I have a furnace that wont run, i have done some

Customer Question
I have a furnace...

I have a furnace that wont run, i have done some troubleshooting and had a repairman out, but it is still not running. was hoping for some help diagnosing the issue.

Contractor's Assistant: Did you check the furnace's filters?

Yes. the furnace filter is new

Contractor's Assistant: Do you plan on doing the work yourself?

Depending on the labor involved, yes.

Contractor's Assistant: Anything else we should know to help you best?

The cycle goes as follows.

Submitted: 4 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 4 months ago
I have a Goodman furnace, model number gms80703ana. Furnace powers on, inducer motor runs, relay clicks and the hot surface ignitor glows. the gas valve clicks and will sometimes fire, sometimes not. If the gas does light, it will stay on for about 20 seconds and than turn off. I cleaned the flame sensor, and then replaced it with a new one. the condition still existed. At that time, i also replaced my HSI. The limits all tested as normally closed. I was told by a technician that the circuit board was bad, so i replaced it, but the condition still existed. I then bought another new circuit board (to make sure the previous new one wasn't also faulty) and the same problem still exists. The indicator light will flash 6 times, and then 7 times when the gas is cut off. I measured voltage to the gas valve, and am only getting 10vac. I jumped the gas valve with 24v directly from the transformer, and it fires up no problem. however, once i remove the 24v jumper wires, it shuts off.
Customer reply replied 4 months ago
I removed the chimney pipe, to see if maybe it was not allowing the exhaust to vent and shutting off the gas, but the house filled with smoke when i did that, so i put that back on immediately. I checked the furnace chimney cap on the roof, and it was not blocked by snow, or any other obstructions. The house is a duplex, and the other unit directly next door has the exact same furnace and exhaust system and is working fine. I have replaced the circuit board in that furnace next door, and it worked fine
Answered in 11 hours by:
2/14/2018
HVAC Technician: Rick, HVAC Supervisor replied 4 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,212
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. If my initial response doesn’t answer your question then let me know and we can continue our conversation.

Test voltage into and out of the 24 volt AC transformer

Ask Your Own HVAC Question
Customer reply replied 4 months ago
120vac, 24vac. As I said earlier, I jumpered 24v directly from the transformer to the gas valve because the wires at the valve are only being given 10vac.
HVAC Technician: Rick, HVAC Supervisor replied 4 months ago

That wasn't clear. I'm going to open this up to my colleagues so one of them can help. Please don't respond (even to acknowledge this post)until you get a response from us. If you respond first it will only delay your answer.

Ask Your Own HVAC Question
HVAC Technician: Regan Land, HVAC Technician replied 4 months ago
Regan Land
Regan Land, HVAC Technician
Category: HVAC
Satisfied Customers: 768
Experience: Over 20 years of experience, NATE Certified, Licensed HVAC Contractor, Certified IAQ Specialist
Verified

Good morning - My name is ***** ***** I'll be happy to help you. How long does the board flash the 6 code before changing to 7? That's an indication of an open roll-out switch... I'm wondering if the contacts in one of the roll-out switches are bad and causing some strange things. Is there one or two roll-outs on your furnace?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
There is the one manual reset rollout limit. But it holds closed even when it says rollout limit. It blinks 6 times just on the first display, then blinks 7 times for two more displays before trying to cycle again.
HVAC Technician: Regan Land, HVAC Technician replied 4 months ago

Okay, thank you. The sensor senses flame through ground, so let's check and make sure the ground to the unit is solid. Make sure there's a ground running to the plug/switch/disconnect of the unit, then that the connection to the unit cabinet is solid.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Okay. The furnace has a 12/2 w ground mc to the disc. It has a ground running all the way from the panel to the switch. The ground bonds the plate which the inducer motor sits on; the inducer motor itself, and the burner housing. I have 1.3v when measured between the ground and neutral.
HVAC Technician: Regan Land, HVAC Technician replied 4 months ago

A small amount between ground and neutral is normal. Sounds like it's grounded properly. Take a look at the gas valve - the diagram shows the brown wire from gas valve runs through an auxiliary limit switch before going to the control board. Try bypassing that auxiliary limit and see if furnace fires properly.

Ask Your Own HVAC Question
HVAC Technician: Regan Land, HVAC Technician replied 4 months ago

Have you had a chance to check that and bypass that limit? The more I think of it the more I'm confident that the switch is bad or there's a loose connection somewhere in that brown wire.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
I won’t have a chance to check until tonight. The gas valve gets both wires directly from the 12 pin connector on the board, it does not run through any switches first.
HVAC Technician: Regan Land, HVAC Technician replied 4 months ago

Okay, thanks. The diagram definitely shows the brown one goes through a switch. When you get a chance test voltage between the two gas valve wires directly at the control board as well.

