Trying to connect a new ecobee4 thermostat to my gas

Trying to connect a...

Trying to connect a new ecobee4 thermostat to my gas furnace/AC. The control board shows wires attached to W,R,T,G screws, and the thermostat has connectors to W,R,Y,G. Since I don't have a common wire, I need to use a PEK adaptor to the control board. The T-wire use is confusing me, since they didn't use the Y-wire at the control board. Any suggestion?

Contractor's Assistant: Did you double-check the thermostat? And what about the pilot light?

It's working fine with the old thermostat, no problem for 25 years. My question concerns how to connect the PEK to the control board, since they didn't use the Y-wire connector.

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

Don't think so.

Show More
Show Less
Ask Your Own HVAC Question
Answered in 8 minutes by:
1/17/2018
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,905
Experience: Furnace, A/C and heat pump specialist.
Verified

Can you give me the mode on your furnace?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
Not sure what you mean by mode

TYpo MODEL So I can pull a manual)Welcome to the JustAnswer/Pearl website.My name is ***** ***** I am happy to be able to work with you on this today.Please be patient as I respond as sometimes it takes me a few moments to gather proper manuals and specifications on your equipment in order to provide accurate answers.Please wait until we are finished to rate my answer.Hopefully at that time I will have earned a five star rating.Now just to let you know, the website does offer a live phone call for one on one discussion for an additional fee. Due to my current work load and responsibilities I may not be available for the live phone call but along the way, the website will automatically present the offer.Please note that there is an additional cost for the service and if a technician calls it may be a different technician. However we can continue here as long as needed .

Ask Your Own HVAC Question
Customer reply replied 1 month ago
Can't find model or original manual.
Customer reply replied 1 month ago
Have photo of control board connectors, but that doesn't help.

Should be on a label above burners on inside panel.

https://i.imgur.com/U8b0GXT.jpg

Do you know brand?

Ask Your Own HVAC Question

Attach photo that may be enough

Ask Your Own HVAC Question
Customer reply replied 1 month ago
Lenox, but haven't found label

Use the "add file button and send me photo

Ask Your Own HVAC Question
Customer reply replied 1 month ago
Model G1703-75-1

Thanks for your patience. The T on your board is actually C (common).

So if you had an extra wire in the bundle to thermostat you could attach it to C at thermostat and T on board and not need the pek adapter.

But since we only have 4 wires to thermostat this is what we will do:

R from board to R on Pek

W on board to W on Pek

G from board to G on Pek

Then we need a wire from the blue (along with the red from outdoor unit to Y on the Pek

Ask Your Own HVAC Question

Forgot to list but also a wire from T on board to C on Pek

Ask Your Own HVAC Question
Customer reply replied 1 month ago
I think I have it, but going to have to study email and draw it out. Pek has no C input, but has C output to board. Am still not sure about blue wire, whether to tie to Pek, with another wire, or take off board. Let me study this. Email?

Look it over and let me know of any questions.Here is what you will have :

Furnace------------(IN) PEK (OUT)---------------------Thermostat

R-------------------------- R/R---------------------------R

G--------------------------G/G---------------------------G

W--------------------------W/W--------------------------W

T---------------------------C

Red wire from outside----Y/Y(Blue) ---------------------Y

Ask Your Own HVAC Question

T on your board is C

Ask Your Own HVAC Question
Customer reply replied 1 month ago
I read the Pek instructions as disconnect the wires from the thermostat and go Into the Pek, and wires Out of the Pek connect to the control board. I read your directions backwards from that. That is my confusion. Sorry

Does this make more sense now? If so let's connect everything

Ask Your Own HVAC Question
Customer reply replied 1 month ago
I still see it backwards. Thermostat (Out) -------(In) PEK (Out)------Furnace control board. Only way it works with 4 in 5 out from Pek. Am I wrong?

I will draw it. 5 in from furnace 4 out to thermostat.Stand by

Ask Your Own HVAC Question

Drawing now.Stand by

Ask Your Own HVAC Question
Customer reply replied 1 month ago
thanks for your extreme patience. I will give it a go.

