WEil McLain oil Boiler Beckett burner will just shut down no…

WEil McLain oil Boiler...

WEil McLain oil Boiler Beckett burner will just shut down no lights on controller. If I shut down power & power back up it usually runs fine again. New fuel pump, filter, nozzle.

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

About 6 weeks, it will run fine for up to a week then trouble again

Contractor's Assistant: Do you plan on doing the work yourself?

To the extent that i can

Contractor's Assistant: Anything else we should know to help you best?

Today, and only today the motor started for about 1 sec then shut down, but then ran fine after that

Show More
Show Less
Ask Your Own HVAC Question
Answered in 4 minutes by:
3/2/2018
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 23,770
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. If my initial response doesn’t answer your question then let me know and we can continue our conversation.

Since the ignition control isn't locking out you need to look at the aqustat/relay and what's signaling a call for heat. If you only have 1 zone that would be the thermostat or thermostat wiring. If you have multiple zones then that would be the zone valves or pump relay(s).

Ask Your Own HVAC Question
Customer reply replied 1 month ago
i have pump relays but problem doesn't seem to correspond to any particular zone

Since the problem is intermittent it will be difficult to pin down but if you have multiple relays it's more likely this is an operating control (aquastat/relay). There's also a chance the ignition control could be faulty. First thing to do is check all your connections. Keep in mind that 18 gauge wire is notorious for partially breaking unnoticed. Ideally you'd monitor voltage at B1 & B2 on the operating control for a voltage drop/loss. Best to do this with the T terminals jumped. If have 120 vac at B1 & B2 and no burner function and no lockout then the ignition control is suspect.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
I'm not extpert , but I assume t = Thermostat, but what do you mean by ignition control?

Yes the T terminals are the "thermostat" terminals but in your case the relay end switches would be connected to them. They are labeled T on virtually all operating controls. Ignition control is the control on the burner with the reset button.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
if it is aquastat/relay wouldn't boiler still lock out eventually or no

You never mentioned a lock out which would require hitting the rest button to restart the burner

Ask Your Own HVAC Question
Customer reply replied 1 month ago
I'm sorry wasn't thinking clearly. The answer is, If the relay doesn't work then the whole process never begins, correct?

Far from the only possibility. The sequence could start then the voltage drops out due to a defect.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
But once process started I wouldn't get locked out?

I just answered this question. The sequence could start then the voltage drops out due to a defect. Again it's not a lock out unless you have to hit the reset button.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
sorry, I knew I wasn't locked out. I just thought that if the process got past the relay that the controller would lock out but I guess I was wrong, my bad

The thing is, intermittent problems are notoriously difficult to diagnose. You can only diagnose when it doesn't work. So next time it goes down you'll need to do the voltage testing I outlined earlier.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
OK, thank you

You're welcome

Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 23,770
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified
Rick and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?
Ask Rick Your Own Question
Rick
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 23,770
23,770 Satisfied Customers
Experience: 40+ yrs. experience as a licensed oil & gas technician.

