I have a reznoir 60k btu heater in my garage, a couple of…

I have a reznoir...

I have a reznoir 60k btu heater in my garage, a couple of months old, I installed it, i have a two wire thermostat wire to it and have it set at 62 degrees sometimes I have noticed it will shut down for no reason, when this happened I found that taking the thermostat off of its electrical prongs seemed to reset and it would start working again but today that did not work. i have checked to make sure it has power but did not take off the cover to check the green light inside

Contractor's Assistant: Just to clarify, do you think this is a larger HVAC problem, or something specific to the thermostat?

I guess im not sure, if i cross the wires from the thermostat will that cause the heater to come on, that way I could tell if its the thermostat

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

I think thats everything, the exhasat is only about 3 feet long but is flexible, like a dryer vent because that was all i had at the time

Show More
Show Less
Ask Your Own HVAC Question
Answered in 22 minutes by:
1/18/2018
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 856
Experience: Owner at Gaztech
Verified

Hi I amCustomer a independent technician, I will assist you with your issue.

Don't forget to rate the 5 star rating AT THE TOP OF PAGE when we are done. this will credit me for assisting you.

What model is it

Ask Your Own HVAC Question
Customer reply replied 4 months ago
UDAP-60 i believe

You could try putting the 2 t-stat wires together to see if its t-stat related

but you really need to get the error code to proceed

Ask Your Own HVAC Question
Customer reply replied 4 months ago
ok if i take off the side cover there is a green light in the unit, is there an error code in there or is this like a car, you need a tool to hook up to it and read the unit to tell what the error code it

Count the amont of flashes between pauses, thats will give us the error code and then look on chart to know whats wrong on page 20 of this manual

http://www.ozheating.com/uploads/3/1/8/1/31810529/reznor_garage_heater_udap_installation.pdf

There should be same chart in your unit

Ask Your Own HVAC Question
Customer reply replied 4 months ago
the green light was on solid so i disconnected the thermostat and crossed the wires and it turned on the thermostat is a honeywell rth636od1002 so im assuming there is something about the thermostat interstingly the back of the thermostat has like 13 possible wire connections i used the w for white wire and r for red wire but am not sure if there is another way you are suppossed to hook it up

Thats right

Ask Your Own HVAC Question

did you leave jumper between R and RC?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
i did not touch that

Did you do system set up on t-stat?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
there is a little door that can be pushed up to cover part of the rc, im not sure in what position it has to be in to be jumped or not
Customer reply replied 4 months ago
what is tstat

Thermostat

Ask Your Own HVAC Question
Customer reply replied 4 months ago
does it matter if they are connected

Little door position, not sure, look in manual

Ask Your Own HVAC Question

Did you do system set up on t-stat?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
not really, i just put the temperature to 61 and press hold

Thats why!!

Get your manual and go into system set up and finish the job

Ask Your Own HVAC Question

Hows it going?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
I set up the thermostat but it is still not turning on the heat I’m going to call Honeywell tomorrow and see what vthey say

Did you figure little door for R and RC jumper?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
I did not change its position but am going to ask about it tomorrow tks for ur help though

Please Don't forget to rate the 5 star rating AT THE TOP OF PAGE if we are done. this will credit me for assisting you.

Best regards

Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 856
Experience: Owner at Gaztech
Verified
Gaztech and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 4 months ago
Got it

Cheers!

Ask Your Own HVAC Question
Was this answer helpful?
Ask Gaztech Your Own Question
Gaztech
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 856
856 Satisfied Customers
Experience: Owner at Gaztech

Gaztech is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have an estimate for a new HVAC system. Could you take a
I have an estimate for a new HVAC system. Could you take a look and see if reasonable in your judgment? My home is approx 13500 square feet with three bedrooms, two baths, and he is going to put an ad… read more
Gaztech
Gaztech
HVAC Technician
856 satisfied customers
I have a Trane 5-ton, 2-speed 16 SEER unit and a 4-story
Hello. I have a Trane 5-ton, 2-speed 16 SEER unit and a 4-story home that was installed with a Honeywell 4-zone thermostat system. Is this a proper installation? … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
My main ac unit just stopped today. The fan on the unit
My main ac unit just stopped today. The fan on the unit won't spin. We had the roof replaced today as well so I'm curious if they accidentally broke something. … read more
Gaztech
Gaztech
HVAC Technician
856 satisfied customers
We have a gas C Heating system we wish to connect radiators
We have a gas C Heating system we wish to connect radiators to a wood burning fire with back boiler. … read more
Plumbers_Mate
Plumbers_Mate
General Manager
Vocational, Technical or Trade Scho
2 satisfied customers
I have just purchased a fridigidare 5,000 btu window AC.
I have just purchased a fridigidare 5,000 btu window AC. It's installed but when looking at the front I am noticing condensation forming on the left front bottom. Where there is a metal bar the runs a… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Do I need a return built in every room of the house with a
Do I need a return built in every room of the house with a new A/C system? Ours is super old and getting a new one put in.… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Trying to locate thermostat panel on Carrier Comfort 13
trying to locate thermostat panel on Carrier Comfort 13 48ES-A … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I recently viewed a potential home to purchase.
Second opinion] I recently viewed a potential home to purchase. ?Coincidently?, the 900 sq ft basement was flooded by what the seller reports that as due to the float in his humidifier getting stuck a… read more
HvacmanSean
HvacmanSean
Owner
HVAC
233 satisfied customers
How much water will dump from the humidifier if float was
How much water will dump from the humidifier if float was “stuck” for a 24-48 hr period? This was my second walk through (first was before the storm) then less than 48 hours after, the basement is wet… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a 50D50-842 direct spark control using the spark rod
I have a 50D50-842 direct spark control using the spark rod for flame detection. When the demand for heat is applied, the spark starts, the slow open Honeywell valve delivers gas, the main burner igni… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have an "all in one" furnace and air conditioning unit in
Hi Tom - I have an "all in one" furnace and air conditioning unit in a condominium closet. The a/c is what I am having trouble with. In order to get the temperature down without the coil icing up I ha… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a 10 year-old Carrier 25HNA660A003 heat pump. At the
I have a 10 year-old Carrier 25HNA660A003 heat pump. At the beginning of the season I kept getting "failed to start" errors so I replaced the start capacitor and the system fired right up and worked f… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
On my second floor thermostat I lost the WiFi connection. It
On my second floor thermostat I lost the WiFi connection. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I am replacing a evaporator on a refrigerator and I have a
I am replacing a evaporator on a refrigerator and I have a FB12 flame barrier. It has two sides and aluminum and fiberglass. There's a little sticker on the aluminum side saying do not use the side to… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I bought a new thermostat and cant figure out the wiring.
i bought a new thermostat and cant figure out the wiring … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Our rheem a/c unit stopped working? the a/c unit was on, it
the a/c unit was on, it suddenly stopped working. we tried resetting the thermostat but it still did not operate. the furnace has a bright red lamp on the top of the unit, I unplugged the unit from the wall and plugged it back in. the a/c unit began to work but only for a few minutes. the red lamp came on and the unit stopped to work. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
My carrier heat pump is reporting error code 82 (high stage
hi, my carrier heat pump is reporting error code 82 (high stage thermal lockout) … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have a Trane XE 900 that the fan and compressor stopped
Good morning. I have a Trane XE 900 that the fan and compressor stopped coming on. From what I have learned so far, sounds like the start capacitor has failed. However, when I open up the access panel… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x