I have an old intertherm propane furnace in my mobile home.

Hi. I have an...

Hi. I have an old intertherm propane furnace in my mobile home. The blowe motor model 497540 has recently been making chirping noise on start up lasting bout 1 minute. Goes away. Doesn't happen again until next startup. Output everything normal except chirping noise. It's single speed motor. Any help u can give greatly appreciated. Also says blower motor compatible with HGHA 056A. It's CFM 700 Thank you so much.

Contractor's Assistant: Did you check the furnace's filters?

Yes. Replace it at start up. Every year

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 7 months ago
Also need to add there are no belts on this furnace. I believe possibly blower motor but can't find any info on replacement model thank you
Answered in 35 minutes by:
1/16/2018
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,377
Experience: Furnace, A/C and heat pump specialist.
Verified

Let me do a little research and see what I can find

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Ok thank u.

Should your post say compatible with the MGHA? ( am not finding anything in my manuals on an HGHA)

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Sorry for delay. Yes it is MGHA. I have another ? Regarding interthermal blower motor. What would the blower assembly kit # be for this blower motor. Thanks

THe small combustion motor? I am not seeing one for this model.What dou mean by interthamal blower?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
For the Intertherm Nordyne 901872 / part 231052 blowe motor. Which runs off Propane for a mobile home.
Customer reply replied 7 months ago
Intertherm / Nordyne name of manufacturer of furnace

If you are referring to the entire circulating lower kit, the part number was 902008, but no longer available as a kit.

You can buy the motor a at the link I sent and the blower wheel (667149) from same place but as far as the housing there no no resources showing the assembly complete available

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Ok. Thank you.

Thanks for letting me work with you.If my answer has been polite, professional,and thorough, please click one of the ratings before you go. If you still need help let me know!.Expert is not paid for assisting you until you rate answer.Feel free to follow up for 30 days at no additional cost. Bonus always appreciated if you feel justified.
To rate answer, please select one of the stars on the page.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Hi. Just to try lol, I searched for the blower assembly kit 902008 for intertherm Nordyne furnace. The replacement # is 902906 which I found info @ Partners Choice heating & cooling replacemen Yeah t parts. I then searched the new # and blower assembly available at several sites !!!

Excellent. I will add this to my files. Thanks again for letting me help and get thee part numbers for you.

airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,377
Experience: Furnace, A/C and heat pump specialist.
Verified
airheatman and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 7 months ago
Ur welcome. And thank you. I will rate u now. Thanks Dr Marzio.

JUst out of curiousity do you have a link to the actual cross reference showing ti to be the replacement so I can share with future clients?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
I searched part # 902008 replacement part. The attached site appeared saw 902008 listed clicked on PRICE LIST took me to yaunco.com where PDF Parts replacement numbers located. But if go yaunco.com, u will not see PDF. Lol. Yeah, seems weird way but worked for me !!

THanks again.Saving now. Often when I give people parts numbers they want me to show them why I am recommending when that is not the number they have. Hope it is right one.If for any reason it is not, please let me know so I don't forward and thanks again

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Ok I will.

