My Amana furnace is not working. I did, There is 3 blink…

Customer Question
My Amana furnace is...

My Amana furnace is not working

Contractor's Assistant: Did you check the furnace's filters?

Yes I did, There is 3 blink error

Contractor's Assistant: Do you plan on doing the work yourself?

Yes I do

Contractor's Assistant: Anything else we should know to help you best?

Fan is working, red led is blinking 3 times

Submitted: 4 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 5 minutes by:
1/16/2018
HVAC Technician: HVAC Guru, HVAC TECH replied 4 months ago
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,393
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified

One moment please..Note it takes time to type and add links so please be patient. Also the site will send you a phone call offer, that is not me.

Ask Your Own HVAC Question
HVAC Technician: HVAC Guru, HVAC TECH replied 4 months ago

That is a pressure switch code, meaning the pressure switch is not closing when the exhaust fan is coming on. So you need to check and make sure the exhaust fan comes on first. You can cycle the power off to the unit at the switch or breaker for a minute and turn it back on to clear the code and restart a heat cycle making sure the thermostat is on or you have R to W jumpered on the board in the furnace. If the fan does not come on check the fan for power. If the fan does come on and nothing is plugged in the exhaust or intake vent then check the pressure tube for blockages. That is the rubber tube that connects the pressure switch to the blower housing. If that tube is blocked or cracked that code will come up. You need to check the port where the tube connects to the exhaust blower housing make sure that port is not blocked with crud. Normally it is one of these issues causing that code on the furnace. Lastly you have to check all condensate lines on the unit, especially the drain line that comes out of the inducer motor housing to make sure nothing is blocked causing a backup of condensate water.

All I ask is...Please remember to use the RATING LINK ON YOUR PAGE by selecting a star at the top or bottom of the screen before you leave today. Even though you paid the site they will not disburse any part of it to me until you supply a good rating. If you need anything else, just let me know. You can continue asking follow-up questions at no additional charge after rating my service if you still need assistance.

Ask Your Own HVAC Question
Was this answer helpful?
Ask HVAC Guru Your Own Question
HVAC Guru
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,393
18,393 Satisfied Customers
Experience: 20yrs in the HVAC industry with certificates and degrees.

HVAC Guru is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have an Amana furnace model 80 sse. Have one flashing red
I have an Amana furnace model 80 sse. Have one flashing red light ontrouble code panel. Indicates furnace lock out. How can I re-set this, or what is causing this.… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
Amana furnace wont kick on. Red blinking light is on inside furnace
amana furnace: will not kick on. \red blinking light is on inside furnace… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Where is the Amana furnace(model Guic070CA30) flame sensor
Where is the Amana furnace(model Guic070CA30) flame sensor located. and how do you remove it to clean it?… read more
Bill P.
Bill P.
Installer/ Troubleshooter/Technician
286 satisfied customers
I have an Amana furnace and am trying to figure out if I can
I have an Amana furnace and am trying to figure out if I can have it pull the cool basement air into the rest of the house (they way my parents taught me) … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have an Amana furnace 70K btu model # GSI070B30B. It
I have an Amana furnace 70K btu model # GSI070B30B. It suddenly stopped operating yesterday morning after running one heating cycle to warm the house. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My Amana furnace is not working. I did, There is 3 blink
Hi JA: Hi. How can I help? Customer: My Amana furnace is not working JA: Did you check the furnace's filters? Customer: Yes I did, There is 3 blink error JA: Do you plan on doing the work yourself? Cu… read more
HVAC Guru
HVAC Guru
HVAC TECH
18,393 satisfied customers
Our new Amana Furnace (installed earlier this year) won't
Hi Pearl, our new Amana Furnace (installed earlier this year) won't seem to heat up past 60-66 … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,808 satisfied customers
My amana furnace is not igniting. Hopefully. The red light
My amana furnace is not igniting JA: Did you check the furnace's filters? Customer: Yes JA: Do you plan on doing the work yourself? Customer: Hopefully JA: Anything else we should know to help you bes… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have an amana furnace pga30b0702c and the led light inn
I have an amana furnace pga30b0702c and the led light inn the control board is not on. I have 120v going to the board in 2 places. It is a 240v unit. Should three light always be on or is there someth… read more
Chad DeYoung
Chad DeYoung
11 satisfied customers
I have an Amana furnace. it won't light. it will if I remove
I have an Amana furnace. it won't light. it will if I remove the drain line on the bottom of the vent blower. i have cleaned the line out but when i put it back in the drip leg it shuts down again. co… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have an Amana furnace and am having trouble getting it to
I have an Amana furnace and am having trouble getting it to fire. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Amana furnace. Heater has only turned on once, very
Amana furnace. Heater has only turned on once, very randomly, since the cooler weather began. Fan works fine when turned to “on”. Doesn't run at all on “auto”. I've tried turning the heat up over 70, … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
How do I light the pilot light on my Amana furnace? I 't see
How do I light the pilot light on my Amana furnace? I don't see any knob with On Off and Pilot settings… read more
Kcrand36
Kcrand36
Technician/Owner
Vocational, Technical or Trade School
72 satisfied customers
Amana air command 80 gas furnace - one of the 2 clips at the
Amana air command 80 gas furnace - one of the 2 clips at the bottom of the panel accessing the filters is broken. The ones that have to be turned horizontally for the furnace to start. If I hold it in… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a amana furnace 80 sse ,the blower fan makes noise on
I have a amana furnace 80 sse ,the blower fan makes noise on start up and continues slightly quiter as it is running kind of sounds like a piece of paper next to or rubbing on the blades. I checked fo… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Having problem with Amana furnace model ams950453bxa. Combustion
Having problem with Amana furnace model ams950453bxa. Combustion motor starts, no glow, runs a few seconds then shuts down with continous flash indicating reversed 115 volt polarity. Polarity hasn't b… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have an amana air command 90 furnace which periodically stops
I have an amana air command 90 furnace which periodically stops working. small fan comes on, igniter glows, burners wont kick on!! steady flashing red light power down and restart will work a few hour… read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
I have an amana furnace Model number GUIC090CA30. The furnace
I have an amana furnace Model number GUIC090CA30. The furnace will not ignite when calling for heat. When I put power on the unit the blower fan runs constantly even when the thermostat is not calling… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less