I have a reznoir 60k btu heater in my garage, a couple of months old, I installed it, i have a two wire thermostat wire to it and have it set at 62 degrees sometimes I have noticed it will shut down for no reason, when this happened I found that taking the thermostat off of its electrical prongs seemed to reset and it would start working again but today that did not work. i have checked to make sure it has power but did not take off the cover to check the green light inside

Contractor's Assistant: Just to clarify, do you think this is a larger HVAC problem, or something specific to the thermostat?

I guess im not sure, if i cross the wires from the thermostat will that cause the heater to come on, that way I could tell if its the thermostat

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

I think thats everything, the exhasat is only about 3 feet long but is flexible, like a dryer vent because that was all i had at the time

Show More
Show Less
Ask Your Own HVAC Question
Answered in 22 minutes by:
1/18/2018
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 682
Experience: Owner at Gaztech
Verified

Hi I amCustomer a independent technician, I will assist you with your issue.

Don't forget to rate the 5 star rating AT THE TOP OF PAGE when we are done. this will credit me for assisting you.

What model is it

Ask Your Own HVAC Question
Customer reply replied 1 month ago
UDAP-60 i believe

You could try putting the 2 t-stat wires together to see if its t-stat related

but you really need to get the error code to proceed

Ask Your Own HVAC Question
Customer reply replied 1 month ago
ok if i take off the side cover there is a green light in the unit, is there an error code in there or is this like a car, you need a tool to hook up to it and read the unit to tell what the error code it

Count the amont of flashes between pauses, thats will give us the error code and then look on chart to know whats wrong on page 20 of this manual

http://www.ozheating.com/uploads/3/1/8/1/31810529/reznor_garage_heater_udap_installation.pdf

There should be same chart in your unit

Ask Your Own HVAC Question
Customer reply replied 1 month ago
the green light was on solid so i disconnected the thermostat and crossed the wires and it turned on the thermostat is a honeywell rth636od1002 so im assuming there is something about the thermostat interstingly the back of the thermostat has like 13 possible wire connections i used the w for white wire and r for red wire but am not sure if there is another way you are suppossed to hook it up

Thats right

Ask Your Own HVAC Question

did you leave jumper between R and RC?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
i did not touch that

Did you do system set up on t-stat?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
there is a little door that can be pushed up to cover part of the rc, im not sure in what position it has to be in to be jumped or not
Customer reply replied 1 month ago
what is tstat

Thermostat

Ask Your Own HVAC Question
Customer reply replied 1 month ago
does it matter if they are connected

Little door position, not sure, look in manual

Ask Your Own HVAC Question

Did you do system set up on t-stat?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
not really, i just put the temperature to 61 and press hold

Thats why!!

Get your manual and go into system set up and finish the job

Ask Your Own HVAC Question

Hows it going?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
I set up the thermostat but it is still not turning on the heat I’m going to call Honeywell tomorrow and see what vthey say

Did you figure little door for R and RC jumper?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
I did not change its position but am going to ask about it tomorrow tks for ur help though

Please Don't forget to rate the 5 star rating AT THE TOP OF PAGE if we are done. this will credit me for assisting you.

Best regards

Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 682
Experience: Owner at Gaztech
Verified
Gaztech and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 1 month ago
Got it

Cheers!

Ask Your Own HVAC Question
Was this answer helpful?
Ask Gaztech Your Own Question
Gaztech
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 682
682 Satisfied Customers
Experience: Owner at Gaztech

Gaztech is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a 2 zone system in a ~2000 sf home, with upstairs and
I have a 2 zone system in a ~2000 sf home, with upstairs and downstairs on separate zones with a honeywell controller. I am in the process of finishing the attic (~360 Sq ft), and would like to set th… read more
Bill
Bill
Service Mgr
20 satisfied customers
I have a 40 gal Rheem Warrior Glass for manufactured
I have a 40 gal Rheem Warrior Glass for manufactured housing. It is a propane conversion S/N RHLN0709800063 Model # 22140FDVX. There is no hot water, the pilot light is lit but nothing to the burner. … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My heater is not working. The flame icon is flashing,
Hi. My heater is not working. The flame icon is flashing, indicating it's trying to turn the heater on but I hear no clicking sound for the furnace pilot and no heated air is coming through. All wires… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a heatilator gas fireplace and when I turn it on the
I have a heatilator gas fireplace and when I turn it on the flame is extremely low. The pressure in the gas line is correct and the pipes to the burner are clear. I am thinking something is going on w… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My rinnai is beeping and the filter light is flashing. The
My rinnai is beeping and the filter light is flashing. The filter is very clean … read more
Bill
Bill
Service Mgr
20 satisfied customers
When the furnace comes on it has a sewer smell. It was
When the furnace comes on it has a sewer smell. It was really strong yesterday when it rained all day. We first noticed it last summer when the AC came on. We recently had a new roof put in and I wond… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
On hot water heater when main burner comes on it blows out
on hot water heater when main burner comes on it blows out the pilot light … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My Goodman furnace is blowing cold air. No flame noted.
My Goodman furnace is blowing cold air. No flame noted. Light flashes … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Raypak pool heater. It turns on lights a spark etc.
I have a Raypak pool heater. It turns on lights a spark etc. but the display does not show any lettering..I do not know what mode I am in. No words show up. … read more
Chris Wagner
Chris Wagner
None
7 satisfied customers
Last week we had our Nortiz fixed and they replaced the
last week we had our Nortiz fixed and they replaced the large copper unit and it worked fine...today when there was no hot water, we saw the unit was off with a red blinking light...we turned it on an… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
We want to control a 230v damper for air conditioning to one
Hi, we want to control a 230v damper for air conditioning to one room. … read more
Bill
Bill
Service Mgr
20 satisfied customers
We had an addition put on the house and now have dual zone.
We had an addition put on the house and now have dual zone. Some of the returns are no longer used and were capped off. 1 unused return is fully exposed in the unfinished basement. Can I remove it an … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I'm working on a 3 phase 575 v 2 hp semi-hermetic. Yesterday
yesterday im almost certain it's siezed but maybe something just not right … read more
Bill
Bill
Service Mgr
20 satisfied customers
Have heat pump it was working great. husband tried to
have heat pump it was working great. husband tried to replace thermostat and now ac condenser is not running. he reinstalled old thermostat and ac condenser is still not running. He did turn off power… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Pilot light won't start burner. About 8 hours. It's a evcon
Pilot light won't start burner JA: I'll do all I can to help. How long have you been dealing with this? Customer: About 8 hours JA: Do you plan on doing the work yourself? Customer: Yes JA: Anything e… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a water heater and seem t be running out of hot water
I have a water heater and seem t be running out of hot water very quickly. Any idea what the problem could be.m … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Having trouble with short cycles on a BIASI series QHT oil
having trouble with short cycles on a BIASI B series QHT oil burner. cycles 4-6 times within 2-3 minutes multiple times as it trys to reach high temp shutoff. how to fix ? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I just pulled down a rheem P/N 41-20804-15 from my
I just pulled down a rheem P/N 41-20804-15 from my downstairs and I am installing a honeywell Wi-Fi thermostat need to confirm wiring placement in honeywell unit? … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x