I have an innovator series mod g32q3 that when heat is

I have an innovator...

I have an innovator series mod g32q3 that when heat is called for the exhaust fan starts, you hear a click, then it stops. it has the right light flashing slow (pressure switch open or open rollout switch circuit)

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Yes fresh filter

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Show More
Show Less
Ask Your Own HVAC Question
Answered in 4 minutes by:
3/7/2018
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 23,799
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your

issue. First I’ll need some more info so I have a more complete picture of your situation.

What is the other LED doing? how long after the exhaust fan starts up before it shuts down?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
the other led is off. it only takes about a second before you hear the click then the fan shuts down
Customer reply replied 1 month ago
keep typing
Customer reply replied 1 month ago
waiting for an answer

Try jumping the R & W terminals on the furnace thermostat terminal strip. Then power it back up. Any change?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
No

Then you probably have a bad board.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
What does it look like. Where is it located

The thermostat terminal strip is on the board

Ask Your Own HVAC Question
Customer reply replied 1 month ago
K Thanks

You're welcome

Ask Your Own HVAC Question
Customer reply replied 1 month ago
How do you know that it's not the rollout switch?

You have to reset a rollout for the unit to start up and the unit would not start up if a rollout was tripped.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
What about the pressure switch?

Draft fan should run a lot longer than 1 second before it shuts down if it was an open draft switch. If the draft switch was stuck closed the fan should not run

Ask Your Own HVAC Question
Customer reply replied 1 month ago
K had to check. 280 for the part. Thanks

My pleasure

Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 23,799
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified
Rick and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?
Ask Rick Your Own Question
Rick
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 23,799
23,799 Satisfied Customers
Experience: 40+ yrs. experience as a licensed oil & gas technician.

Rick is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
AN OLD HONEYWELL MERCURY THERMOSTAT WITH A 1F80-0471 RODGERS
I AM REPLACING AN OLD HONEYWELL MERCURY THERMOSTAT WITH A 1F80-0471 WHITE RODGERS PROGRAMABLE THERMOSTAT. 4 WIRES COMING OUT OF WALL, W,G,Y, R. NEW THERMOSTAT HAS RC JUMPED WITH RH. CANT ADD RED TO TH… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
My son removed his old mercury thermostat without taking a
My son removed his old mercury thermostat without taking a picture of the wiring. He is trying to replace his old thermostat for a new digital one. What can we do to determine what each colored wire r… read more
Rick
Rick
HVAC Supervisor
23,799 satisfied customers
My water furnace thermostat is saying call service
My water furnace thermostat is saying call service technician and then under that it says system on heat pump plus two is flashing what does that mean we have no heat in our house … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
My heater is not working. The flame icon is flashing,
Hi. My heater is not working. The flame icon is flashing, indicating it's trying to turn the heater on but I hear no clicking sound for the furnace pilot and no heated air is coming through. All wires… read more
Rick
Rick
HVAC Supervisor
23,799 satisfied customers
We just bought the Honeywell RTH 6360. We, unfortunately,
We just bought the Honeywell RTH 6360. We, unfortunately, did not mark where the wires went on our old thermostat. Our furnace is a Bryant 90i. We have 4 wires coming out of the wall and we do not kno… read more
Rick
Rick
HVAC Supervisor
23,799 satisfied customers
Damper stuck closed. How can I remove cover? A couple week -
a couple week - had service out on 1/30 said damper working fine, just stuck … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I am installing zone valves and can find no wiring diagram
I am installing zone valves and can find no wiring diagram for my very old Aquastat relay type L8048a … read more
Rick
Rick
HVAC Supervisor
23,799 satisfied customers
I have a rheem classic 90 plus that has no heat, no fan
I have a rheem classic 90 plus that has no heat, no fan blowing for heat or air. The diagnostic leds are as follows flame=not lit, the next one=constant green, the next one=constant green. I have chan… read more
Rick
Rick
HVAC Supervisor
23,799 satisfied customers
It seems that one of my TACO zone valve is stuck closed. I
It seems that one of my TACO zone valve is stuck closed. I tried to open it manually by pushing the manual lever up (toward the pipe) all the way, but nothing is flowing. The other zone valve is fine … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Trying to rewire a thermostat rth6350. What happened is a
what happened is a friend of mine disconnected the wires and doesn't remember where the wires go … read more
Rick
Rick
HVAC Supervisor
23,799 satisfied customers
York diamond 80. I just bought this house as a rental and
York diamond 80. I just bought this house as a rental and when I turn on the furnace I get 5 short blinks. I go to the flame rollout switch and see it was removed by the previous owner. I then connect… read more
Rick
Rick
HVAC Supervisor
23,799 satisfied customers
Rick, The thermostat terminals on the ZVC404 Zone Valve
Hi Rick,The thermostat terminals on the ZVC404 Zone Valve Control are marked as 24 VAC. Does this mean that when the terminals on the thermostat are closed, the circuit is completed and energized with… read more
Rick
Rick
HVAC Supervisor
23,799 satisfied customers
My honeywell thermostat dose not have a rh inlet only an r.
my honeywell thermostat dose not have a rh inlet only an r … read more
Rick
Rick
HVAC Supervisor
23,799 satisfied customers
I believe we have a flap that is stuck closed on our unit.
I believe we have a flap that is stuck closed on our unit. We are having the same problems we had a few months back, with lonely a small amount of warm air blowing through out system. We tried switchi… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Ruud furnace. error code says pressure switch stuck closed
ruud furnace. error code says pressure switch stuck closed (4 blinks). I was trying to find out where that switch is. We have had high winds and at least one note suggested that might have tripped the… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Need battery for - Rodgers 1970s furnace thermostat. Battery
Need battery for White - Rodgers 1970s furnace thermostat. Battery Replacement W.R Part no.(###) ###-#### 44-4868. Have tried Specialty Battery stores to no avail.… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Forced air NG furnace...thermostat replaced (yesterday) and
Forced air NG furnace...thermostat replaced (yesterday) and now blower fan comes on BEFORE furnace burner ignites??? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
No power to flame rollout switch on gas furnace. Thermostat
no power to flame rollout switch on Bryant gas furnace … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x