Have a rheem classic heat is only blowing from 2 vents in…

Have a rheem classic...

Have a rheem classic heat is only blowing from 2 vents in one room rest very little air movement

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Both filters are new the blower on unit is working just no air flow in vent

Contractor's Assistant: Do you plan on doing the work yourself?

Possibly

Contractor's Assistant: Anything else we should know to help you best?

Like I stated one room in house has good air flow from vent rest of vents very little air

Show More
Show Less
Ask Your Own HVAC Question
Answered in 47 minutes by:
1/17/2018
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,200
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, so far it sounds like a flexible duct connect connection has broken. Tell me if this happened all of a sudden or developed slowly.

.

If you have a 'zoned system' there will be a zone control panel somewhere AND you will have two thermostats... Tell me if that is the case or not, we can go from there.

.

My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today.

If you need more assistance, please use the reply box and let me know.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
Decreased flow about a month ago only one thermostats.
Customer reply replied 1 month ago
As I stated one room has good air flow the rest have almost no air flow in vents.

Thanks, ***** ***** the problem down to a disconnected duct that feeds air to those areas, no longer getting air (98% chance) OR duct liner insulation that came loose inside the sheet metal box where all of the ducts attach... and has blocked those ducts going to the rooms with insufficient air..(2% chance of that).

.You will have to physically inspect to see whats actually happening.

.

My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today.

If you need more assistance, please use the reply box and let me know.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
one more thing I took panel off side where blowers is . Started it up with panel off had good flow at all vents just cold air because of panel off

Thanks, ***** ***** like the return air duct is blocked, that can happen if SOFT flexible duct is used in the return duct, its plastic inside liner can get sucked flat blocking air flow... you can can also have insulation come loose from the sheet metal plenum that blocks air flow.

And of course a clogged air filter will cause the problem

Ask Your Own HVAC Question
Customer reply replied 1 month ago
Don't think return blocked because of 2 vents in one room blowing air out as they should and they are longest run from unit

Your logic is good.... however you would not be getting good air flow through all of the vents with the blower access door removed if the return air duct was not blocked.

.

So what are we to make of that one?

.

It could be that your longest duct runs are laid in in a straight line with the main trunk line and that rooms that are not getting any air are on 90 degree tee's... so that when air flow is reduced it goes down the path of least resistance to the more distant rooms..

We know for sure however (thanks to your test) that with the blower access door removed, there is plenty of air in all the rooms... that points directly to a partially blocked return duct.

Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,200
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified
Phil and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,200
9,200 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,200 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a 1500 sq.ft, brick ,single story. ceiling & walls
I have a 1500 sq.ft, brick ,single story. ceiling & walls are insulationed. l live in whiteville, N.C. what size hgt/ac, heat pump sys. would need for my home. a 1t , 2t, 3ton ? thank you,***** *****,… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a GE BH85DB combination heat lamp/exhaust fan. It is
I have a GE BH85DB combination heat lamp/exhaust fan. It is located in a bathroom. It is installed thru the ceiling into an unheated attic. Since the weather has turned cool here in northern MN the ho… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Rental hot water tank - serviced and insulated pipes Oct
rental hot water tank - serviced and insulated pipes Oct 2017 by Reliance tech-ice build up at elbows on insulated outside plastic pipe - when fan comes on -can hear running water outside from inside … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Installed a forced air furnace this summer in the attic of
Installed a forced air furnace this summer in the attic of my small second home in Michigan. Since it gets extremely hot up there in the summer (90+degrees) The air conditioning struggles to keep the … read more
Phil
Phil
Mechanical Engineer
9,200 satisfied customers
Question about basement insulation... It's not a problem -
It's not a problem - it's a question...we live in the Atlanta area. 3 years ago, we purchased an existing home that has a full, unfinished walk-out basement, which means that the entire north and west side of the basement is above grade. The south and east walls are poured concrete and are below grade. When we bought the home, it had zero insulation in the stud walls on the north and west sides. The concrete walls also were not insulated. However, there was faced fiberglass insulation stuffed between the floor joists in the basement ceiliing … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
The yellow wire on the blower motor through insulation. It
The yellow wire on the blower motor burnt through insulation. It appears to be 15 years old. Would it be safe to repair the yellow wire and continue to run the motor? The ground wite is hanging loose … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I'm looking for the best method and type of insulation to
I'm looking for the best method and type of insulation to use in an 1890's home that has non-uniform stud and rafter spacing that ranges from 28"- 34" on center. In this process should I use a vapor b… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
What is the use of insulating suction pipe of compressor? I
What is the use of insulating suction pipe of compressor ? I mean is it useful in package units also ?… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
I purchased a 60 x 100 insulated metal building. It had 3
I purchased a 60 x 100 insulated metal building. It had 3 1991 7.5 ton gas packs in it using lp tanks. The tanks are gone and they stole the guts out of the 1991 units. I'm building living quarters on… read more
Phil
Phil
Mechanical Engineer
9,200 satisfied customers
Instaling fie insulation. Which way does the metal piece go
which way does the metal piece go to hold the baffles … read more
Phil
Phil
Mechanical Engineer
9,200 satisfied customers
Dose the ac unit outsde need a foan insulation, yhermostat
yhermostat turns unit on the unit outside blow cold air … read more
Phil
Phil
Mechanical Engineer
9,200 satisfied customers
I have a 120 year old two story Victorian, poorly insulated
I have a 120 year old two story Victorian, poorly insulated home. Recently installed a four ton system with the thermostat set at 68 degrees. Yesterday the outside temperature was 69 degrees, and my s… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I live in Bellevue WA and have a 1961 fully insulated 1550
Hello I live in Bellevue WA and have a 1961 fully insulated 1550 sq ft rambler how large a gas furnace do I need at 80% efficiency … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My question is: is it necessary to remove ALL old insulation
Hi,My question is: is it necessary to remove ALL old insulation before blowing in new insulation?What I'd like to accomplish is: 1. Improve the air quality in the house by getting rid of that dusty la… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have three rooms, all r13 insulated walls, r30 insulated
I have three rooms, all r13 insulated walls, r30 insulated ceiling with 1/2 inch drywall used across the whole room. The four rooms are 16 ft x 11 ft with a 9 ft ceiling, 15 ft x 21 ft with a 9 ft cei… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
Even though my suction line on my split system is insulated
Even though my suction line on my split system is insulated I having a lot of condensation dripping from the seams of the insulation. My unit is 17 years old … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Air handler insulation in my classroom. Condensation line
Air handler insulation in my classroom. Condensation line plugs and over flows into drain pan and the insulation under the drain pan gets soaked. Do you think this is mold? CO2 levels average 1600 ppm… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Phil, I have mold on my ceiling registers, in the insulation
Hi Phil, I have mold on my ceiling registers, in the insulation above the register, on the duct fin, and within the first foot of the ducting... how do I get rid of it? Spray some household mold clean… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x