- Super Quiet 80. I
Hi guys. I have a Rheem Classic Series- Super Quiet 80. I just had to reset the furnace -twice- by shutting off the furnace service switch, waiting, then turning it back on. After the 2nd power up, it… read more
Rick
Rick
HVAC Supervisor
24,408 satisfied customers
I have a Bryant Plus 80 furnace. Getting error code 34. I took
I have a Bryant Plus 80 furnace. Getting error code 34. I took the covers off and pressed the safety switch. After a few seconds the ignitor glows and the gas lights and the fan blows. After 3 seconds… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
have a rheem furnace.... 3 lights in the window. left yellow,
have a rheem furnace.... 3 lights in the window. left yellow, middle and right are green. when not on, left light off, right green on, middle green blinking. when i turn up thermostat, the furnace com… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My Ruud achiever series super quiet 80 gas furnaces ignites
My Ruud achiever series super quiet 80 gas furnaces ignites for about 5 seconds and then the flame goes out, the fan continues, and not heat is produced… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Rheem classic 90 plus furnace with a direct spark.
I have a Rheem classic 90 plus furnace with a direct spark. It won't stay on, although the flame goes on briefly. From the question below, it seems I should check to make sure the PVC vent is clear. I… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
i noticed that my lennox furnace was not running. i went to
i noticed that my lennox furnace was not running. i went to look at it and the green led lights on the bottom section were not blinking simultaniously they were alternating. when i flipped the breaker… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I have a rheem classic 80 quiet series furnace. It does not
I have a rheem classic 80 quiet series furnace. It does not stay on to raise temp to desired setting, it will turn-on for a couple minutes and then turn off. It will continue this indefinitely. In the… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
Rheem Classic Super Quiet 80 - RGPN - Burner shuts off after
Rheem Classic Super Quiet 80 - RGPN - Burner shuts off after a few seconds - only blows cold air.… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
i have a rudd series 80 why as soon as the the blowers kick
i have a rudd series 80 why as soon as the the blowers kick in the gas shuts off instantly not heating the house… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
super quiet 80 gas furnace, no heat, blower runs, when reset
super quiet 80 gas furnace, no heat, blower runs, when reset breaker, flame comes on then goes out… read more
JBM HVAC
JBM HVAC
HVAC/R Technician
Vocational, Technical or Trade Scho
50 satisfied customers
I have an Amana air command 80 GCI Furnace. The ignitor comes
I have an Amana air command 80 GCI Furnace. The ignitor comes on but the furnace will not fire. The diagnostic light blinks continually. According to the trouble shooting tips with my furnace it tells… read more
Mario
Mario
Owner Of At Your Service Plumbing & Heat
High School or GED
672 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x