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Ended up being the capacitor for the circulator blower.
HVAC Technician: Regan Land, HVAC Technician replied 3 months ago

Thank you for the update! That's strange that it was giving a 6 and 7 flash code - should've been 4 flashed indicating open limit. Glad it was taken care of!

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Regan Land Your Own Question
Regan Land
Regan Land
Regan Land, HVAC Technician
Category: HVAC
Satisfied Customers: 768
768 Satisfied Customers
Experience: Over 20 years of experience, NATE Certified, Licensed HVAC Contractor, Certified IAQ Specialist

Regan Land is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My goodman furnace blower wont start running when the a/c
My goodman furnace blower wont start running when the a/c unit starts running outside. The blower fan runs slowly then shuts off. … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,872 satisfied customers
My Goodman furnace AC unit will not kick on the blower motor
My Goodman furnace AC unit will not kick on the blower motor outside AC unit is working but do not get any blower motor at the furnace … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Goodman furnace that works good but there is a
I have a Goodman furnace that works good but there is a flashing red led when heater is on I want to know what is going on … read more
David Bowden
David Bowden
Owner
990 satisfied customers
I have a goodman furnace model GMS90904CXA and when i turn
i have a goodman furnace model GMS90904CXA and when i turn it on the fan starts but the never tries to light and then the fan shuts down. the red light flashes 4 times. … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,872 satisfied customers
I have a Goodman furnace and air conditioning system in my
I have a Goodman furnace and air conditioning system in my house had to replace the main board this winter and I didn't have the time reattach the control wires to the air-conditioner I don't know whe… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Are permanent furnace filters a better option than the one
Are permanent furnace filters a better option than the one you need to replace every 3 months?I have been using the 3M Filtrete filters for a while, but recently I was told that electromagnetic filter… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,872 satisfied customers
Goodman furnace with trouble code no data, yes, at this time
furnace will not start draft inducer motor no signal.… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,872 satisfied customers
Have Goodman furnace model CNPVP3017ALAAAAA. Yesterday had
Yesterday had to shut down [with thermostat] to change some gas lines. It ran ok upon restart, but today blower runs continuously no matter what setting the thermostat is adjusted to. … read more
Rick
Rick
HVAC Supervisor
24,212 satisfied customers
I have a Goodman furnace. And it's continually blinking.. I
I have a Goodman furnace. And it's continually blinking.. I was wondering how does it reverse polarity?.... … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
I have goodman furnace GMH80803BNBB, WILL NOT START, RED
I have goodman furnace GMH80803BNBB, WILL NOT START, RED LIGHT BLINKING 6 TIMES UNDER bottom case. yesterday furnace fired but not ignite today not firing, what?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have new goodman furnace model GMVC960603BNAA that my
i have new goodman furnace model GMVC960603BNAA that my plumer could not start for first time with code 88 … read more
Chris Wagner
Chris Wagner
None
27 satisfied customers
Goodman furnace will not start. Solid red light. Checked the
Goodman furnace will not start. Solid red light. Checked the transformer have 24 volts. By-paqssed the thermostat at the board (jumped R & W) nothing when pushing door switch on. Also, at the beginnin… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a goodman furnace mod# GMH950904CXAA 2 blinks for
I have a goodman furnace mod# ***** 2 blinks for code … read more
Rick
Rick
HVAC Supervisor
24,212 satisfied customers
I have a goodman furnace. It will turn on the initial blower
I have a goodman furnace. It will turn on the initial blower to prepurge, then it will ignite and as soon as the main blower turns on, the flame will go out. It will keep igniting and going out for a … read more
Rick
Rick
HVAC Supervisor
24,212 satisfied customers
I have a 3 year old Goodman furnace Model#CAPF303C6DB. About
I have a 3 year old Goodman furnace Model#CAPF303C6DB. About every other night, it stops working and I have to reset the circuit breaker. I don't think it is blowing the breaker switch because there a… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a nine-year-old Goodman furnace it won't start it has
I have a nine-year-old Goodman furnace it won't start it has a one flash code I go through the reset procedures and it does the same thing again price start three times and locks out … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Goodman furnace acts as if it's not getting gas. Slightly
We just went through about 2wks of extreme cold temps. For whatever reason when the furnace has a lead time that lapses the furnace shuts down.… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a Goodman furnace that has tripped the lockout
I have a Goodman furnace that has tripped the lockout sensors twice now … read more
Rick
Rick
HVAC Supervisor
24,212 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x