THanks again

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,377
9,377 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Sometimes my mobile home intertherm propane furnace blower
Sometimes my mobile home intertherm propane furnace blower does not run and the unit gets really hot. Then after a while (maybe cools down) then the blower runs and things seem normal. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a York Affinity YP9C two stage furnace with a YCJF AC
Hello, I have a York Affinity YP9C two stage furnace with a YCJF AC unit that is a single stage. Both wiring diagrams show the wire running from the Y at the AC unit to the Y/Y2 at the furnace to the … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
Have a Intertherm M1M 070 mobile home furnace. The furnace
Hi Tim, Have a Intertherm M1M 070 mobile home furnace. The furnace came with the 1/4 hp, 3 speed (multi speed) blower motor. As you're probably aware my speed choices are high, med high, and med low. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Have an a/c unit model Rheem RGRM-07EYBGS, when the blower
Have an a/c unit model Rheem RGRM-07EYBGS, when the blower starts it makes a noise as if is trying to start making a woosh noise then it kiks in. I asked the a/c person that install it He said it was … read more
airheatman
airheatman
HVAC Technician
6 years college
9,377 satisfied customers
I have to install a makeup air unit to compensate 1200CFM
I have to install a makeup air unit to compensate 1200CFM range hood in my kitchen. I am hoping to introduce outside air into the air return on a York Diamond 90 furnace return. Manual I have consulte… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Just installed a new rheem rgps- 12earjr and the noise it
Just installed a new rheem rgps- 12earjr and the noise it makes when its running is extremely loud. My wife describes it as a generator noise, and it definitely makes this initial revving up sound. An… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Need a "VERY" quiet blower that can stand up to high humidity
Need a "VERY" quiet blower that can stand up to high humidity operation, and "hose-able" cleaning with excellent suction. Must be variable speed with flow of between about 800 to 2000 cfm pulled thru … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
I purchased a mobile home recently and the previous owner installed
I purchased a mobile home recently and the previous owner installed a new Intertherm M1 furnace. This is the noisiest furnace I have ever heard. It has 1 speed it seems and that is High! Everytime it … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a 90plus Reehm furnace with a 3 ton AC unit installed
I have a 90plus Reehm furnace with a 3 ton AC unit installed in March 2011. Fan motor has made a humming sound when first trying to start up ever since I have owned. Installer has experimented continu… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
Can a 1/3 HP single speed belt driver be replaced with a ½ HP?
Can I replace my 1/3 hp single speed belt drive furnace blower with a 1/2 or 3/4 hp 4-speed furnace blower? (1600 sq ft 2 story, well insulated house, oil burner is working well, 2-stage air condition… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We have a recently installed Lennox G61MPV-60C-091-12 furnace
We have a recently installed Lennox G61MPV-60C-091-12 furnace and an XC17-036-230-02 A/C in our home. We assume that these units are compatible and will work together even though the furnace is two-st… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
Regarding the previous question about the Rudd furnace, I did
Regarding the previous question about the Rudd furnace, I did get the blower speed to its lowest level. But I still had someone come out to look at it. The tech said the furnace is too big for the hou… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
Hello, Im gonna try this again w/someone who knows, I purchased
Hello, I'm gonna try this again w/someone who knows, I purchased a brand new Split Heil A/c system, in the spring, The unit(s) are as follows, Heil-DX1400 3Ton model #H4A436GKD200 in tandem w/a Heil 4… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
Will I notice a significant difference in the noise level between
Will I notice a significant difference in the noise level between a Bryant 95% single stage gas furnace and a Bryant 2 stage variable speed natural gas furnace? Our furnace will be centrally localted … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I replaced my Lennox 80% circa 1978 80000 in 64000out with a
I replaced my Lennox 80% circa 1978 80000 in 64000out with a Payne P9 80000in 72000 out direct vent furnace.1. Did not change duct sizes.2. Checked input rate at gas meter . Checks out at 72000 input … read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
HVAC Technical Support I recently had a Trane XV95 - 2
HVAC Technical Support I recently had a Trane XV95 - 2 Stage Furnace installed with a variable speed blower (4 Speeds) Upflow Modlel# XXXXX We replaced a 25 year old model Trane to gain improved effec… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
hello, i have an intertherm mac 1265 year 1976 in my mobile
hello, i have an intertherm mac 1265 year 1976 in my mobile home. my problem is a raw fuel smell thru the ductwork while operating. not very strong until the blower turns on, then worse if i run the b… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
Have recently purchased 1994 mobile home with propane downflow
Have recently purchased 1994 mobile home with propane downflow furnace. Makes irritating clanging noise when thermostat calls for heat, even before blower motor kicks on.… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x