I replace the ignitor and still not turning on flame.

I replace the ignitor...

I replace the ignitor and still not turning on flame. Everything looks attached and working.

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

Bryant

Contractor's Assistant: Do you plan on doing the work yourself?

Yes.

Contractor's Assistant: Anything else we should know to help you best?

Last Thanksgiving 15 mos ago similar problem, then worked. Began again this winer

Show More
Show Less
Ask Your Own HVAC Question
Answered in 10 hours by:
2/19/2018
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,201
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. First I’ll need some more info so I have a more complete picture of your situation.

Does the draft inducer fan on the front of the unit run when there is a call for heat?

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Hi Rick. I couldn't find the response from you, b/c way I "didn't set up an acct." I just spoke customer service and they have us connected.Regarding your last question: that brown spinny thing does spin. The ignitor does not go on. (before it was intermittent - sometime did, sometimes not...odd, sometimes wouldn't work, but if left furnace on for a couple days, it would just start up sometime.) I have replaced the flame sensor and ignitor - they are new. I can't seen any wiring disconnected.
Customer reply replied 3 months ago
let's see if we can do this by text first. If not work, and a call will solve it, i'll try that. already paid $28.

What's the brand and model of your furnace? The model is on the BTU rating tag inside the burner compartment.

Call prompt is automatic I have no control over it. We can continue here

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Looking. One sec

ok

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Bryant
Product 312aavo24070. Aaja
Customer reply replied 3 months ago
First#s model , no period then aaja added for product
Customer reply replied 3 months ago
Series a

Are you getting a flash code on the control board LED inside the blower compartment? Do not remove the compartment panel. There should be a viewing port to see the LED

Ask Your Own HVAC Question
Customer reply replied 3 months ago
It was 12 but then 34 and 14. Right now it is turned off. I can turn it back on if need to.

Turn it back on and test for power to the igniter after the draft fan has been running

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Sounds like a fan or furnace on. Hear clicking. Thing is spinning
Customer reply replied 3 months ago
34 blinking

I'm going to open this up to my colleagues so one of them can help. Please don't respond (even to acknowledge this post)until you get a response from us. If you respond first it will only delay your answer.

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Seems to be trying again I heard clicking...now just turned off
Bill
Bill, HVAC Technician
Category: HVAC
Satisfied Customers: 103
Experience: Service Mgr
Verified

Hello,

It sounds like the ciurcuit board is not sending power to the ignitor. Have you already changed the circuit board?

Ask Your Own HVAC Question
Customer reply replied 3 months ago
No.

If you have code 34...and no glow:

It is a bad ignitor or a bad circuit board. It is always one of those 2 if there is no glow.

Bill

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Fuse is good.

I know the fuse is good but the ignitor relay is not.

There is a manual test if you are game. Do you have a small propane torch?

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Im game
Customer reply replied 3 months ago
I think so. Referring to yellow canister?

correct, yellow or blue canister.

We want to light torch, start furnace....sfater the exhaust fan is running hold the torch flame next to the glow ignitor.

When you hear the clicking the gas valve will open and give gas for 3 seconds....if the gas lights in that 3 seconds flame stays on.

Try this test and tell me if the burner lights

Ask Your Own HVAC Question
Customer reply replied 3 months ago
K. Give me a few minutes to set up

No problem, take your time

Bill

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Yeah. Working
Customer reply replied 3 months ago
Staying on nicely
Customer reply replied 3 months ago
Really quick ignition. Automatic. Working well.

Ok, so this means bad ignitor or board...and you already replaced ignitor. So your board is not energizing the ignitor.

Bill

Ask Your Own HVAC Question
Customer reply replied 3 months ago
I should purchase the circuit board and replace it? Yes ignitor is brand new.

Yes, then getting the board will take care of the issue.

I did hundreds of these and when it was not ignitor it was always the board...thus my torch test:)

You can also do that each time to light it to get by until new board installed.

Just rate service to close and thank you!

Bill

Ask Your Own HVAC Question
Customer reply replied 3 months ago
That's great. I will rate very well and use service again. Recommend.
Customer reply replied 3 months ago
Question...that red box with tree switches
Lht and dff are off
Dly is on
Are these significant?

No those are just blower on/off/delay differential.

