I have a Lennox lf24-150 that is giving me a 4 flash. It…

Hi I have a...

Hi I have a Lennox lf24-150 that is giving me a 4 flash. It runs perfectly for 2-3 cycles then starts fires but the fan doesn’t turn on. Then I get the 4 flash since it is overheating without the fan blowing.

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

A few days now

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

It’s 1 of 45 heaters I have so I’m use to working on these. It has 120v to the board all connections are good

Show More
Show Less
Ask Your Own HVAC Question
Answered in 32 minutes by:
1/17/2018
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,366
Experience: Furnace, A/C and heat pump specialist.
Verified

Are we getting 120v to the fan when it should be on but fan is just not coming on or is board not sending power to fan?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
No power to the fan at that point but the first few cycle it all works perfectly

BUt pressure switch is not opening or a limit until the fan actually causes limit to open due to not coming on?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
I think the limit switch is opening since the fan isn’t coming on. But I don’t know why the fan doesn’t come on after it had been working fine the fan moves freely

Has to be a failing ignition control board. Erratic behaviour is characteristic of a board going out. THere are no other components in the sequence after burners come on and prove flame that would keep fan from coming on. Can you steal a board from one of the other heaters to try ?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
that was my next step but I just wanted a second opinion I’ve had the boards go bad before on other heaters but they were just dead.
Customer reply replied 7 months ago
That’s great info I couldn’t find that anywhere I figured it was on a timer thank you I’ll switch the board out in the morning

I will upload you a manual if you don't have one

Ask Your Own HVAC Question
Customer reply replied 7 months ago
That would be great thanks
Ask Your Own HVAC Question
Customer reply replied 7 months ago
I got it thanks

If you have further questions, please let me know.
Thanks for letting me work with you.If my answer has been polite, professional,and thorough, please click one of the ratings before you go. If you still need help let me know!.Expert is not paid for assisting you until you rate answer.Feel free to follow up for 30 days at no additional cost. Bonus always appreciated if you feel justified.
To rate answer, please select one of the stars on the page.

airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,366
Experience: Furnace, A/C and heat pump specialist.
Verified
airheatman and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,366
9,366 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
What are the chances the valve is bad when there are flames?
What are the chances the valve is bad when there are flames ? I'm about to go out and buy a new circuit board. What odds do you give that as being the problem? 10 to one over the valve being the prima… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
Amana furnace. Heater has only turned on once, very
Amana furnace. Heater has only turned on once, very randomly, since the cooler weather began. Fan works fine when turned to “on”. Doesn't run at all on “auto”. I've tried turning the heat up over 70, … read more
airheatman
airheatman
HVAC Technician
6 years college
9,366 satisfied customers
I have a Lennox garage heater. The thermostat broke so I
I have a Lennox garage heater. The thermostat broke so I installed a new thermostat. When I turned the power back on, the garage heater runs continuously. How do I get it to stop and only run when nec… read more
airheatman
airheatman
HVAC Technician
6 years college
9,366 satisfied customers
I have a Lennox HOT SHOT gas furnace Model LF24 60-2 and
I have a Lennox HOT SHOT gas furnace Model LF24 60-2 and there is 24v coming from the transformer, however no 24v to gas valve. The ignition control code flashes two times and that tells me the sysyte… read more
airheatman
airheatman
HVAC Technician
6 years college
9,366 satisfied customers
. My furnace has not been heating my house to the temperature
Hi. My furnace has not been heating my house to the temperature set on the thermostat. The thermostat calls for heat and the furnace ignites. I get a continuous flashing red light (i read stands for "… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hi, I have an American Standard Freedom 90 Single Stage that
Hi, I have an American Standard Freedom 90 Single Stage that has been cycling no heat with 4 flashes code. I have checked and tapped the two primary problems. The only fix seems to be wiggling the mai… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Trane xb80. Furnace comes on, but won't move the heat. The
Trane xb80. Furnace comes on, but won't move the heat. The small exhaust fan comes on, and the burners fire. Originally I had 4 flashes on the LED. I reset the limit switches and now they're reading a… read more
airheatman
airheatman
HVAC Technician
6 years college
9,366 satisfied customers
Our hanging Lennox Model number Lf24-150 furnace is acting
Our hanging Lennox Model number Lf24-150 furnace is acting up. It will ignite and get warm for a while then quit heating, while the fan keeps blowing. Any ideas what to look at first? Thank you… read more
airheatman
airheatman
HVAC Technician
6 years college
9,366 satisfied customers
I have a Lennox CBX32MV unit with a heat plate ECB29EH, the
I have a Lennox CBX32MV unit with a heat plate ECB29EH, the 3AMP fuse (CB8 on the diagram) keeps on blowing up. The system has been working fine for 5-years. The issue happened a few days after hurric… read more
mranswer
mranswer
TECHNICIAN
Bachelor's Degree
481 satisfied customers
I have a 1998 Lenox HVAC model GHR26Q4/5-100-2 you helped me
I have a 1998 Lenox HVAC model GHR26Q4/5-100-2 you helped me replace the motor Saturday, the unit keeps cycling on and off when the heater comes on, do you have any suggestions? At this moment the hea… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a Lennox LF24-125A-5 furnace in my shop. It will not
I have a Lennox LF24-125A-5 furnace in my shop. It will not light and the LED code light is flashing three times. Schematic says this is a pressure switch What do I do to get this working?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Lennox signature collection oil fired forced hot air
I have a Lennox signature collection oil fired forced hot air furnace. The burner has been firing on for 3-5 minutes then shuts off without reaching temperature. He model number is XXXXX… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We have a Lennox furnace (Series G51MP) model C33 - 48C that
We have a Lennox furnace (Series G51MP) model C33 - 48C that is four years old. Since year 1 we have had problems every year at the same time. This time the fan (blower) keeps running without shutting… read more
KenCan
KenCan
Vocational, Technical or Trade Scho
111 satisfied customers
Ameristar Gas furnace Even when the furnace shuts off but
Ameristar Gas furnace : Even when the furnace shuts off but the fan keeps on blowing air. The Fan doesnot shutdown since a week.… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have has a new LF24-45A #5610E09056 installed in my garage
I have has a new LF24-45A #5610E09056 installed in my garage and i turned in on for the first time today. It doesn't seem to run as it should. As the thermostat calls for heat the burner comes on and … read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
I have a reznor unit heater (I think it is a UDAS 30,000 BTU)
I have a reznor unit heater (I think it is a UDAS 30,000 BTU) that is showing three flashes on the green light - limit switch? I have powered off, turned off the gas and followed the restart procedure… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
My Lennox HotShot LF24 garage heater heats up when the thermostat
My Lennox HotShot LF24 garage heater heats up when the thermostat requests heat, but the main fan does not kick in, so the upper limit is soon reached and the gas cuts off. How do I check the circuit … read more
KenCan
KenCan
Vocational, Technical or Trade Scho
111 satisfied customers
I did not know what the board number was unitl your last post....Thanks!!!
I did not know what the board number was unitl your last post....Thanks!!! The OE board is #43K49801, GCI-3, dated 9704. What are the changes with the new repalcment boards??… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x