I am replacing the gas control valve in my G26Q3-75-1

Customer Question
I am replacing the...

I am replacing the gas control valve in my G26Q3-75-1 furnace with a white rodgers 36H series valve. Can you tell me the correct wiring connections? It is not a direct swap.

Contractor's Assistant: Did you check the furnace's filters?

Yes, just replaced

Contractor's Assistant: Do you plan on doing the work yourself?

Valve is installed. Need to verify the wiring.

Submitted: 4 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 minute by:
2/6/2018
HVAC Technician: airheatman, HVAC Technician replied 4 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,085
Experience: Furnace, A/C and heat pump specialist.
Verified

Welcome to the JustAnswer/Pearl website.My name is ***** ***** I am happy to be able to work with you on this today.Please be patient as I respond as sometimes it takes me a few moments to gather proper manuals and specifications on your equipment in order to provide accurate answers.Please wait until we are finished to rate my answer.Hopefully at that time I will have earned a five star rating.Now just to let you know, the website does offer a live phone call for one on one discussion for an additional fee. Due to my current work load and responsibilities I may not be available for the live phone call but along the way, the website will automatically present the offer.Please note that there is an additional cost for the service and if a technician calls it may be a different technician. However we can continue here as long as needed .

Let me grab a wiring diagram

Ask Your Own HVAC Question
Customer reply replied 4 months ago
I am looking for the correct connections of the C, MV, and PV connections from the furnace controller to the new gas valve.
Everything seems to work properly when turned on, but does not seem like there is any gas flow. pilot does not light and therefore burner does not fire.Need to get the furnace going for the night. I'm in Michigan.
HVAC Technician: airheatman, HVAC Technician replied 4 months ago

THere should be matched terminals on the ignition module that feed voltage to the valve. Are you getting 24 volts between COM and PV on call for pilot and COM and MV when burners should come on?

The PV is the pilot side of the valve and MV is main valve which opens to light burners.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
I can check quick.The main doesn't come on due to pilot not firing.Is the wiring as simple as yellow to C, MV from controller to M on valve, and PV on controller to P on valve?
Customer reply replied 4 months ago
between PV and com, voltage jumps when pilot igniter starts and then levels out around 6 V. There is no power to the main as there is no pilot to start the main burners.
HVAC Technician: airheatman, HVAC Technician replied 4 months ago

Most likely going to have to replace the ignition module if 0nly sending 6 volts

Ask Your Own HVAC Question
Customer reply replied 4 months ago
The old valve worked, but solenoid was sticking. Couldn't count on the valve to open everytime. Lots of time the blower would run and the burner would not ignite.Is there a way to check the module to see if it is good?
HVAC Technician: airheatman, HVAC Technician replied 4 months ago

If the board is not sending 24v to pv you have already done so

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Why would the other valve work then?
HVAC Technician: airheatman, HVAC Technician replied 4 months ago

I have to leave for a while for a meeting.I will think this over while I am driving and see if I can think of why a bad valve was opening with 6v and why new valve does not.If I don't come up with anything , when I return I will do some research in troubleshooting the particular unit to see if Lennox designed this one to open pilot on 6v.PLease reply with module number you have so I can research.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Intermittent Pilot Ignition Control G776RGD-10
HVAC Technician: airheatman, HVAC Technician replied 4 months ago

Sorry for the delay.I have looked everything over and 6v will not open valve to light pilot.Not sure if perhaps the board going bad could have at that time been sending 24v to PV and now it is not or what.I do know erratic behaviour is common for a failing board.

