Carrier gas furnace won't ignite. Fault code 31. It will run…

Carrier gas furnace won't...

Carrier gas furnace won't ignite. Fault code 31

Contractor's Assistant: Did you double-check the thermostat? And what about the pilot light?

It will run blower after 5 minutes

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

Model 58mcb060

Show More
Show Less
Ask Your Own HVAC Question
Answered in 3 minutes by:
1/20/2018
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,631
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. If my initial response doesn’t answer your question then let me know and we can continue our conversation.

A 31 error is a draft pressure switch (see attached pic) error. The question is do you have a bad switch or a weak fan ( is the draft fan running?) or a blocked exhaust vent. You can check the vent for blockages and also the vac tubing connected to the switch. Be sure the tubing is not kinked, deteriorated or doesn't have water in it. You can also poke a paper clip into the port where the tubing connects but not into the switch connection. If all that checks out. Turn the power off to the unit wait a couple minutes then turn it back on. After the fan starts remove one of the leads from the pressure switch and connect it to the other lead. If the sequence continues then you may have a faulty pressure switch or possibly a weak fan. The next thing we would do is put a manometer on the exhaust to check the actual draft pressure but you aren't likely to have a manometer and they are expensive. Replacing the switch is one other option since it's less money than a manometer (or a new draft fan) and it is a likely culprit.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
The furnace never ignites but the inducer fan will run after a couple of minutes

If you want to fix this yourself you need to follow the troubleshooting steps I outlined earlier

Ask Your Own HVAC Question

The inducer should start up immediately upon a call for heat

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Ok. After jumping the pressure switch it ignites
Customer reply replied 7 months ago
After the 5 minutes when the fan starts

So you're saying you have a call for heat and it takes the draft fan 5 minutes to start up? If so does now that it fired up does it still take 5 minutes for the draft fan to start? Did you check the the other possible culprits?
Please differentiate between the draft fan and the main blower that moves air through the vents.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
it takes 5 min. Pull switch leads and connect together then it ignites blow comes on. I letgo of the wires igniter goes off fan stops after a minute. Inducer will then start again since calling for heat.

Ok, so if you ruled out all the other possibilities I listed before then you either have a weak fan or a bad switch.

Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,631
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified
Rick and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Rick Your Own Question
Rick
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,631
24,631 Satisfied Customers
Experience: 40+ yrs. experience as a licensed oil & gas technician.

Rick is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Having error 22 on my carrier furnace. according to the
having error 22 on my carrier furnace. according to the panel error 23 . Check for obstructing error tubing. Pressure switch stuck close … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
HAVE A CARRIER FURNACE 95% MODEL #59SP5A100ES211120. FURNACE
HAVE A CARRIER FURNACE 95% MODEL #59SP5A100ES211120. FURNACE BLINKING 31 THEN BLOWER RUNS THEN INDUCER THEN IGNIGHTER THEN GAS VALVE THEN BLOWER SHUTS DOWN AFTER 20 MINUTES EVEN WHEN R &W JUMPED OUT… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a carrier gas furnace model 59sc2b. It stopped running
I have a carrier gas furnace model 59sc2b. It stopped running because I assume there was insufficient air flow due to a dirty filter. So I changed it and opened the access panel for more than 15 mins.… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
we have a Carrier 58mya080 furnace serial #0398a003a get codes
we have a Carrier 58mya080 furnace serial #0398a003a get codes 12 and 13. At call for heat, pre blower comes on for 90 seconds, no gas, no ignition, especially on damp days after heat not used for day… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
intermittent Carrier Weathermaker 9200 displays a continuous
intermittent Carrier Weathermaker 9200 displays a continuous red led light. What does this mean? How do I know if it is red light 1 or red light 2? Thanks!… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My Bryant furnace is not putting out warm air. I just went
My Bryant furnace is not putting out warm air. I just went and looked at the RED LED status light and it was blinking. After removing both panels and then replacing the top panel, the light remained o… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Payne PG8UAA060135ABJA furnace where the big blower
I have a Payne PG8UAA060135ABJA furnace where the big blower fan comes on instead of the litter exhaust fan that generally comes on just before ignition. What should I do to trouble shoot?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a carrier model 58PAV135-20 furnace. It wont start
I have a carrier model 58PAV135-20 furnace. It won't start and the LED appears to be flashing a code (2 short flashes followed by 4 long flashes). Is there a place online that describes these codes?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a carrier weathermaker 8000 58wav and it shuts down
I have a carrier weathermaker 8000 58wav and it shuts down after running properly for about 5 minutes or so. I then get an error LED blinking message as follows: short blink, long blink, short blink, … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Carrier Model 58zav furnace. Recently as I set it
I have a Carrier Model 58zav furnace. Recently as I set it up to run for the winter season it would not start. It shows a 12 code initially then turns to a 13 code after several minutes. It ran fine w… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Carrier Furnace Weather Master 58mvp. During the winter the
Carrier Furnace Weather Master 58mvp. During the winter the furnace worked and heated but flashed a code of 31 most of the time.… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a Carrier 58pav070-1-08 furnace with a problem. The
I have a Carrier 58pav070-1-08 furnace with a problem. The blower comes on, but it never ignites. It is giving me error code: 31 & 12. There doesn't seem to be any air blockage on the unit. Could it b… read more
TimVZ26
TimVZ26
Service Foreman
Vocational, Technical or Trade Scho
157 satisfied customers
Carrier gas furnace model 58pav111-20. Control board not calling
Carrier gas furnace model 58pav111-20. Control board not calling for induced draft. Diagnostic code # XXXXX Checked induced draft, pressure switch, blocked vent shutoff switch, flame sensor & rollout … read more
Zev Simfukwe
Zev Simfukwe
High School or GED
23 satisfied customers
We have a Carrier 9200 Weathermaker Gas Furnance. It is not
We have a Carrier 9200 Weathermaker Gas Furnance. It is not providing heat. We have turned off the breaker, turned off the switch on the furnance, and turned off the gas switch and back on. That's wor… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hi there, I have a Carrier Weathermaker 8000. From 1994.
Hi there, I have a Carrier Weathermaker 8000. From 1994. My LED diagnostic light is blinking but I do not have an error code legend on my furnace, so I do not know what the flashes mean. Help!… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
my Bryant heater is not working - the led code is #21 - what
my Bryant heater is not working - the led code is #21 - what is involved and what is the cost to fix that problem?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Nov.16, 2009 I have a Carrier Weathermaker in my home. This
Nov.16, 2009 I have a Carrier Weathermaker in my home. This morning I placed the switch to heat, and the unit started it's sequence. However, after a few minutes, it shut down and the blower never cam… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
hav e a carrier model 58mxa gas furnace and glow plug heats
hav e a carrier model 58mxa gas furnace and glow plug heats up and blower runs but does not ignite gas code 31 onprocesser lite checked pvc pipes looks ok… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x