I have a Lennox furnace SL280UH070V36A-3 and I can see the…

Customer Question
I have a Lennox...

I have a Lennox furnace SL280UH070V36A-3 and I can see the ignitor glowing, but sometimes, (I think it's 5 or 6 times), though it's glowing, it doesn't ignite the gas.

Contractor's Assistant: Did you check the furnace's filters?

Yep... fine, but I installed a new one

Contractor's Assistant: Do you plan on doing the work yourself?

I'd like to try. I have the manual. I pulled the cover off (power off first)... I think I read somewhere that the ignitor could possibly be slightly misaligned?

Contractor's Assistant: Anything else we should know to help you best?

If the furnace fails to ignite, I've learned (if I'm home) to turn off the furnace switch, count to 5, then turn back on to initiate the ignition sequence... usually one of those 5 or 6 tries will achieve "ignition".

Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 6 minutes by:
1/15/2018
HVAC Technician: Phil, Mechanical Engineer replied 7 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,822
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, the igniter needs to glow very very brightly almost white hot ... if its glowing a duller red then it needs to be replaced.

.

IF the igniter is glowing very brightly, then use a wire brush and compressed to blow the dirt out of the burners and the slot along the front edge that lets the flame travel from one burner to the other.

.

We can go from there without a time limit.

.

My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today.

If you need more assistance, please use the reply box and let me know.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,822
9,822 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,822 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Ruud Achieve Super Quiet 80. It will not ignite,
I have a Ruud Achieve Super Quiet 80. It will not ignite, even though I can hear it trying. It has 1 flashing light which indicates a soft lockout. I can't find a reset button and have not been succes… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Lennox C33-48B-2F gas furnace. It will power on and
I have a Lennox C33-48B-2F gas furnace. It will power on and the igniter will flow for several seconds, then it shuts off for a second and repeats that whole process.… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Hello. I have a Lennox G40UH that's not firing. The Inducer tur
Hello. I have a Lennox G40UH that's not firing. The Inducer turns on and the igniter gets bright. But the valve is not turning on and I'm not getting 24v at the valve.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
lennox unit with heatcraft ignition control board retrofit,
lennox unit with heatcraft ignition control board retrofit, unit operates heat cycle normally and properly, however if unit is running more than two heat cycles to achieve desired room temp. it sounds… read more
hvacexpertjoe
hvacexpertjoe
Electronics Technician
Vocational, Technical or Trade Scho
80 satisfied customers
goodman gmnt100-4 . wont ignite . igniter is lighting bright
goodman gmnt100-4 . wont ignite . igniter is lighting bright orange 3 time then furnace shuts down . . no gas releasing . . blinking 1 blink ...… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
HELLO I have a lennox G61MP furnace. The thermostat is calling
HELLO I have a lennox G61MP furnace. The thermostat is calling for heat (2 LED's flashing rapidly_) After about 5 seconds the fan stops and theLED's now flash alternately indicating ignitor failure or… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a bryant 398aav gas furnace. When it starts up everything
I have a bryant 398aav gas furnace. When it starts up everything is normal up to the ignitor glowing then nothing after that. If I recycle the furnace numerous times it will come on and work. when it … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hi. I have a 9 year old carrier 58tma 085 120 furnace. I think
Hi. I have a 9 year old carrier 58tma 085 120 furnace. I think I let the filter get too dirty and now I get very intermittent heat. When the house gets cold, I trip the furnace circuit breaker and wai… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
Hello, I have a problem here in Ohio where it is currently
Hello, I have a problem here in Ohio where it is currently on 19 degrees outside. I have a tappen furnace about 6 years old. After the heating elements glow for about 30 seconds there is a click click… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My Ruud (propane) furnace must have turned off sometime last
My Ruud (propane) furnace must have turned off sometime last night...I think it's getting gas but the pilots aren't lighting and apparently, I can't light it myself. The hot water heater right next to… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Lennox 80UHG series gas-fired furnace controlled by
I have a Lennox 80UHG series gas-fired furnace controlled by a Honeywell T8602D thermostat. It was working fine two days ago and then the gas furnace failed to ignite. The blower fan would start to cl… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
No heat. Fan turns on only in on position still no heat. Thermo
No heat. Fan turns on only in on position still no heat. Thermo coupling clean. Ignitor turns on sometimes. Is this the mother board? Furnace is 4 years old.… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a trane XL 80 furnace that is blowing cold air. When
I have a trane XL 80 furnace that is blowing cold air. When I turn off the thermostat, the unit will continue running until I unplug the igniter. When the unit turns on, should I see a flame or flames… read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
I have a lennox GWB8-245S boiler and this pilot light seems
I have a lennox GWB8-245S boiler and this pilot light seems to be out. Can you walk me through re-lighting? It doesn't appear that there is a red pilot button to hold down - just goes from on to off.… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Carrier Infinity 80 furnace. Its not working this
I have a Carrier Infinity 80 furnace. It's not working this year. Is there a pilot that has to be lit?… read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
My furnace controller LED is flashing twice and pausing. The
My furnace controller LED is flashing twice and pausing. The legand sticker on the inside panel shows "external lockout, retries or recycles exceeded". What does this code mean and what can I do about… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
i have a friend who has a problem with a lennox lf3e-110-1,he
i have a friend who has a problem with a lennox lf3e-110-1,he recently had a new ignitor installed and it worked for a little while,but now it is not.… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
i have a lennox e1603-20-ip when i put the heat on ,,,the
i have a lennox e1603-20-ip when i put the heat on ,,,the fan on auto the heat wont come on but when i put the stat on (fan on ) the fan and heat come on… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x