Here is the flow chart based on the fact that we are getting spark but not pilot.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,085
9,085 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have 7 wires your thermostat wiring shows only 4 wire to
I have 7 wires your thermostat wiring shows only 4 wire to connect … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have trane xe 78 with a rodgers model 50A50 - 405 board.
I have trane xe 78 with a white rodgers model 50A50 - 405 board. My fan runs continously with or without calling for it? I have removed the thermostat and it still continues to run? Does the fan for A… read more
Bill
Bill
Service Mgr
104 satisfied customers
Old thermostat rodger, 6 wires this include the much desired
old thermostat white rodger, 6 wires this include the much desired C wire. I want to install a new smart Honeywell T5. Most wires seem straight forward but the old white rodger bridge (jumper) between… read more
airheatman
airheatman
HVAC Technician
9,085 satisfied customers
My white rodgers thermostat 4875B has only up and down
My white rodgers thermostat 4875B has only up and down buttons. How do I switch to air from heat ?… read more
airheatman
airheatman
HVAC Technician
9,085 satisfied customers
I have an old white rodgers thermostat that is used for air
i have an old white rodgers thermostat that is used for air conditioner it is an outside unit nothing in the house it only has three wires 1 red and 2 green want to change i with a honeywell … read more
airheatman
airheatman
HVAC Technician
9,085 satisfied customers
My Mom calls when anything electrical happens. Her HVAC will
My Mom calls when anything electrical happens. Her HVAC will not cool I have had the same situation in my place How do you reset the system? … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
The whole screen on my -Rodgers thermostat is blinking. I
The whole screen on my White-Rodgers thermostat is blinking. I replaced the batteries, nothing happened. … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,874 satisfied customers
I have a white Rodgers heat only thermostat, mod.1e78-140.
I have a white Rodgers heat only thermostat, mod.1e78-140. it is not working, does it run on batt. or is the power wired from home. … read more
airheatman
airheatman
HVAC Technician
9,085 satisfied customers
I have a White-Rodgers 1 F81-261 Programmable thermostat.I
I have a White-Rodgers 1 F81-261 Programmable thermostat.I want to operate it manually. Please help. It has reset at 62 degrees. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a White-Rodgers thermostat with the flap that opens
Hi, I have a White-Rodgers thermostat with the flap that opens to the menu. All of a sudden the temp of the room that the display shows on the left is not showing the temperature in Fahrenheit, but it… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My white rodgers 1f78 non-prgm thermostat won't work. The
My white rodgers 1f78 non-prgm thermostat won't work. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have a White Rodgers !F-95-1291 Touch screen thermostat
I have a White Rodgers !F-95-1291 Touch screen thermostat with remote outdoor sensor. The out door reading is off by 10 degr F, too low. What's the prob? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have an f8024 white rodgers, i am renting right now but
I have an f8024 white rodgers, i am renting right now but the unit worked last summer, i just replaced the batteries, but when i press the temp down button, nothing happens. … read more
Iohn Keffer
Iohn Keffer
HVAC Tech
Associate Degree
68 satisfied customers
I have a white/rodgers 8A05A -101 relay that I want to use
I have a white/rodgers 8A05A -101 relay that I want to use for a hot water circulating pump. The thermostat wiring is straight forward but the wiring for the 120 v is not. I have the following wires. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
White Rodgers Thermostat 1f78-1151 is hooked up but not
I have a white Rodgers Thermostat 1f78-1151, I've hooked it up and it isn't working. I don't know if I wired it wrong. When I just connect the wires together the baseboards come on.… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have an old White/Rodgers thermostat that I'm upgrading to
I have an old White/Rodgers thermostat that I'm upgrading to a wifi Honeywell. All wires are labeled, but there is one labeled W that has no corresponding slot in the new thermostat. Is this W equal C… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We have a 15-20 yr old white-Rodgers thermostat wired to an
We have a 15-20 yr old white-Rodgers thermostat wired to an attic furnace; a pain to get to. We have to keep getting up in there to reset it. This time it's not coming on? … read more
airheatman
airheatman
HVAC Technician
9,085 satisfied customers
My white-Rodgers thermostat keeps failing. Sometimes it works.
The white-Rodgers thermostat keeps failing. Sometimes it works sometimes it doesn't. A company came to check and when they were here, it was working then it failed again. They check the HVAC in the at… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x