I noticed that the fan was running continuously and only…

Customer Question
I noticed that the...

I noticed that the fan was running continuously and only providing cold air. LED flashed code 33. Checked and replaced filter. It still looked fine. No help. We’ve been out of the house for about 36 hours but furnace had been working properly prior. Started running thru possible problems. Everything was fine until I checked the fresh outside air intake

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

I removed the ductwork to intake and found a recently dead squirrel. Removed it and replaced ductwork. Flipped off the breaker and back on a while later. For the past 5 hours it’s been only cold air and no ignition. Code 33 still flashing. Yes thermostat good. Yes new filter.

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

Need it done now

Submitted: 4 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 50 minutes by:
3/7/2018
HVAC Technician: airheatman, HVAC Technician replied 4 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,175
Experience: Furnace, A/C and heat pump specialist.
Verified

The 33 flash code is an open high temp limit error.
There may be
several limits on the furnace.Below describes locations:
PRI***** *****MIT
The pri***** *****mit control is located on the partition panel and monitors
heat exchanger compartment temperatures. It is a normally closed
(electrically), automatic reset, temperature-activated sensor.
The limit guards against the overheating as a result of insufficient
conditioned air passing over the heat exchanger.
AUXILIARY LIMIT
The auxiliary limit control(s) are located on or near the circulator
blower and monitors heat exchanger compartment temperatures.
They are a normally-closed (electrically), manual-reset, temperature
activated sensors. These limits guard against overheating as a
result of insufficient conditioned air passing over the heat exchanger.
VENT DRAFGAURD
These would be located on the draft hood if you have one on your furnace.
ROLLOUT LIMIT
The rollout limit controls are mounted on the burner/manifold assembly
and monitor the burner flame. They are normally-closed
(electrically), manual-reset, temperature-activated sensors. These
limits guard against burner flames not being properly drawn into the
heat exchanger.
Lets start with the most simple and easy. Look near burners for limits with a little button in center.It will push in to reset.If none are tripped we will go from here. Let me know if you have a multi meter for troubleshooting.
http://i.imgur.com/CGkB9sa.jpg

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Recently we've been having some issues with our furnace. It
Good afternoon, recently we've been having some issues with our furnace. It will run its full cycle until it reaches temp and shut off as normal. However, it won't kick back on until we turn the therm… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,942 satisfied customers
I have a furnace model 350MAV. The main blower motor runs
I have a Bryant furnace model 350MAV. The main blower motor runs but the furnace does not get a call for heat, the igniter does not glow. The hot surface ignition pilot does not heat up. I cleaned the… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Trane furnace #TUH2C100A9V4VAC 2 stage. After it
I have a Trane furnace #TUH2C100A9V4VAC 2 stage. After it satisfies the thermostat and shuts down, at random times it will not restart. The fan continues to blow cold air. If I shut off power for a fe… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I get a code 33 on a Bryanr MAV 350MAV. I reset the temp
I get a code 33 on a Bryanr MAV 350MAV. I reset the temp reset button. It runs for 5 minutes and shuts off again. The intake pipe pups out. … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
My name is***** have a Rheem Classic 90 Plus natural
My name is***** have a Rheem Classic 90 Plus natural gas furnace. It has three lights on the control board. 2 green and one orange. One green is for power, the second says ready also green and the ora… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
my furnace keeps shutting off. I press the reset button, it
my furnace keeps shutting off. I press the reset button, it comes on then reaches the set temp goes off, then wont come back on until I hit the reset button again.… read more
theplumber717
theplumber717
Plumber
Vocational, Technical or Trade Scho
791 satisfied customers
I have a Lennox G32Q-3/4-100-2 forced hot-air house heater
I have a Lennox G32Q-3/4-100-2 forced hot-air house heater firing off of natural gas. Everything is fine except the main blower (that circulates the air through-out the house) is making a minor vibrat… read more
airheatman
airheatman
HVAC Technician
9,175 satisfied customers
During operation the unit turns off. Diagnostic description
During operation the unit turns off. Diagnostic description refers to the Open Limit Switch Fault; Green LED - Flash, Red LED- Off.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hello, I am having trouble with my furnace. It is a Payne
Hello, I am having trouble with my furnace. It is a Payne Model PGMAA. It's a forced hot air, but is blowing cold air. It is flashing error code 33, then after 5 minutes changes to 31. I have tried to… read more
airheatman
airheatman
HVAC Technician
9,175 satisfied customers
1. I have Carrier WeatherMaker 8000 gas furnace, which does
1. I have Carrier WeatherMaker 8000 gas furnace, which does not have a pilot. The furnace was working until last night. This morning it is dead. My desired temperature on the thermostat is 75 but the … read more
airheatman
airheatman
HVAC Technician
9,175 satisfied customers
I have a model 58ta hot air furnace. The vent motor will not
I have a model 58ta hot air furnace. The vent motor will not start, the blower motor is running, thermostat call for heat. The led code seems to to be 3 long 3 short blinks… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
I have a Model 350MAV furnace and am getting a fault code of
I have a Model 350MAV furnace and am getting a fault code of 23. What does this signal and how do I fix it?… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
carrier model 58stx090. error code 33 and or 13... i reset
carrier model 58stx090. error code 33 and or 13... i reset from the breaker, changed the filter, and set it to 70 - not blowing particularly hot air - has been on now for several hours, led still flas… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
I have a bryant plus 80 model 395CAV024070. It has had a few
I have a bryant plus 80 model 395CAV024070. It has had a few problems in the past with the flame sensor, that was fixed with some steel wool. Now it is turning on but then shutting itself off after a … read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I recently purchased a foreclosed home that had been vacant
I recently purchased a foreclosed home that had been vacant for over a year. About 3 months prior to my purchasing the home, the bank that owned it started paying the electriciy bill to make the home … read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Have spoken to M Ogalsbee (sp ) about our heater. Had to sign
Have spoken to M Ogalsbee (sp?) about our heater. Had to sign off before we resolved it. It is a carrier 58 STA/STX. The problem seems to be intermitant. Everything triggers fine but there is no flame… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have a Payne PG 8MAA048110 furnace which flashes an LED code
I have a Payne PG 8MAA048110 furnace which flashes an LED code of 33. I purchased a spare limit and flame roll out switch for backup a few years ago. I replaced the flame roll out switch and still had… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
Hi I have a goodman heating & Air Condition Unit with a approx.
Hi I have a goodman heating & Air Condition Unit with a approx. 15 yr old 4 zone carrier thermostats. Have not be able to find a carrier dealer in Hartsville, SC that can solve my thermostats problem … read more
Rick or Nick in Texas
Rick or Nick in Texas
General Manager-Lead Tech
Own and run HVAC business 29yrs
44 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x