I have a 30 year old Bryant Plus 90 furnace. Recently I noticed a humming noise when the blower starts up, and is gone when at full speed. In other forums (and this one), the capacitor has been identified as the likely culprit so I installed a new one. The replacement part for my furnace model was listed as 12.5uF, 370v. However, when I replaced it the hum seemed louder, and though it got quieter at full speed, it was still noticeable. I put back in the old capacitor and hum level returned to the original lower audible levels at startup and quiet at full speed. I noticed the old part was a lower 7.5uF, 370v part. Any idea what is going on?
Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 minutes by:
1/17/2018
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,922
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

Hello,

My name is Billy. The first thing to do is look at the motor and see what capacitor it was rated for. Many times motors get replaced and the capacitors do not so they end up mismatched.

Do you know what the motor in the furnace has on label for cap size?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
The furnace has not had either the motor or the capacitor replaced (until I just replaced the cap). I am the original home owner.

then you simply were given the wrong capacitor as a replacement.

If 7.5 uf was previous part you must match that. So at this point you need to get a 7.5 and try that. Plus....using the wrong cap can cause a early failure for a motor so I hope it is still ok...

Billy

Ask Your Own HVAC Question
Customer reply replied 1 month ago
Understand, but all the on-line parts stores recommended the same 12.5uF capacitor for my furnace model number (which fits many other carrier furnace models as well). I think Carrier must now recommends this size for these models. Why would a higher capacitance make the hum worse?

Did anyone ask for serial number? The motors change from series to series in the same model number.

If you had a 7.5 then it was OEM. A 12 will burn the motor out. What is your model number and serial and I will confirm

Ask Your Own HVAC Question
Customer reply replied 1 month ago
Model # 398AAW060120D
Product # 398AAW060120AEBA
Serial # 2487A05308

I show that as an OEM oval 7.5uf 370 volt

See here

If you like you can enter your model directly in the model field and find your parts.

I went to Carrier/Bryant parts and found the original part was HC91CA007...this crosses to what I sent link of.

Billy

Ask Your Own HVAC Question
Customer reply replied 1 month ago
OK, I will test the old part before I get a new one and try to return old one. Not sure the old one is bad and that a new one will quiet the startup hum. Is there a chance the hum can be a result of the motor going bad? Thank you.

It could be start windings getting weak...weak capacitor....

Many of these "groaned" at start up and in lower speeds. Sometimes changing the speed tap on the board to a higher speed changes it or shortens the duration.

Honestly...a hum is generally the "get to ready to replace me" sound.

Billy

Ask Your Own HVAC Question
Customer reply replied 1 month ago
Thanks for the advice. The speed is set to lowest (for heating). I can try a higher speed with the negative tradeoff of a louder overall fan sound and higher air flow from vents. But if it helps with motor longevity it is worth it (I know, 30 years is pretty good already). Did have to replace the inducer motor 25 years ago, but that turned out to be a known issue.

the good thing about this board is the blower wires set up...you can easily swap speeds by looking at diagram on back of the blower door.

I hope all goes well for you and if you need further info let me know....I cut my teeth installing those 30 yr old units:)

Just rate service to close ( 5 star system)

Billy

BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,922
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
BillyHvac and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?
Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,922
22,922 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Carrier furnace. Igniter comes on, but no flame. There was
Carrier furnace. Igniter comes on, but no flame. There was an electrical issue earlier today on the electric company's side of the meter. It has been repaired. Furnace was OK prior to that. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Carrier furnace rated at 1865 cfm was recently installed in
carrier furnace rated at 1865 cfm was recently installed in Jan 2018. Total cfm for all vents is 1056 cfm. heat distrbution for 16 vents ranges from 69 to 95 cfm. what could be the problem? Please adv… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,922 satisfied customers
I just replaced the circuit board in my carrier furnace
i just replaced the circuit board in my carrier furnace because the blower was not working. now, the blower blows all the time and the flames wont light… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have a Carrier furnace model 58CTA090-12114 that was
I have a Carrier furnace model 58CTA090-12114 that was installed in 2005,I am currently having an issue with it when it is called upon for heat, it will start the burner sequence with the ignitor glow… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
The ignitor to my Carrier furnace will not trigger so no
Hi Pearl. The ignitor to my Carrier furnace will not trigger so no heat can enter the house. I've manually reset the limit switch and cleaned the flame sensor and was looking for suggestions on what t… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My carrier furnace is not turning on. Thermidistat is blank.
My carrier furnace is not turning on. Thermidistat is blank. Error codes is 33. … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,922 satisfied customers
My carrier furnace is not igniting, no error code. Last
My carrier furnace is not igniting, no error code. Last night it was glowing like it was trying to ignit, but it's not glowing anymore. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have 2 Carrier furnaces that are a few months old but are
I have 2 Carrier furnaces that are a few months old but are not coming on … read more
Jarrett Baker
Jarrett Baker
Building Analyst and Home Inspector
BPI license
24 satisfied customers
I have a 1983 Carrier furnace 294gaw00100. There is not
I have a 1983 Carrier furnace 294gaw00100. There is not pilot ignition. I've checked blower, theromstat, … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Im getting an error code of 12 on my carrier furnace, trying
im getting an error code of 12 on my carrier furnace, trying to figure out how to fix it … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Getting a code 33 on my carrier furnace intermittently. And
getting a code 33 on my carrier furnace intermittently … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have an 18 month old Carrier furnace and infinity touch
I have an 18 month old Carrier furnace and infinity touch control thermostat, in the last 2 weeks a pop up screen shows "SYSTEM FAULT 13-LIMIT LOCKOUT and the furnace will not heat. The service tech c… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,922 satisfied customers
Got an carrier furnace 58mxa080112 new air filter burner
got an carrier furnace 58mxa080112 new air filter burner goes out when big fan kicks on … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
I have a carrier furnace model 58 PAV090-14 the 3amp fuse
I have a carrier furnace model 58 PAV090-14 the 3amp fuse keeps blowing. I changed motor speeds and it's running ok now. Could it be something in the motor or did I not do anything and it could happen… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My Carrier Furnace Model CNPVP4324ATAACAA says humidifier
My Carrier Furnace Model CNPVP4324ATAACAA says humidifier pad needs to be changed. Is that something easy to do? … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
My carrier furnace says secondary voltage fuse is open. I
My carrier furnace says secondary voltage fuse is open … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Furnace not working. Carrier Furnace Model 58PAV070-16112
Furnace not working. Carrier Furnace Model 58PAV070-16112 Blinking code is 2 short and 4 long - 24.Code 24 reads SECONDARY VOLTAGE FUSE IS OPEN Check for short circuit in secondary voltage (24VAC) wir… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,922 satisfied customers
My Carrier Furnace goes on but will not stay on,the red
My Carrier Furnace goes on but will not stay on,the red blinking code is 3blinks and pause,3 … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x