Gibson KG7SC090D35C 92% afue upflow natural gas furnace.

Gibson KG7SC090D35C 92% afue...

Gibson KG7SC090D35C 92% afue upflow natural gas furnace. Furnace running normal heat cycle. Flame in burner goes out, fan runs constantly. Temporary solution reset flame roll out switch. Then furnace runs til switch kicks out again. To keep house warm took roll out switch out and put in jumper wire Is is safe to leave jumper wire? Presume week roll out switch/replace with same?

Contractor's Assistant: Have you tried power cycling the appliance -- unplugging it and leaving it off for a few hours?

No, Are you saying it is a computer board relearn issue?

Contractor's Assistant: Do you plan on doing the work yourself?

Yes, if possible

Contractor's Assistant: Anything else we should know to help you best?

Nothing additional to original explanation

Show More
Show Less
Ask Your Own HVAC Question
Answered in 3 minutes by:
3/4/2018
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,154
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

Hello,

This is actually pretty dangerous. The roll out switch is one of the more important switches on this furnace.

This means the heat is being being washed backwards due to an obstruction or bad heat exchanger.

Bypassing this swiutch can lead to melted parts, possible fire and carbon monoxide. The reason they make this a push button is draw attention to it...unlike autoreset switches elsewhere.

I do not know what the failure is that is tripping the switch...BUT please have it checked and do not bypass.

Billy

Ask Your Own HVAC Question
Customer reply replied 5 months ago
We will put switch back in. We will start with new flame rollout switch. Thank you.

Thank you,

Just rate service to close for now. If new switch trips have heat exchanger inspected.

The rating system is at top of page.

Thank you,

Billy

BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,154
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
BillyHvac and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,154
23,154 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Gibson GL1RA that has been cycling. I cleaned the
I have a Gibson GL1RA that has been cycling. I cleaned the flame sensor and replaced the board without fixing the problem. I'm guessing the problem is the roll out switch or the sense that is checking… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
A hot air Gibson furnace that was install last year is now
A hot air Gibson furnace that was install last year is now tripping roll-out switches. Is the gas pressure to high?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
During operation the unit turns off. Diagnostic description
During operation the unit turns off. Diagnostic description refers to the Open Limit Switch Fault; Green LED - Flash, Red LED- Off.… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,154 satisfied customers
it is is 43 below zero outside, my furnance is set at 72 degrees,
it is is 43 below zero outside, my furnance is set at 72 degrees, but does not get warmer than 60 degrees in the house. Is it the cold outside temperatures or is there something wrong with my thermost… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Carrier 8000TS. It is not staying on to warm house
I have a Carrier 8000TS. It is not staying on to warm house up. I did some research, cleaned the sensor, and the error code changed from 14 to 33. I read what it said to do, but cant find the flame ro… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,154 satisfied customers
i am having a problem with my furnace. it blinks 12 but when
i am having a problem with my furnace. it blinks 12 but when test wire it blinks rapidly and the code says reverse polarity. this is a new board. jumped all the flame blow outs… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,154 satisfied customers
i have a trane xe90 furnace that fails to light...ive replaced
i have a trane xe90 furnace that fails to light...i've replaced igniter and and the circuit board but it still fails to ignite. blower comes on before igniter can light....I'm getting 5 blinking light… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,154 satisfied customers
i have a upflow/horizontal gas furnace.it lighit off and fire
i have a upflow/horizontal gas furnace.it lighit off and fire for maby 20 min. but flame goes out with the fan running i cac reset roll out switch and it will light off but again flame out please help… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
i have a carrier model 58sxc upflow furnace. the burner shuts
i have a carrier model 58sxc upflow furnace. the burner shuts off before it reaches thermostat temp. it immediatly restarts and runs until temp is reached. i have replaced inducer motor,circuit board,… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
I have a Bryant 395 cav upflow furnace. (10 yrs old) It showed
I have a Bryant 395 cav upflow furnace. (10 yrs old) It showed a code 33, I had a service tech out and he told me that the circuit board needed to be replaced, after troubleshooting the pressure senso… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,154 satisfied customers
My Bryant gas furnace came on and I smelled a very strong gas
My Bryant gas furnace came on and I smelled a very strong gas odor. I turned the thermostat lower than the room temperature so it would stop running. The pilot light is lit but the burners will no lon… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
furnace gas valve will not open.Hot surface ignotor lights,
furnace gas valve will not open.Hot surface ignotor lights, Can here click for solenoid, no 24v. Replaced board, gas valve, hot surface ignitor, flame sensor and tstat.We disconnect re and white wire … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,154 satisfied customers
Carrier 58sta/stx 6 years old. found code 33. starts up fine.
Carrier 58sta/stx 6 years old. found code 33. starts up fine. inducer and flame kick off and blow runs for 2-3 minutes and then it starts rigth back up. had stupid tech come out and he cleaned the fla… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Our main floor furnance does not ignite! (Coleman upflow natural
Our main floor furnance does not ignite! (Coleman upflow natural gas furnace Model G9T10020UPC13C) We have a second furnace exactly the same for the basement which we don't need running right now-can … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
i have a rudd series 80 why as soon as the the blowers kick
i have a rudd series 80 why as soon as the the blowers kick in the gas shuts off instantly not heating the house… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
Dear Bryant and team- I have a 383KAV Upflow furnace, and
Dear Bryant and team- I have a 383KAV Upflow furnace, and I accidentally blew out the pilot light on the water tank with a fan. Therefore, I temporary shut off the gas line which supplies both the fur… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
My comfortmaker furnace wont stay running. The flame comes
My comfortmaker furnace won't stay running. The flame comes on but it looks like the main flame is not going into the burner tube very well. The flame seems to be outside of the tube and there is a hi… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,154 satisfied customers
I have a Goodman model GMP050-3 Gas Furnace. The igniniter
I have a Goodman model GMP050-3 Gas Furnace. The igniniter works the gas comes on. I see it blowing through the burners. Though at the vents there is only cool to mildly warm air???… read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x