NUGE075DH01. The flames on my furnace will start, but then…

Customer Question
Hi My name is*****...

Hi My name is*****: I'll do all I can to help. How long have you been dealing with this?

The flames on my furnace will start, but then they go out before the blower comes on, the process repeats itself continually

Contractor's Assistant: Do you have fuel in the tank? If so, is the shut-off valve open and the fuel clean?

This is using natural gas via pipeline

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

I have a 52 second video showing this sequence I can send you

Submitted: 4 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 4 months ago
Posted by JustAnswer at customer's request) Hello. I would like to request the following Expert Service(s) from you: Live Phone Call.
Customer reply replied 4 months ago
Let me know if you need more information, or send me the service offer(s) so we can proceed.
Answered in 2 hours by:
3/8/2018
HVAC Technician: Chris Wagner,
 replied 4 months ago
Chris Wagner
Category: HVAC
Satisfied Customers: 27
Experience: Phone Consultant at Fixya
Verified

Hi, my name is ***** ***** I'll be assisting you with your question regarding your Furnace. I apologize for the extended wait time you experienced, I've only just come online now and would like to assist you with your question. How long does the unit run for before the system cuts out?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
About 20 seconds, then the green light flashes re-ignite the furnace jets for 20 seconds again , then shutdown and restart process runs endlessly
HVAC Technician: Chris Wagner,
 replied 4 months ago

Ok, the order of operation tells us several things. 1. Safeties are not tripped ( currently ), 2. The Inducer is running 3. Pilot/Igniter is activating. 4. Gas valve is turning on. While the run time is slightly longer than I would expect. I would check the Flame sensor first. As they get dirty they do not allow the board to sense the flame well

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Ok, do you happen to know the part number for that?
HVAC Technician: Chris Wagner,
 replied 4 months ago

Unfortunately I am unable to pull up a parts list for that unit. You would have to contact your local supply house. Fortunately, they are all pretty much the same with exception of shape. Should look similar to the included picture. I would first try to remove it and clean it up. Might still be fine, just dirty.

Ask Your Own HVAC Question
HVAC Technician: Chris Wagner,
 replied 4 months ago

Found a part list, yours is actually a pilot assembly. The Flame sensor is built into the pilot. If you can get to it you can try to clean in place. If not the part number is(###) ###-####/p>

https://www.searspartsdirect.com/model-number/NUGE075DH01/0492/0912100.html?blt=06&prst=&shdMod=NUGE075DH01

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Great thanks, ***** ***** with sears, but they don’t have it in stock . May try eleswhere
HVAC Technician: Chris Wagner,
 replied 4 months ago
Anytime. Glad i could assist. Did you try to clean it? Might get you through till you get a new one
Ask Your Own HVAC Question
Customer reply replied 4 months ago
I found other suppliers, may buy one but try cleaning the old one first, they are only around 26 dollars I guess
HVAC Technician: Chris Wagner,
 replied 4 months ago
fairly cheap parts. Got a love a cheap easy fix.
Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Chris Wagner Your Own Question
Chris Wagner
Chris Wagner
Chris Wagner
Category: HVAC
Satisfied Customers: 27
27 Satisfied Customers
Experience: Phone Consultant at Fixya

Chris Wagner is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I cleaned the flame rod but the furnace will start and flame
I cleaned the flame rod but the furnace will start and flame quits when fan starts. … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have an old G12Q110 Dual function A/C unit. The Blower
I have an old G12Q110 Dual function A/C unit. The Blower motor died I have purchased the appropriate replacement 1/3 hp by Dayton. I need wiring schematic to hook up the new motor. I found some useful… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Lennox Elite Series furnace that is about 16 years
I have a Lennox Elite Series furnace that is about 16 years old. The blower fan will not turn off. Is there a service tech I could talk too? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have G40UH(X) furnace. Heater is running for 5 to 6
heater is running for 5 to 6 minutes then stops flaming after 5 to 6mins and red led slow flash and green led on … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Furnace will automatically restart when tempers urethane
Furnace will nut automatically restart when tempers urethane drops? … read more
Chad DeYoung
Chad DeYoung
11 satisfied customers
I have York furnace starts shuts off after 1 minute I
I have York furnace starts shuts off after 1 minute I replaced fame sensor did not help … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Furnace stopped heating and blower remains on and will not
Furnace stopped heating and blower remains on and will not turn off by it self. Replaced thermostat and limit switch next to burner. Any idea? Is there a reset button… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Furnace is not running. Flame is on for few seconds, but no
Furnace is not running. Flame is on for few seconds, but no fire. The furnace will do that for three times, then it will shutdown. The red light blinks continuously. Furnace is comfortmaker model# : G… read more
HvacmanSean
HvacmanSean
Owner
HVAC
233 satisfied customers
I have a Rheem RDGD furnace. The flame led lights steady and
I have a Rheem RDGD furnace. The flame led lights steady and burners burn until main blower turns on. Then flame led starts blinking, and sometimes the furnace will shut down and then restart. I have … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,944 satisfied customers
The inducer motor comes on ignitor comes on burners light,
OK, the inducer motor comes on ignitor comes on burners light, then go back out … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have York model FG8B07512MU11A heating furnace. Red Led is
changed the filter, flame comes blower not turning on… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Are furnace seems to have stopped working. In the upper
Hello, Are furnace seems to have stopped working. In the upper compartment 1 in circular window there is no flame visible. Is the pilot flame out?… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Talked this morning but did not have time to trouble shoot,
Customer: Talked this morning but did not have time to trouble shoot, my furnace is blowing cold air … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a heil dc90 furnance and need to replace the blower
i have a heil dc90 furnance and need to replace the blower fan blades. how does that unit come out of the furnace?… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have a house furnace. I was changing out the swamp cooler,
I have a house furnace. I was changing out the swamp cooler, lit up the friedrich house furnace ok, but I don't know which air vent panels to remove above the furnance. there are two, one small and ab… read more
Heath.M
Heath.M
Refrigeration Mechanic
Vocational, Technical or Trade School
223 satisfied customers
I have a Trane Gas Furnace XE 60. The blower does not come
I have a Trane Gas Furnace XE 60. The blower does not come on when the thermostat is set to auto on when it is set to on. Once on the blower motor clicks on and off constantly but the furnace does not… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
All of a sudden both of my Venstar thermostats both stopped
All of a sudden both of my Venstar thermostats both stopped working. Tried to reconnect to wifi but it does not accept the WIFI connection. Help ?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Ruud Super Achiever Quiet 80 in my attic that isn't
I have a Ruud Super Achiever Quiet 80 in my attic that isn't working properly. The fan comes on when I turn the thermostat to ON but will not turn on by itself even when the temp is WAY below what I h… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x