Rick is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Crown wall hung boiler with a Wilocirculator that
I have a Crown wall hung boiler with a Wilo(###) ###-####circulator that has failed. would like to buy just motor cartridge if possible. is there a part number for that , or what other model pump woul… read more
Rick
Rick
HVAC Supervisor
23,770 satisfied customers
I need a blower for a Burnam Alpine boiler. It seems to be
I need a blower for a Burnam Alpine boiler. It seems to be discontinued. Can you advise? … read more
Rick
Rick
HVAC Supervisor
23,770 satisfied customers
Regarding steam boilers wiring to pressure controls and
Regarding steam boilers wiring to pressure controls and switches … read more
Rick
Rick
HVAC Supervisor
23,770 satisfied customers
Having a problem with my Weil Mclain boiler. It's hot but no
having a problem with my Weil Mclain boiler. It's hot but no heat to radiators … read more
Rick
Rick
HVAC Supervisor
23,770 satisfied customers
140M boiler goes to F09 the ignitor was replaced. Does the
140M boiler goes to F09 the ignitor was replaced. Does the rectifier need to be replaced too? … read more
Rick
Rick
HVAC Supervisor
23,770 satisfied customers
Buderus GB142 wall hung boiler with in concrete floor
Buderus GB142 wall hung boiler with in concrete floor radiant heat. Boiler Temp is set at 135, the attached AM10 has the target temp point set at 135 as well and the base temp point at 110. On cold da… read more
Rick
Rick
HVAC Supervisor
23,770 satisfied customers
I have a Lochinvar boiler that is not running. Sticker on
I have a Lochinvar boiler that is not running. Sticker on panel says do the reset switch but I can't find the reset switch. Where is it? … read more
Rick
Rick
HVAC Supervisor
23,770 satisfied customers
My boiler is not lighting. I can see that the pilot is
My boiler is not lighting. I can see that the pilot is burning. I have tried switching power off, and the system makes a noise like it is trying to light but does not. Noticed this this am as I was ch… read more
Rick
Rick
HVAC Supervisor
23,770 satisfied customers
I have a burnham boiler date on it is 2006, no sign of
I have a burnham boiler date on it is 2006, no sign of leakage but need to fill every 3-4 days. … read more
Rick
Rick
HVAC Supervisor
23,770 satisfied customers
My boiler has leak at the top... is that possible to fix
Hi.. my boiler has leak at the top... is that possible to fix this or better cal to the local HVAC specialist..?… read more
Rick
Rick
HVAC Supervisor
23,770 satisfied customers
I have a cg5 boiler for my home. The boiler ignites and runs
I have a cg5 boiler for my home. The boiler ignites and runs for 10 seconds or so, turns off for 1 or 2 seconds and then reignites, that happens over and over again for 30 minutes or so and then shuts… read more
Rick
Rick
HVAC Supervisor
23,770 satisfied customers
Crown boiler model # AWI128SNSTPSU NATURAL GAS. Boiler shut
Boiler shut down last night , how do I relight it ? … read more
Rick
Rick
HVAC Supervisor
23,770 satisfied customers
EcoTecplus 428 boiler,after reset boiler not coming on,but
ecoTecplus 428 boiler,after reset boiler not coming on,but pcb has power. … read more
Plumbers_Mate
Plumbers_Mate
General Manager
Vocational, Technical or Trade Scho
2 satisfied customers
Can you refer me to a Weill McLain boiler repairman? Boiler
Can you refer me to a Weill McLain boiler repairman? … read more
Rick
Rick
HVAC Supervisor
23,770 satisfied customers
Im getting an error code #65 on my pennco boiler. Boiler.
im getting an error code #65 on my pennco boiler JA: What device or product does this involve? Customer: boiler JA: What's the brand and model of your product? Customer: pennco JA: What have you tried… read more
David Bowden
David Bowden
Owner
757 satisfied customers
My crown boiler boiler model no. AWR070ENST2PSU runs for a
My crown boiler boiler model no. AWR070ENST2PSU runs for a short time, shuts down, then takes a long time on start running again. We change the control. the pump, and the gas valve, Don't appears to h… read more
Rick
Rick
HVAC Supervisor
23,770 satisfied customers
Im working on a boiler right now and the boiler is running
Hi pearl im working on a boiler right now and the boiler is running but is not heating the downstairs not the upstairs. I can't figure out why. Yesterday I replaced the pressure relief valve and the e… read more
Rick
Rick
HVAC Supervisor
23,770 satisfied customers
This is a boiler. The past 10 days. The Munchkin 80M boiler
the past 10 days. The Munchkin 80M boiler is a gas-fired boiler that was designed for residential homes. This boiler is rated at 92% efficiency and an Input Btu's of 27,000 to 80,000 Btu's. … read more
Rick
Rick
HVAC Supervisor
23,770 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x