I have a GSZ130421AE condensing unit and ARUF486016CA air…

I have a GSZ130421AE...

I have a GSZ130421AE condensing unit and ARUF486016CA air handler. The heat pump intermittently comes on and may operate a few minutes. When it stops operating, the air handler continues to run until it is switched off. The condensing unit may or may not start again.

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

The setting is 72 and filters are new.

Contractor's Assistant: Do you plan on doing the work yourself?

Yes, if possible. I replaced the fan board today and nothing has changed.

Show More
Show Less
Ask Your Own HVAC Question
Answered in 11 minutes by:
1/19/2018
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,366
Experience: Furnace, A/C and heat pump specialist.
Verified

You may have more than one issue here.Let me get some details.

1.Is this a new system or did it used to work and just started doing this?

2.Has thermostat or any other changes been made?

3.Does it do this in heat mode cool mode or both?

4.ARe you a technician or homeowner and do you have tools for troubleshooting?

My name is ***** ***** I am happy to be able to work with you on this today.Please be patient as I respond as sometimes it takes me a few moments to gather proper manuals and specifications on your equipment in order to provide accurate answers.Please wait until we are finished to rate my answer.Hopefully at that time I will have earned a five star rating.Now just to let you know, the website does offer a live phone call for one on one discussion for an additional fee. Due to my current work load and responsibilities I may not be available for the live phone call but along the way, the website will automatically present the offer.Please note that there is an additional cost for the service and if a technician calls it may be a different technician. However we can continue here as long as needed .

Ask Your Own HVAC Question
Customer reply replied 7 months ago
The system is 4 years old (Goodman). The thermostat has not been changed or checked. The cool is fine but the heat is the problem.
I am a homeowner not a HVAC tech but have experience with repairing a vast variety of electrical/electronic equipment as well as mechanical. I have ac gauges, freon, volt meters and various other tools.

THanks for this information. Now lets start with the issue of the outdoor unit.Since unit works fine in cool mode I suspect the TXV (Metering device) in the outdoor unit may be sticking and be the culprit for outdoor unit not staying on.The only difference between heat and cool modes is that in Cool mode the TXV at indoor coil meters refrigerant and in heat mode the txv at outdoor coil meters refrigerant.

If the txv sticks closed that will create a restriction and unit shuts down on low pressure

If we connect gauges and watch pressures do you think it will fail while we are watching them?Or does it sometimes run quiet a while?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
I can get the gauges connected and switch from strip heat to heat pump and see if outside unit will immediately start. Its erratic.

That would be great, See if the suction starts to drop and head starts to rise just before it shuts down.Remember to connect the suction gauge to the true suction port rather than the large valve since we are in heat mode.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
66 low 50 High. Outside temp 40

System is low on refrigerant.It will short cycle soon if it has not already

Ask Your Own HVAC Question

t 40 degree ambient we should be at about 125/350

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Unit has not started. I had strip heat on before I switched and after connecting gauges

LOL. Let me know when it starts.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
I can switch gauges but each is calibrated for 410a

UNit should be 410a isn't it?

Ask Your Own HVAC Question

UNit came on yet?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Nope but the blower is working

UNit seriously may be too low for it to come on. Manually energize contactors and watch gauges

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Ok I’ll take the cover off and let u know. Hang on

Take your time

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Ok
Customer reply replied 7 months ago
It’s off .

Watch gauges while depressing and see what pressures do

Ask Your Own HVAC Question
Customer reply replied 7 months ago
No change. It’s making a rattling sound below the fan

THat's not good. Let's try cool mode since it WAS working on cool mode.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Ok. Its in cool mode

anything come on and if so what are pressures?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
It’s on. I’ll ck pressure

OK

Ask Your Own HVAC Question
Customer reply replied 7 months ago
16 large line 25 small line

System should not even stay on with pressures that low

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Ac works.

Feel of copper lines and tell me if one is really cold as it should be in cool mode?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
It just cycled back on and they are about the same, although the suction is insulated. Wierd. When the heat works, the high side is cold and now it and the low side is cold.

I don;t thin the compressor is pumping.The large line should be so hot you can't touch with about a 350psig head in heat mode and the large line should be beer can col and running about a 300 head

Ask Your Own HVAC Question

THis unit should be under warranty for another 6 years so I recommend getting a Goodman dealer out there to see what is going on.WE have already spent an hour and a half, way beyond a simple question and answer and am no closer to a resolve than when we started.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
I think you are correct. I appreciate your help and will get the local distributor to do something about it.
Thanks for you time.