Those are not related to igniton

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Okay. Thanks. Warm family again :). Best.

You are very welcome,

stay warm

Bill

Bill
Bill, HVAC Technician
Category: HVAC
Satisfied Customers: 103
Experience: Service Mgr
Verified
Bill and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Bill Your Own Question
Bill
Bill
Bill, HVAC Technician
Category: HVAC
Satisfied Customers: 103
103 Satisfied Customers
Experience: Service Mgr

Bill is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Have a UAPC-024JAZ, getting 25AC signal from upstairs,
Have a UAPC-024JAZ, getting 25AC signal from upstairs, change relay and start cap. TS, 26AC getting through the switch attached to compressor, but not through the switch that has a coiled tube attache… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
I replaced my failing carrier humidistat wir. With a Nest
I replaced my failing carrier humidistat wir JA: I'll do all I can to help. How long have you been dealing with this? Customer: With a Nest and have a wiring error JA: How old is the appliance? Have y… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
My central air system is not working the fan is not spinning
my central air system is not working the fan is not spinning outside and it is a Rheem Classic XII … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I opened the front panel on the unit to check for mold or
I opened the front panel on the unit to check for mold or mildew and the unit cut off. The red light is blinking and now the unit will not come back on. I didn't touch anything, just replaced the pane… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My Rodgers thermostat will not bring down the temp. The
My White Rodgers thermostat will not bring down the temp. The Cooling icon keeps flashing … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,870 satisfied customers
I have a Ruud ultra Super Quiet 80 2 stage unit that the
I have a Ruud ultra Super Quiet 80 2 stage unit that the blower is not working. It has a Honeywell wireless thermostat that I don't believe is the issue. With the blower door removed, and the door int… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
WHIRLPOOL n40s61-403 gas water heater; pilot light lit;
WHIRLPOOL n40s61-403 gas water heater; pilot light lit; won't come back on to heat tank … read more
Rick
Rick
HVAC Supervisor
24,201 satisfied customers
I have a rcc48a2b and im looking for a hard start kit. Can
i have a rcc48a2b and im looking for a hard start kit. Can you help … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My ac compressor works fine but the condenser fan will
Hello, my ac compressor works fine but the condenser fan will sometimes not start automatically, especially in the morning, evening or at night. The condenser fan starts fine during the day. When it d… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a L 10 eccotemp water heater that will not light
I have a L 10 eccotemp water heater that will not light unless I take the drain plug out then it fires up.Any thoughts ? … read more
Bill
Bill
HVAC Technician
103 satisfied customers
I replaced the capacitor and fan motor, but now the
I replaced the capacitor and fan motor, but now the capacitor won't turn on. What should I look at now? … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
MY WHIRLPOOL WATER HEATER MODEL# IS L40S62-403 PURCHED 7/13
Second opinion] MY WHIRLPOOL WATER HEATER MODEL# ***** ***** PURCHED 7/13 WILL NOT LICHT. I HAVE DONE WHAT THE BOOK SAYS DO AND GET NO SPARK FROM THE IGNITER. I TRIED LIGHTING THE PILOT ( HOLDING THE … read more
Rick
Rick
HVAC Supervisor
24,201 satisfied customers
FFBD2406NS3A Frigidaire dishwasher: 3 years, does not dry
3 years, does not dry heating element has continuity, high limit is normally closed. No ac to either … read more
David Hanger Jr
David Hanger Jr
Appliance Repair
1 satisfied customers
Unit quit working after we changed batteries in thermostat.
Unit quit working after we changed batteries in thermostat. Green light flashing on mother board … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My air conditioner quit the filter was stopped up I changed
My air conditioner quit the filter was stopped up I changed it but now I have nothing please help this Georgia heat is bad … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,870 satisfied customers
The head pressure slowly raises as the suction pressure
The head pressure slowly raises as the suction pressure stays steady in the cooling mode … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Switching Condensor Motors - same type, new motor has 5
Switching Condensor Motors - same type, new motor has 5 wires, existing had 3, need help connecting the wires properly… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I'm trying to make a repair or replace decision on a 7 year
I'm trying to make a repair or replace decision on a 7 year old Goodman 70,000 BTU 95% A.F.U.E rating with a burnt out blower motor. The part cost is quite high and probably approaching 40% of replace… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x