WEil McLain oil Boiler Beckett burner will just shut down no…

WEil McLain oil Boiler...

WEil McLain oil Boiler Beckett burner will just shut down no lights on controller. If I shut down power & power back up it usually runs fine again. New fuel pump, filter, nozzle.

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

About 6 weeks, it will run fine for up to a week then trouble again

Contractor's Assistant: Do you plan on doing the work yourself?

To the extent that i can

Contractor's Assistant: Anything else we should know to help you best?

Today, and only today the motor started for about 1 sec then shut down, but then ran fine after that

Show More
Show Less
Ask Your Own HVAC Question
Answered in 4 minutes by:
3/2/2018
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,378
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. If my initial response doesn’t answer your question then let me know and we can continue our conversation.

Since the ignition control isn't locking out you need to look at the aqustat/relay and what's signaling a call for heat. If you only have 1 zone that would be the thermostat or thermostat wiring. If you have multiple zones then that would be the zone valves or pump relay(s).

Ask Your Own HVAC Question
Customer reply replied 4 months ago
i have pump relays but problem doesn't seem to correspond to any particular zone

Since the problem is intermittent it will be difficult to pin down but if you have multiple relays it's more likely this is an operating control (aquastat/relay). There's also a chance the ignition control could be faulty. First thing to do is check all your connections. Keep in mind that 18 gauge wire is notorious for partially breaking unnoticed. Ideally you'd monitor voltage at B1 & B2 on the operating control for a voltage drop/loss. Best to do this with the T terminals jumped. If have 120 vac at B1 & B2 and no burner function and no lockout then the ignition control is suspect.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
I'm not extpert , but I assume t = Thermostat, but what do you mean by ignition control?

Yes the T terminals are the "thermostat" terminals but in your case the relay end switches would be connected to them. They are labeled T on virtually all operating controls. Ignition control is the control on the burner with the reset button.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
if it is aquastat/relay wouldn't boiler still lock out eventually or no

You never mentioned a lock out which would require hitting the rest button to restart the burner

Ask Your Own HVAC Question
Customer reply replied 4 months ago
I'm sorry wasn't thinking clearly. The answer is, If the relay doesn't work then the whole process never begins, correct?

Far from the only possibility. The sequence could start then the voltage drops out due to a defect.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
But once process started I wouldn't get locked out?

I just answered this question. The sequence could start then the voltage drops out due to a defect. Again it's not a lock out unless you have to hit the reset button.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
sorry, I knew I wasn't locked out. I just thought that if the process got past the relay that the controller would lock out but I guess I was wrong, my bad

The thing is, intermittent problems are notoriously difficult to diagnose. You can only diagnose when it doesn't work. So next time it goes down you'll need to do the voltage testing I outlined earlier.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
OK, thank you

You're welcome

Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,378
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified
Rick and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Rick Your Own Question
Rick
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,378
24,378 Satisfied Customers
Experience: 40+ yrs. experience as a licensed oil & gas technician.

