I have a honeywell comfortmaker, and the blower does not…

I have a honeywell...

I have a honeywell comfortmaker, and the blower does not start - just a high pitched electrical type hum coming from the circuit board. Bad transformer perhaps?

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

Heater would sometimes come on, and sometimes not for a couple weeks now. Now it's just not coming on - or at least the blower part isn't

Contractor's Assistant: Do you plan on doing the work yourself?

If possible. Most places are closed today

Contractor's Assistant: Anything else we should know to help you best?

Honeywell model NBF100F20G1

Show More
Show Less
Ask Your Own HVAC Question
Answered in 3 minutes by:
1/21/2018
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,751
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified

One moment please..Note it takes time to type and add links so please be patient. Also the site will send you a phone call offer, that is not me.

Ask Your Own HVAC Question

If you take the panel off is the blower humming?

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Blower motor is not humming. There's a high pitched whine coming from the circuit board
Checked capacitance on capacitor, since that's usually the cause of a fan not running - got 8.98 on a 10uf capacitor.
Tried spinning the fan to start, does not start.

I would say the baord is bad if the noise is coming from the board. Can you see what part on the board is making the noise?

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Can't really isolate the sound, but it does sound like a bad transformer maybe.
Guess I can check to see if it's putting out 24v

Yes check it out that would be about the only thing that could be making the noise, but if it is something on the board replace the board.

All I ask is...Please remember to use the RATING LINK ON YOUR PAGE by selecting a star at the top or bottom of the screen before you leave today. Even though you paid the site they will not disburse any part of it to me until you supply a good rating. If you need anything else, just let me know. You can continue asking follow-up questions at no additional charge after rating my service if you still need assistance.

HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,751
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified
HVAC Guru and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask HVAC Guru Your Own Question
HVAC Guru
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,751
18,751 Satisfied Customers
Experience: 20yrs in the HVAC industry with certificates and degrees.

HVAC Guru is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Gas Furnace TUE060A936K Blower does not stop after gas
Gas Furnace TUE060A936K Blower does not stop long after gas burning stopped. How to troubleshoot the problem?… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
I have a Trane XL 1400 gas heat and air conditioner. I bought
I have a Trane XL 1400 gas heat and air conditioner. I bought a new wifi Honeywell thermostat to replace my old thermostat. I have ony the four wires now and no c wire. My plans are to move the G to C… read more
Wvfan79
Wvfan79
Mecanical Designer & Estimator
High School or GED
775 satisfied customers
I have a Trane TXCO31C4HPCO. Its buzzing a high pitch buzz
I have a Trane TXCO31C4HPCO. It's buzzing a high pitch buzz and the DS1 light is on. Otherwise everything is working just fine But it buzzes when the air is on or off. Ideas?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hi I have a honeywell s8670j for my powder coating oven, and
Hi I have a honeywell s8670j for my powder coating oven, and it has a #8 code ( low voltage ) can you tell me what this means.… read more
jhvac
jhvac
2 satisfied customers
I have a 17 y.o Carrier gas furnace w 3 ton AC. When I call
I have a 17 y.o Carrier gas furnace w 3 ton AC. When I call for AC thru the 'stat the indoor fan blower doesn't work and neither does the outdoor compressor/fan. When I open the indoor service panel a… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Hi Matthew I just purchased a Honeywell 260A Humidifier and
Hi Matthew I just purchased a Honeywell 260A Humidifier and wanted to hook it up to my furnace directly for power. I have a HUM outlet on my circuit board. The install kit came with a transformer but … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
hi, my immitter clicked off on my oil hot water heater burner
hi, my immitter clicked off on my oil hot water heater burner and when i went to reset it, the immitter and the honeywell RA89A started to click repeatedly at a fast pace. I have no idea what this cou… read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
Why is SV9502H2522 using a ST9120U1011 unit short cycling
I have SV9502H2522 using ST9120U1011 unit "short cycling" in odd way. Inducer comes on, normal ignition. Blower cuts off mid-cycle, with stat calling. Gas valve closes, blower comes back on. Reignites… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
hello I have a old furnace in one of my rental homes, it has
hello I have a old furnace in one of my rental homes, it has honeywell controlls, and it has a honeywell transformer type AT72B9CG2 115 volt , and i believe it reads 60/60 cycle it is faded also says … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I am installing a Honeywell HE220A humidifier to a York Diamond
I am installing a Honeywell HE220A humidifier to a York Diamond 80 furnace. The furnace control board has an open HUM connection. Can you help?… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a Bryant Plus 95s gas furnance and I have installed
I have a Bryant Plus 95s gas furnance and I have installed just installed Aprilaire 700 series whole house humidifier. I have got it to work manually but I need to know how to wire it to the high spee… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I just had an Amana 16 seer HVAC system installed. The closet
I just had an Amana 16 seer HVAC system installed. The closet mounted blower sounds just like the old system did when I set it to run "fan only". But if I set the thermostat to "cool" and the AC start… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
My Comfortmake EnviroPlus 90 heater sometimes fails to start
My Comfortmake EnviroPlus 90 heater sometimes fails to start when heat is called for. The exhaust blower comes on for almost exactly 7 seconds and goes off. Then within a few seconds it tries to start… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Carrier furnace 58SX. The blower motor is constantly
I have a Carrier furnace 58SX. The blower motor is constantly running without the burners igniting. I turned the thermostat to off and disconnected the ground to the thermostat and the blower remained… read more
Jason  Hvac
Jason Hvac
Hvac Tec
Vocational, Technical or Trade Scho
120 satisfied customers
On a lp gas heater, the thermostat sends call for heat, I can
On a lp gas heater, the thermostat sends call for heat, I can hear the Induced Draft blower come on. I know the burners are burning fuel because I can smell the "hot" smell in the house. However, the … read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Hello, I have a residential furnace and I am installing a bypass
Hello, I have a residential furnace and I am installing a bypass humidifier to it, I was told that i can wire the humidifier to the w and common terminals on the furnace board. Now i have the low volt… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I a york furnice that works o.k. and is 3 years old. When I
I a york furnice that works o.k. and is 3 years old. When I came home from work today, I noticed a humming noise coming from the return air vent, as though the heater was turning on. It continues to m… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have an armstrong air unit that the combustion blower comes
I have an armstrong air unit that the combustion blower comes on regularly and the heater does not. Sometime it takes 1/2 hour before the heater lights and blowes hot air. This unit was installed in 1… read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x