My steam boiler is discharging steam and water from the

relief valve. I just...
My steam boiler is discharging steam and water from the relief valve. I just changed it to a new one and issue seemed to intensify. Any idea what’s going on
Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 7 months ago
All radiators get hot
Customer reply replied 7 months ago
Weil McLain 125000btu has fired steam boiler
Answered in 11 minutes by:
2/14/2018
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,878
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, it is most likely that your temperature controllers, both the high limit and the operating temperature control inside the boiler are set too high, OR defective with the contacts burnt closed.

.

Take close up, exceedingly well focused photo of the boiler wiring diagram glued inside its service access panel and I will mark it up with trouble shooting instructions.

Use the 'add files' link next to your send button to get the photo(s) to me.

.

We can go from there with training, coaching and diagnosis.... without a time limit, In depth with as much detail as needed .

.

When we finally get the situation solved, please select the 'finish and rate your expert link' near the top of your page and click on it.

.
My goal is to give you the best experience possible!
I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today.

If you need more assistance, please use the reply box and let me know.

Ask Your Own HVAC Question

Thanks, click here please

.

Tell me where the thermostat and limit switches are set please.

.

Next remove one wire from the thermostat and tell me if boiler ceases firing or not.

Next remove one wire from the limit switch and tell me if the boiler ceases firing or not.

That will tell me whats most likely wrong with the boiler.

We can go from here until we get it sorted out

Ask Your Own HVAC Question
Customer reply replied 7 months ago
I have it off right now
Customer reply replied 7 months ago
Should I turn it on?

First tell me where the thermostat and high limit switches inside the boiler are set.

.

Steam boilers can be *dangerous, even with a working pressure relief valve in place.... you should not be working on this unless you are confident in your skills and wish to take the risk.

.

If so then turn the boiler on until it blows the relief valve and follow my instructions to disconnect the one wire from each from the thermostat and high limit switch marked on the wiring diagram you sent me.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
The pressuretrol is set at 0.5 and where can I see the thermostat

Thanks, ***** ***** the model number of the boiler and I will see if I can pull the manual on it

Ask Your Own HVAC Question
Customer reply replied 7 months ago
EG-40-PI series 2

Hello again, click here please, see page 20.

we can work with the pressure limit switch only.

Follow my earlier directions on that

Ask Your Own HVAC Question
Customer reply replied 7 months ago
If I wait for the relief valve to blow, I take off one wire from the pressure control
Customer reply replied 7 months ago
if it stops discharging, it tells me the pressure control is no goo?
Customer reply replied 7 months ago
Good

When you take one wire off of the pressure control the burner should shut off, then a minute or so later it will cease discharging.

If the burner does not go off, the gas valve is stuck open and must be replaced

Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,878
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified
Phil and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,878
9,878 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,878 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Pressure gage on boiler wont go lower than 20 psi regulator
pressure gage on boiler wont go lower than 20 psi regulator is set at 12 lbs turn water on a week later relief valve went off why is this and could the boiler be damaged… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I just replaced a Honeywell L8148J on my boiler, and all it
I just replaced a Honeywell L8148J on my boiler, and all it does is hum. There is no power being sent to the gas valve terminals, and the circulator does not kick on. This is what the old one was doin… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Weil-Mclain oil fired hot water furnace in my residence
I have a Weil-Mclain oil fired hot water furnace in my residence and would like to know what is the recommended water pressure. Thank you… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
WATER IN BOILER SYSTEM TURNS TO STEAM AND POPS OFF RELIEF WHILE
WATER IN BOILER SYSTEM TURNS TO STEAM AND POPS OFF RELIEF WHILE TEMP GAUGE SHOWS ONLY 170 DEGREES AND BURNER IS SET TO TURN OFF AT 160… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Weil Mclain Model #CGA -6-SPDN boiler. It has been
I have a Weil Mclain Model #CGA -6-SPDN boiler. It has been used for hot water baseboard but I was wondering if this model is capable of being used for steam application such as steam radiators?… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
What is the "Operating Gauge Pressure" for Gas fired Steam
What is the "Operating Gauge Pressure" for Gas fired Steam Boiler EGH-105? What is the "Pressure Setting of Relief Valves" for Gas fired Steam Boiler EGH-105? Art XXX-XXX-XXXX… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Weil McLain CGt-5-PIN boiler with waterless hot water
I have a Weil McLain CGt-5-PIN boiler with waterless hot water heater with hot water baseboards. I only get almost luke warm water for showers with an occasional minute of nice warm/hot water. Also wa… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,878 satisfied customers
How exactly do you take the air out of the central heating
How exactly do you take the air out of the central heating system (the radiators make a lot of noise suggesting air bubbles in the closed water circuit) and refill it with sufficient water?… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,878 satisfied customers
I have a GV-4 Weil-McLain Boiler for domestic heatn indirect
I have a GV-4 Weil-McLain Boiler domestic heat. An indirect fired W-M water heater is attached. The boiler relief valve is regularly discharging a small amount of water. The valve has been replaced. T… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Hi, I manage a building (low-rise, 3 floors, 16 units) with
Hi, I manage a building (low-rise, 3 floors, 16 units) with a weil-mclain boiler. I'm unfamiliar with steam boiler systems in general (i bought this building 18 months ago). I have a situation where 3… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,878 satisfied customers
Have a Weil Mclain boiler steam heating a house built in 1928.
Have a Weil Mclain boiler steam heating a house built in 1928. Boiler is about 12 years old as is the plumbing and new radiators. Have had various problems with the system almost since it was put in, … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I am in the process of converting from oil to a gas steam boiler
I am in the process of converting from oil to a gas steam boiler and the installer has recommended a Burnham IN7 gas boiler and a WeilMclain or a.o.smith gas water heater for installation. Subsequentl… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
i have peerless 120btu series 61, 15 years old cracked boiler
i have peerless 120btu?series 61, 15 years old cracked boiler pse&g estimate 6500$ estimate replacement a wiel-mclain eg series 4 ef gas boiler 209000btu/hr hot water- steam 192 to 750 sq ft model #pe… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a 15 year old 200 BTU steam furnace and am planning
I have a 15 year old 200 BTU steam furnace and am planning to buy a gas condensing boiler. Is the UG230 Mclain corresponding size unit? I read that with low temperature application the efficiency goes… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a 1500 sq. ft home with oil steam heat, Im converting
I have a 1500 sq. ft home with oil steam heat, I'm converting to natural gas and need reccomendations for a gas fired high effeciency steam boiler.… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have had to replace a cracked boiler twice in the last six
I have had to replace a cracked boiler twice in the last six years. It's a Weil McLain. What's going on?… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Mark or Jim, the following are the answers to your questions My
Mark or Jim, the following are the answers to your questions: My two Questions are: 1. Is there any reason that we should not fed the steam header from either or both ends of this maybe 6 foot long st… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
My son owns a Weil McLain boiler. It is an Ultra 230 which
My son owns a Weil McLain boiler. It is an Ultra 230 which heats a two story house with cast iron radiators on a single loop. It also heats the domestic hot water. He was having trouble with the relie… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x