I have a Goodman GMVC950905DXAB gas furnace. It has recently…

Customer Question
I have a Goodman...

I have a Goodman GMVC950905DXAB gas furnace. It has recently become very noisy when it runs with a loud vibration-type sound. I have investigated the motors on the fans and found them not to be the problem. This furnace has a Goodman A-Coil mounted on top which connects to an outside condenser that provides air conditioning. I have found that the vibration seems to be coming from the outside condenser/compressor which surprised me very much. I did not think it would operate when the thermostat is set to heat mode. Anyway, when the vibration starts, the burner shuts off, when the compressor stops on the AC unit a pressure relief valve (I think) pops off then the inducer starts back up and the burners reignite. The end result is lackluster heating and little sleep due to the vibration. Any help would be appreciated. Dan

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

thermostat settings are okay and filters are clean. They are the type you wash and replace which we do monthly.

Contractor's Assistant: Do you plan on doing the work yourself?

I am an old retired engineer and I have done this type of maintenance around my house for a long time, but one bad knee and two bad shoulders have limited me to light duty. So if needed I will seek outside help.

Contractor's Assistant: Anything else we should know to help you best?

I don't think so.

Submitted: 5 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 minute by:
1/16/2018
HVAC Technician: HVAC Guru, HVAC TECH replied 5 months ago
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,643
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified

One moment please..Note it takes time to type and add links so please be patient. Also the site will send you a phone call offer, that is not me.

Ask Your Own HVAC Question
HVAC Technician: HVAC Guru, HVAC TECH replied 5 months ago

Do you have a heat pump system?

Ask Your Own HVAC Question
Customer reply replied 5 months ago
It is not a heat pump but a gas furnace with vertical flow and a central air unit with A-coil on top and condenser unit outside.
HVAC Technician: HVAC Guru, HVAC TECH replied 5 months ago

You are sure the main blower is not causing the issue?

Ask Your Own HVAC Question
Customer reply replied 5 months ago
Because of the very cold weather, I have called in a local HVAC company to make the repair. Thanks for your help
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,424
7,424 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,424 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Need to know how to check a condensate drain - appears to be
need to know how to check a condensate drain - appears to be clogged … read more
Rick
Rick
Supervisor
24,042 satisfied customers
My ac compressor works fine but the condenser fan will
Hello, my ac compressor works fine but the condenser fan will sometimes not start automatically, especially in the morning, evening or at night. The condenser fan starts fine during the day. When it d… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
The pan beneath the AC condenser has rusted and if the AC is
The pan beneath the AC condenser has rusted and if the AC is running, leaks into the ceiling beneath. This part of the AC is in the attic. Is the pan replaceable and how costly is this repair. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I just had a completely new Rheem HVAC and Condenser
Good day. I just had a completely new Rheem HVAC and Condenser installed about 3 weeks ago. 2 days ago, my wife noticed that water was dripping out of one of the ducted vents pretty badly. The tech ca… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I'm installing a nest e thermostat. Set up went well but my
I'm installing a nest e thermostat. Set up went well but my outside unit didn't kick on. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Our condensate drain in not working properly. It has been
Our condensate drain in not working properly. It has been cleaned out and is clear. There is a cleanout before the p-trap. It seems that when the cap is removed, the system drains properly. Any sugges… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My blower fan does not run. The condenser and condenser fan
My blower fan does not run. The condenser and condenser fan run fine but the air handler fan does not. The squirrel cage turns freely and makes weak attempts to turn but does not run so it seems there… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,344 satisfied customers
I have been told my condenser is not working on my Nordyne
I have been told my condenser is not working on my Nordyne air conditioner Model FS3BA - 042KA.......how can I trouble shoot what part may not be working so I can get it fixed. … read more
Phil
Phil
Mechanical Engineer
7,424 satisfied customers
Thermostat setting flashing or blinking. Thermostat. fan
what else do you need to know. house built in 1991. recently changed battery. just happened… read more
Phil
Phil
Mechanical Engineer
7,424 satisfied customers
I have tempstar central a/c. Thermostat set to auto and
Good morning. I have tempstar central a/c. Thermostat set to auto and cool. Inside fan running, heartbeat LED on furnace is blinking normally, outside fan is running (t-bar shows both fuses are workin… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,874 satisfied customers
What is size of clear tubing for condensation for Friedrich
What is size of clear tubing for condensation for Friedrich room air conditioner PH14B … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have had my thermostat set at 68 for the past two
Hello....I have had my thermostat set at 68 for the past two years.....now my indoor temp is 80. I have changed my batteries today … read more
Phil
Phil
Mechanical Engineer
7,424 satisfied customers
Need to confirm Air filter direction. Thermostat settings
Thermostat settings are irrelevant ? My question is about the filters … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Nest Learning Thermostat set for 80 but temp is 63. Gas
Nest Learning Thermostat set for 80 but temp is 63. Gas forced hot water boiler working fine. Other zones in my apartment are 70. Working fine yesterday. What's up? … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,344 satisfied customers
I have a Honeywell thermostat set at 74 (Heat on, Fan
I have a Honeywell thermostat set at 74 (Heat on, Fan automatic). But the house temp is 61. What do I do to get the heat up? … read more
Rick
Rick
Supervisor
24,042 satisfied customers
Heat won't come up to thermostat setting. New furnace and
Heat won't come up to thermostat setting JA: Did you double-check the thermostat's settings? And what about the filters? Customer: New furnace and a.c. installed this year JA: Do you plan on doing the… read more
HVAC Guru
HVAC Guru
HVAC TECH
18,643 satisfied customers
Gasfurnace has pilot light but no flame thermostat set on
gasfurnace has pilot light but no flame thermostat set on heat … read more
Rick
Rick
Supervisor
24,042 satisfied customers
Can you answer a question about a thermostat setting on a.
Can you answer a question about a thermostat setting on a. Vive Box? … read more
HVAC Guru
HVAC Guru
HVAC TECH
18,643 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.