Let me know. When we are done,If my answer has been polite, professional,and thorough, please click one of the ratings before you go. If you still need help let me know!.Expert is not paid for assisting you until you rate answer.Feel free to follow up for 30 days at no additional cost. Bonus always appreciated if you feel justified.
To rate answer, please select one of the stars on the page.

airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,905
Experience: Furnace, A/C and heat pump specialist.
Verified
airheatman and 87 other HVAC Specialists are ready to help you
Ask your own question now
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,905
8,905 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
display backlite not working on honeywell thermostat #TH6220D.
display backlite not working on honeywell thermostat #TH6220D. can this be fixed?… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
LUX XT500E thermostat is flashing "FAN" and heater won't turn on
My LUX XT500E thermostat has been flashing the word "FAN" and my heater won't turn on because of it. I have tried online suggestions of restarting it and taking out the batteries, then putting them ba… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
My furnace (Rheem Classic 90 Plus) runs only if the panel is
My furnace (Rheem Classic 90 Plus) runs only if the panel is off. When the panel is replaced, the flame on the burners goes out and the system cycles every few minutes. when I re-set the system and op… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I, I installed a furnace control Board part # 62-24084-82.
I, I installed a furnace control Board part # 62-24084-82. It cycled once and will will not cycle again. all the controls are ok after checking them. any Ideas? … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Xrv95 trane furnace. Power to unit, fuse ok, transformer ok,
xrv95 trane furnace. Power to unit, fuse ok, transformer ok, Circuit breaker ok. Power to furnace. Changed thermostat batteries. Problem is fan will not run even in on position. No heat. No codes, no … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Both of my TH8321WF1001 Honeywell thermostats have gone
Both of my TH8321WF1001 Honeywell thermostats have gone dark? Seems like no power is going to it but I checked circuits and none are tripped.… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
Have an t8411r thermostat. After several failed attempts to
have an t8411r thermostat. After several failed attempts to change temp. I turned off circuit breaker ---now screen is blank … read more
airheatman
airheatman
HVAC Technician
8,905 satisfied customers
I wanted to replace a T8112D Thermostat with an RTH 111B and
I wanted to replace a T8112D Thermostat with an RTH 111B and in removing the T8112D, I accidentally touched the red and white wires. The system went on. I relaced the thermostat and the Air Cond came … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I am having heating issues with what I believe is my
Hi Pearl... my name is ***** ***** I am having heating issues with what I believe is my thermostat … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
How can I tell I my York furnace control board is the cause
How can I tell I my York furnace control board is the cause of the furnace not completing the heat cycle. It shuts down and give me the pressure sensor/switch code but two tech's have been out and ver… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
This is the same guy with the Goodman furnace control board
Hi, this is the same guy with the Goodman furnace control board / transformer. My plumber said what caused the board to fail was a short in the blower motor from water from AC unit backing up into blo… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Goodman GMNTE120-5 It has a furnace/control board
I have a Goodman GMNTE120-5 It has a furnace/control board with this part number B1809925two of the wires have come off two connectors, and the wires are the same color - trying to determine if it mat… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I recently replaced my furnace control board. The furnace is
I recently replaced my furnace control board. The furnace is a Lennox G40-OUH and the control board was a White Rodgers 50-A65-121-07. The only replacement was a White Rodgers 50A65-843 Universal Boar… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have an amana furnace control board with an led flashing 3
I have an amana furnace control board with an led flashing 3 times … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I need help with my -Rodgers furnace control board 50e47-060
I need help with my White-Rodgers furnace control board 50e47-060 on a Trane furnace. It has a blinking red light. On the unit it says " steady red light- replace control, blinking red light-referred … read more
type2technician
type2technician
253 satisfied customers
I have a nordyne KG7TC-080D, with a furnace control board
I have a nordyne KG7TC-080D, with a furnace control board #624790/920916. this is a 2-stage upflow unit. Furnace ignites but goes out wihin seconds. flame sensor replaced, still the same issue. Has in… read more
airheatman
airheatman
HVAC Technician
8,905 satisfied customers
I think that I may have a bad furnace control board. Trouble
Hello I think that I may have a bad furnace control board. Trouble shooting so far. Two different thermostats with the same behavior. Direct connection of the R&W&G wires make the furnace run continuo… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My furnace control board light is not coming on. Yes, the
My furnace control board light is not coming on. JA: Did you check the furnace's filters? Customer: Yes, the furnace filter is new. JA: Do you plan on doing the work yourself? Customer: Yes. JA: Anyth… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x