My carrier gas furnace is acting up .It will Ron and cut off normally but every once in a while will not light and ignite if I turn the thermostat down then back up it will light and ignite reach temperature and cut off then it may or may not relight
Submitted: 6 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 10 minutes by:
1/9/2018
HVAC Technician: airheatman, HVAC Technician replied 6 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,181
Experience: Furnace, A/C and heat pump specialist.
Verified

Welcome to the JustAnswer/Pearl website.My name is ***** ***** I am happy to be able to work with you on this today.Please be patient as I respond as sometimes it takes me a few moments to gather proper manuals and specifications on your equipment in order to provide accurate answers.Please wait until we are finished to rate my answer.Hopefully at that time I will have earned a five star rating.Now just to let you know, the website does offer a live phone call for one on one discussion for an additional fee. Due to my current work load and responsibilities I may not be available for the live phone call but along the way, the website will automatically present the offer.Please note that there is an additional cost for the service and if a technician calls it may be a different technician. However we can continue here as long as needed .

The next time it does not light,go to thermostat and disconnect the R and W wires and touch them together to see if furnace comes on.If so issue is with thermostat,could be as simple as low batteries.If it doesn't,Can you look inside the burner compartment on label on side panel and get me the model on your furnace? Then look in blower compartment and see if there is an error light blinking that will guide us in determining what is failing with the furnace.)Not if no peep hole and you have to remove blower panel to see control board, it will be necessary to hold door switch in to have power to board)

Ask Your Own HVAC Question
Customer reply replied 6 months ago
58efao75 cc. 0592v00544. This is the model and serial number
Customer reply replied 6 months ago
The exhaust fan stays on but the unit is not light.
Customer reply replied 6 months ago
Could it be the limit switch
HVAC Technician: airheatman, HVAC Technician replied 6 months ago

ow about the error light on board.Is it blinking?

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 6 months ago

Looks like that one ws before they started putting diagnostic lights

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 6 months ago

Very possible a limit.Can you bypass it and see if it comes on?

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
XR80, 7 years old. Will light and run fine one time. Will not
XR80, 7 years old. Will light and run fine one time. Will not relight, flame dies out before full ignition. Blower will run with no heat until I turn it off. After 30 to 60 minutes off, furnace will l… read more
airheatman
airheatman
HVAC Technician
9,181 satisfied customers
Luxaire Model G9708016UPC13A - the gas was off the add a new
Luxaire Model G9708016UPC13A - the gas was off the add a new line now the furnace will now start is there a need to purge the gas to start the furnace or is there a proceedure to start the furnace… read more
jhvac
jhvac
2 satisfied customers
New Mobile Home: Furnace recently cleaned and inspected. Beckett
New Mobile Home: Furnace recently cleaned and inspected. Beckett R7184B prime controller. Brand new igniter. Burner cycles on and off every few minutes while there is a constant call for heat (thermos… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a carrier 58sta/stx furnace. The blower fan runs constantly.
I have a carrier 58sta/stx furnace. The blower fan runs constantly. The fan switch on the thermostat is set to auto and even if I turn it to off the fan continues to run. When the thermostat does call… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a ugph-12earjr and the burner will not light. I replaced
I have a ugph-12earjr and the burner will not light. I replaced the igniter but it still does not light. If I turn off the furnace then turn it back on, it begins the start up cycle. I wait for the ga… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
My gas pac runs fine until it reaches the thermostat temperature
My gas pac runs fine until it reaches the thermostat temperature that I set it at, then shuts off (as it should), but never comes back on. The only way I can get it to restart is to flip the breaker. … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a HE-4 series 3 boiler. it keeps the fan running and
I have a HE-4 series 3 boiler. it keeps the fan running and wont restart the flame untill i turn off the power and power up again. I replaced the honeywell control but no luck.Now what do I check?… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
We have an old, 1970, Day and Night Gas Furnace that has developed
We have an old, 1970, Day and Night Gas Furnace that has developed a problem in the last few months of use (the end of last winter and start of this winter). At the end of each heating cycle, the fan … read more
A-1 Tech
A-1 Tech
Service Manager
Vocational, Technical or Trade Scho
361 satisfied customers
My carrier furnace will come on and run when you turn the thermostat
I need help with my carrier furnace. It will come on and run when you turn the thermostat switch on, It will run for a while then shuts off, but it will not turn back on unless I turn thermostat switc… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
we have a carrier 2 stage furnace, I intalled a honeywell rth6350
we have a carrier 2 stage furnace, I intalled a honeywell rth6350 thermostat. The A/C worked fine, the heat will not come on sometimes when it is programmed to. If I turn the electric power switch on … read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
My Carrier furnace is giving me trouble, the induced draft
My Carrier furnace is giving me trouble, the induced draft blower starts, then the igniter lights the pilot light, then the gas valve opens and soon after the plenum lights, then the blower turns on a… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
Yesterday I came home from a long weekend and my house was
Yesterday I came home from a long weekend and my house was cold??? I have a Carrier Crusader furnace from 1987. I went and turned thermostat off and then back on. The furnace went thru the normal moti… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hello, I have a Carrier furnace that is acting up on me and
Hello, I have a Carrier furnace that is acting up on me and I want to see if I can fix the problem. The furnace will work fine when it has been off for a few hours and I turn it up from 60 degrees to … read more
Bill P.
Bill P.
Installer/ Troubleshooter/Technician
286 satisfied customers
Re Model 58PHA/PHX System off during the night. Turned
Re: Model 58PHA/PHX System off during the night. Turned on at 6:00 am, thermostat set to 68 degrees. It takes 4 hours to reach 68 from an original house temp of 60 degrees. Is it normal for the system… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I have a trane XL-90 furnace about 20 years old. It has been
I have a trane XL-90 furnace about 20 years old. It has been intermittent for two years. It will always light the burners the first time the thermostat calls for heat but will sometimes fail to religh… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I have a weil mcclain he-4 boiler furnace and when it cycles
I have a weil mcclain he-4 boiler furnace and when it cycles on the gas valve not all of the burner tubes light every time. It often short cycles not maintaining an even temperature.… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a trane gas hot air furnace model TDE 060A936A1 -Igniter
I have a trane gas hot air furnace model TDE 060A936A1 -Igniter energizes and gas vlve opens and gas ignites. -After running contiuously for 10-15 minutes the gas valve clicks several times in repid s… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Nat gas furnace. While on a heat call the flame goes out and
Nat gas furnace. While on a heat call the flame goes out and then relights. Same thing about three times before the thermostat is satisfied. Not a high limit call. Temp is steady at 140 degrees.… read more
Jason Martin
Jason Martin
Maintenance Supervisor
Vocational, Technical or Trade Scho
88 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x