Rick is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Weil Mclain (CP5470602) boiler which heats our domestic
I have a Weil Mclain (CP5470602) boiler which heats our domestic hot water through an indirect fired water heater. In the past 2 weeks, has shut down, though the circulating pump is running. I called … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Weil-mclain afg gold oil boiler fires then spits and sputters
weil-mclain afg gold oil boiler fires then spits and sputters and shuts down new nozzle and new filter pump was blead before starting it acts as if running out of fuel… read more
Rick
Rick
HVAC Supervisor
24,378 satisfied customers
I have Weil-McLain Gold oil burner WTGO-3. Yesterday boiler
I have Weil-McLain Gold oil burner WTGO-3. Yesterday boiler stopped. When I tried to restart it, flame starts and goes off after ~30 sec. Flame is normal yellow color. Restart safety switch on burner … read more
Rick
Rick
HVAC Supervisor
24,378 satisfied customers
I have a weil mclain gold furnace ,ten yrs old always serviced
I have a weil mclain gold furnace ,ten yrs old always serviced annually,, sometimes now it will totally shut down, and not come back on, has to be restarted, last time service guy came out, he said yo… read more
Rick
Rick
HVAC Supervisor
24,378 satisfied customers
Im looking for a HVAC answer. I have a Weil-McLain gold oil
I'm looking for a HVAC answer. I have a Weil-McLain gold oil boiler. I changed oil filter on the tank, changed nozzle on boiler. I am getting fuel through the line, the motor spins but I'm not getting… read more
Rick
Rick
HVAC Supervisor
24,378 satisfied customers
I have a weil mclain ultra oil burner model #uo-5 with a beckett
I have a weil mclain ultra oil burner model #uo-5 with a beckett motor. (primary control #R7184P) This unit is approx 7 years old Every 1 to 3 months it shuts down ,even after new filters, nozzle and … read more
Rick
Rick
HVAC Supervisor
24,378 satisfied customers
I am having trouble with a Lennox oil burner. It has a Beckett
I am having trouble with a Lennox oil burner. It has a Beckett AFII 85 burner. It has been working intermittently for the past couple of days. Due to the holiday my availability of parts is very limit… read more
Rick
Rick
HVAC Supervisor
24,378 satisfied customers
Have a ThermoPride oil fired hot air furnace w/ Beckett R7184B
Have a ThermoPride oil fired hot air furnace w/ Beckett R7184B controller, one pipe feed: Will heat fine for 5 hours, shuts off, will not restart upon controller reset. Indicator light is off--never i… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have a Weil Mclean Boiler with a Becket AG2 gun. I has developed
I have a Weil Mclean Boiler with a Becket AG2 gun. I has developed a miss when it runs about every five second. I had it tuned up three months ago and again this week. Techs chnanged nozzle and cuplin… read more
Rick
Rick
HVAC Supervisor
24,378 satisfied customers
I have a weil mclain boiler with a beckett burner,its 20 yrs
I have a weil mclain boiler with a beckett burner,its 20 yrs old,been running fine,came home today circulator running,burner not running… read more
Rick
Rick
HVAC Supervisor
24,378 satisfied customers
have a beckett burner w/an R7184 primary...its locked out
have a beckett burner w/an R7184 primary...it's locked out w/ a flashing GREEN light (approx 1/2 sec apart)...burner won't reset...i shut power to burner for 15 minutes hoping it would reset...no luck… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Just turned oil boiler on for first time this year. Came on
Just turned oil boiler on for first time this year. Came on fine but is not burning clean--dark smoke. Baromatic damper seemed like it was working but now staying closed and getting smoke in furnace r… read more
Rick
Rick
HVAC Supervisor
24,378 satisfied customers
Beckett AF2-150. 3 yrs old. Problems with outo shut downs(very
Beckett AF2-150. 3 yrs old. Problems with outo shut downs(very hard smokey starts,very shakey running and un called for cycling of motor). Replaced pump last year (leaking). Tech did not use beckett r… read more
Rick
Rick
HVAC Supervisor
24,378 satisfied customers
hello I am at my wits end with my new pinnacle po 84il boiler
hello I am at my wits end with my new pinnacle po 84il boiler it has a beckett afg burner . My electrician and installer have tried many things to figure out why the burner shuts off on safety. we add… read more
Rick
Rick
HVAC Supervisor
24,378 satisfied customers
I have a Weil McLain P-WGO-4 Series 3 Oil burner that wont
I have a Weil McLain P-WGO-4 Series 3 Oil burner that won't ignite. I've bled the fuel line and ensured that the boiler itself isn't saturated with fuel. It begin like normal but acts as if it's getti… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have a Beckett AFG with single fuel line and a Honeywell
I have a Beckett AFG with single fuel line and a Honeywell Aquastat controller. It's getting good ignition (new electrodes set properly) but the oil flow out the nozzle is weak. Nozzle was replaced an… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
i have a weil mclain wgo 4 oil fired boiler with 3 honeywell
i have a weil mclain wgo 4 oil fired boiler with 3 honeywell v48043e zone valves 2 for heat and one for hot water storage tank. a taco zvc 3 zone control and a honeywell l8148a aquastat with one circu… read more
Rick
Rick
HVAC Supervisor
24,378 satisfied customers
Hello, I have an oil fired heat and hot water problem. I have
Hello, I have an oil fired heat and hot water problem. I have a new boch water heater with a new beckett af burner with solid state ign etc. It runs fine with no problems. Nest to it is a Weil McLean … read more
Robert
Robert
Associate Degree
161 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x