Thanks for letting me work with you.If my answer has been polite, professional,and thorough, please click one of the ratings before you go. If you still need help let me know!.Expert is not paid for assisting you until you rate answer.Feel free to follow up for 30 days at no additional cost. Bonus always appreciated if you feel justified.
To rate answer, please select one of the stars on the page.
Leaving a poor service rating will not automatically refund your money,but reflects poorly on your expert. You have to request a refund if not satisfied with the information provided being accurate.

airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,366
Experience: Furnace, A/C and heat pump specialist.
Verified
airheatman and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,366
9,366 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
2shp13le136p-1 heat pump, heat pump will not come on unless
2shp13le136p-1 heat pump, heat pump will not come on unless I manually hold contactor in, how do jump thermostat or test it for voltage? … read more
airheatman
airheatman
HVAC Technician
6 years college
9,366 satisfied customers
I have a lennox 4 ton high effiency 16 sear unit installed
I have a lennox 4 ton high effiency 16 sear unit installed 3/2016. my unit on heat not a heat pump has heat strips .the unit thermostat is set at 74 degrees now. the unit starts up and runs 3 min cuts… read more
hvacdave84
hvacdave84
53 satisfied customers
I have a Goodman GSZ140301 with heat pump. It was installed
I have a Goodman GSZ140301 with heat pump. It was installed last year but the thermostat only allowed heat or cooling. I had the thermostat switched so that it could go between heat and cooling by a s… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
Trane twe048c140b0 fan operates intermittent. When fan runs,
Trane twe048c140b0 fan operates intermittent. When fan runs, heat pump system operates otherwise normally. … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Goodman air handler model mbe2000aa-1. Installed in 2005. In
Hi, goodman air handler model mbe2000aa-1. Installed in 2005. In ace mode only, air handler fan runs constantly. In heat mode, fan runs 60 to 90 seconds after compressor stops. Suspected control board… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
Have a a carrier air handler and a trane heat pump
Have a a carrier air handler and a trane heat pump condenser. When the t stat calls for heat the indoor unit comes on immediately and blows cold air for about 3-4 min then hot air. And help would be g… read more
airheatman
airheatman
HVAC Technician
6 years college
9,366 satisfied customers
I have a 2009 Luxaire Acclimate Modulating gas furnace...it
I have a 2009 Luxaire Acclimate Modulating gas furnace...it is turning on at correct programmed time, but not to desired temperature. Thermostat has been replaced. It is supposed to come on at 6am and… read more
airheatman
airheatman
HVAC Technician
6 years college
9,366 satisfied customers
Billy, You answered my question fan. It worked. Today I
Billy, You answered my question for condenser fan. It worked. Today I noticed that while running in ac mode, it started blowing warm air. compressor and condenser fan is running, the large copper tube… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Goodman air handler Goodman 5 ton a/c (not used
I have a Goodman air handler for a Goodman 5 ton a/c (not used for heating). When I have the fan switch on the thermostat (non programmable Honeywell) set to auto and the switch set to cool - the unit… read more
AssuredElectrical
AssuredElectrical
Electrical Contractor
High School or GED
332 satisfied customers
I have a Lennox XP14 heat pump that wont operate correctly.
I have a Lennox XP14 heat pump that won't operate correctly. The other day I noticed that the "Check Filter" notice was flashing on the thermostat so I replaced the filter and pushed the reset button … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
Nordyne Model#GB5BM-T36K-B air handler. Unit has stopped pumping
Nordyne Model#GB5BM-T36K-B air handler. Unit has stopped pumping air in-house. Have reset thermostat several times and changed air filter as well. Outside heat pump / condenser continues tp work. Cann… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Does anyone have experience with the necessary control upgrade(s)
Does anyone have experience with the necessary control upgrade(s) required to let a Rheem air handler (7KW electric heat already installed) operate fully - particularily for defrost tempering - with a… read more
V12Tech
V12Tech
252 satisfied customers
The other night, I was cold, so I turned off the air conditioner
The other night, I was cold, so I turned off the air conditioner (Lennox heat/cool pump) at the digital control in the house. When I turned it back on the next morning, nothing happened. The digital d… read more
airheatman
airheatman
HVAC Technician
6 years college
9,366 satisfied customers
Periodically (once or twice per week) my unit will be running
Periodically (once or twice per week) my unit will be running outside but no air is entering the house thought the vents in each room. Thermostat is set at 72 and temp. in house will show as 79. Then … read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have a T8411R Honeywell thermostat connected to an Armstrong
I have a T8411R Honeywell thermostat connected to an Armstrong Heat Pump. When I turn the thermostat to heat...unit kicks on...runs normal cycle...heats the house...but fans does not stop (on auto set… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
honeywell model th6220d 1028 achieves set temp for heat, runs
honeywell model th6220d 1028 achieves set temp for heat, runs but fan circulator fan continues to run, blows cool air, then heat comes back why will fan not shut off… read more
Master tech
Master tech
High School or GED
62 satisfied customers
I have an 11 year old Goodman heat pump (CPKE24-1AB). I have
I have an 11 year old Goodman heat pump (CPKE24-1AB). I have had two instances in the past week where the air handler blower did not start when the outside unit came online. Everything else appears to… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
installed a New Amana air conditioning system last year. Turned
installed a New Amana air conditioning system last year. Turned it on this year and the unit runs outside but it doesn't appear the blower in the base ment unit is working...Now it's Friday evening an… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x