I have a Rodgers 50A55-288-05. Furnace has been working but…

I have a white...

I have a white Rodgers 50A55-288-05. Furnace has been working but no on the control board I am getting 3 flashing lights and ignition switch does not heat up. Exhaust fan tuns on but burners and ignition do not. What should I look for as possible problems

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Filter little dirty not bad but changed and thermostat is at 69 and temp in home is 61

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

Changed ignition switch did not help

Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 minutes by:
1/17/2018
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,747
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified

One moment please..Note it takes time to type and add links so please be patient. Also the site will send you a phone call offer, that is not me.

Ask Your Own HVAC Question

That is a pressure switch code, meaning the pressure switch is not closing when the exhaust fan is coming on. So you need to check and make sure the exhaust fan comes on first. You can cycle the power off to the unit at the switch or breaker for a minute and turn it back on to clear the code and restart a heat cycle making sure the thermostat is on or you have R to W jumpered on the board in the furnace. If the fan does not come on check the fan for power. If the fan does come on and nothing is plugged in the exhaust or intake vent then check the pressure tube for blockages. That is the rubber tube that connects the pressure switch to the blower housing. If that tube is blocked or cracked that code will come up. You need to check the port where the tube connects to the exhaust blower housing make sure that port is not blocked with crud. Normally it is one of these issues causing that code on the furnace. Lastly you have to check all condensate lines on the unit, especially the drain line that comes out of the inducer motor housing to make sure nothing is blocked causing a backup of condensate water.

All I ask is...Please remember to use the RATING LINK ON YOUR PAGE by selecting a star at the top or bottom of the screen before you leave today. Even though you paid the site they will not disburse any part of it to me until you supply a good rating. If you need anything else, just let me know. You can continue asking follow-up questions at no additional charge after rating my service if you still need assistance.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
The exhaust fan does come on right away

Ok did you check the pressure tube and ports?

HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,747
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified
HVAC Guru and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 7 months ago
Where is the pressure tube located
Customer reply replied 7 months ago
Is the rubber tube inside the exhaust vent where it attaches to the exhaust fan
Phone call session started

Yes the rubber tube that comes off the inducer motor housing goes to the pressure switch check that tube and port

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Thank you that was the problem the port was clog cleaned out and working like a champ again. I have had this happen 4 years ago but forgot but once you directed me to where I needed to look I remembered. Thanks worth the $23.

No problem

Ask Your Own HVAC Question
Customer reply replied 7 months ago
No phone call was ever made do not charge my card for that.Thank you.
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask HVAC Guru Your Own Question
HVAC Guru
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,747
18,747 Satisfied Customers
Experience: 20yrs in the HVAC industry with certificates and degrees.

HVAC Guru is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
What is the heat anticipator setting on my -Rodgers
What is the heat anticipator setting on my White-Rodgers 1E56N-444 thermostat, for Amana Air Command 80 SSE? … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Getting continuous led blinking on rodgers 50A55-480 when
Getting continuous led blinking on white rodgers 50A55-480 when calling for heat. Furnace ignites and then shuts off … read more
Webb-Guy
Webb-Guy
Maitenance Supervisor
Associate Degree
3,335 satisfied customers
Rodgers 50a55-288 Furnace Control Board Amana 102077-09,
White Rodgers 50a55-288 Furnace Control Board Amana 102077-09 … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Hello, I have a York Diamond 80 upflow furnance and it stopped
Hello, I have a York Diamond 80 upflow furnance and it stopped working today. Just 1 flash on the control board (system lockout). Few days ago it had 7 flashes (low flame sense signal). I tried to pow… read more
theplumber717
theplumber717
Plumber
Vocational, Technical or Trade Scho
791 satisfied customers
I have a 2001 Amana 90 Air Command gas furnace that has a moisture
I have a 2001 Amana 90 Air Command gas furnace that has a moisture problem and will not run. They thought it was the ignition control unit, as the unit tries to start, then stops. But there is visible… read more
HVAC Guru
HVAC Guru
HVAC TECH
18,747 satisfied customers
I have an Amana 80 SSE furnace with a White Rodgers 50A55-288
I have an Amana 80 SSE furnace with a White Rodgers 50A55-288 Integrated Control Module. If I have my thermostat on heat and I manually close the blower access door switch the following sequence occur… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
HAVE A TRANE UNIT AND FURNACE WOULD NOT IGNITE.FOUND CIRCUIT
HAVE A TRANE UNIT AND FURNACE WOULD NOT IGNITE.FOUND CIRCUIT BOARD BURNT.OLD NUMBER IS XXXXX RODGERS 50A55-480.NEW NUMBER IS XXXXX RODGERS 50A55-843.JUMPED RO1 TO RO2 . IGNITOR WORKS NOW BUT SEEMS TO … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a white-rodgers universal 50A55-843 with diagnostic
I have a white-rodgers universal 50A55-843 with diagnostic indicator flash code 4 open high temp limit switch flashing....the furnace only blows cold air.. I bypassed the limit switch and the burners … read more
V12Tech
V12Tech
252 satisfied customers
I have an amana 90 furnace that lights and turns off in minutes.
I have an amana 90 furnace that lights and turns off in minutes. The light blinks once them goes off.… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Hi, I think I have a problem with the control board on my
Hi, I think I have a problem with the control board on my York Diamond 80 gas furnace. Keep getting 3 blinks (pressure switch stuck open or closed...don't remember which). Replaced pressure switch and… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a white-rodgers universal 50A55-843 with diagnostic
I have a white-rodgers universal 50A55-843 with diagnostic inicator flash code 4 open high temp limit switch flashing....the furnace only blows cold air....what to do??? Thanks Tracy… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Twice now, Ive come home and the house is cold. Thermostat
Twice now, I've come home and the house is cold. Thermostat shows setting at 67, and temp at 61. When I've gone to check the furnace, the exhaust fan is running, but burners are not going. Last night,… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
My furnace blower has been running constantly despite being
My furnace blower has been running constantly despite being set to auto, however the gas only kicks on intermittently stay on at best for 10 min atva time. It has been unusually cold and my home is in… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Hunter 42999B Thermostat. The furnace was running
I have a Hunter 42999B Thermostat. The furnace was running properly until I Changed the Batteries and Changed the Filters in the furnace. Now..... the furnace is still blowing heat, but the thermostat… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
Hello, I have a Trane XL80 that appears to be running fine.
Hello, I have a Trane XL80 that appears to be running fine. When it reaches the desired temperature set by a programmable thermostat it shuts down as it's supposed to. The problem somes when the tempe… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
American Standard Furnace error codes 2 flashes. Blowing cold air.
We have an American Standard Furnace that has had problems since installation approx. 6 years ago. The furnace will ignite (sometimes) and heat will be distributed -- then switch to cold air and cycle… read more
G Wurtz
G Wurtz
Instructor of HVACR Program
Master's Degree
57 satisfied customers
Hi, I have a Temstart furnace. Two days in a row my house got
Hi, I have a Temstart furnace. Two days in a row my house got real cold. The thermostat showed 61 when the temp was set to 74. And I flipped the thermostat fan switch between auto and on couple of tim… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Amana 80 SV . The main blower will not turn on. The
I have a Amana 80 SV . The main blower will not turn on. The diagnostic indicator flashes once which indicate a system lockout. Is there a reset proceedure?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x