HVAC

Have HVAC questions? Ask an HVAC Expert for answers

Ask an Expert,
Get an Answer ASAP!

I have a Reznor gas heater with Honeywell V8200 gas

Customer Question
I have a Reznor...

I have a Reznor gas heater with Honeywell V8200 gas controls. It won't fire up. I have replaced the thermocouple and the thermostat. When I turn up the thermostat there is no sound at the unit.

Contractor's Assistant: Just to clarify, do you think this is a larger HVAC problem, or something specific to the thermostat?

Think larger problem than the thermostat. Pilot stays lit. Don't think it is power problem unless there is a fuse somewhere that is bad.

Contractor's Assistant: Do you plan on doing the work yourself?

Would like to but really don't know where to start beyond the thermocouple and thermostat.

Contractor's Assistant: Anything else we should know to help you best?

The book talks about a blocked vent switch but I haven't found the reset button. don't think the vent was blocked since nothing has changed with the vent. Is there a fuse somewhere?

Submitted: 3 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 3 minutes by:
1/9/2018
HVAC Technician: Gaztech, HVAC Technician replied 3 months ago
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 799
Experience: Owner at Gaztech
Verified

Hi I amCustomer a independent technician, I will assist you with your issue.

Don't forget to rate the 5 star rating AT THE TOP OF PAGE if we are done. this will credit me for assisting you.

Turn up thermostat and check if there is 24 volt ac at the gas valve wires

Ask Your Own HVAC Question
Customer reply replied 3 months ago
I checked the red wires near the thermocouple goes into the gas control unit. If those are the gas valve wires there is no juice.
HVAC Technician: Gaztech, HVAC Technician replied 3 months ago

Check if transformer input has 120 volts in and 24 volts output

And check if high limit switch has opened contact.

Ask Your Own HVAC Question
HVAC Technician: Gaztech, HVAC Technician replied 3 months ago

BTW, whats the model number?

Ask Your Own HVAC Question
HVAC Technician: Gaztech, HVAC Technician replied 3 months ago

Where are you????

Ask Your Own HVAC Question
HVAC Technician: Gaztech, HVAC Technician replied 3 months ago

I noticed question is still opened?

Did you resolve problem?

Ask Your Own HVAC Question
Was this answer helpful?
Ask Gaztech Your Own Question
Gaztech
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 799
799 Satisfied Customers
Experience: Owner at Gaztech

Gaztech is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
What's code 13 on a Richmond tankless water heater? Just
What's code 13 on a Richmond tankless water heater? … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Burnham sea 15 code. All day. Maby. No sea 15 code wating
burnham sea 15 code JA: I'll do all I can to help. How long have you been dealing with this? Customer: all day JA: Do you plan on doing the work yourself? Customer: maby JA: Anything else we should kn… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Well my furnace will not turn on I have a dependent
Well my furnace will not turn on I have a dependent dependable ninety two not sure the model number I believe it's the flame detector that's dirty but I can't seem to find where that is even located o… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Can you tell me what the service code #9 is for a Trane XV
Second opinion] Hi. Can you tell me what the service code #9 is for a Trane XV 80 Furnace?… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a MMHA 056ABHR 02 in my summer Home and it won't stay
Hello I have a Miller MMHA 056ABHR 02 in my summer Home and it won't stay lit. I will get the ignition and a great flame and then it goes out. I have replaced the igniter kit but it still won't stay l… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a evcon dgato56bdd that the circuit broad blinks
I have a evcon dgato56bdd that the circuit broad blinks continuous and does not run … read more
HvacmanSean
HvacmanSean
Owner
HVAC
232 satisfied customers
My central AC unit shuts off soon after it turns on. 5-30
My central AC unit shuts off soon after it turns on. 5-30 seconds … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Plus 90 age about 1997, codes between 13-33. currently 33.
bryant plus 90 age about 1997, codes between 13-33. currently 33. ohm meter goes clear over on limit switch … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a fairly new Ruud gas furnace. Yesterday we got heavy
Hi...I have a fairly new Ruud gas furnace. Yesterday we got heavy rain here in CT and the basement flooded. I turned off the furnace and the rain stopped with water draining out but furnace got wet. I… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My boiler is losing Pressure. 1weeknow. How much Treasure
My boiler is losing Pressure JA: I'll do all I can to help. How long have you been dealing with this? Customer: 1weeknow JA: Do you plan on doing the work yourself? Customer: Yes JA: Anything else we … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My outside HVAC compressor is making a vibrating noise that
My outside HVAC compressor is making a vibrating noise that I need help diagnosing. Has been going on for a couple of weeks now. Unit works but the noise is concerning. I have a video recording of the… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I had an 18000 BTU heat pump installed in my garage. Its is
I had an 18000 BTU heat pump installed in my garage. Its is 30x30 . Not happy but my installer says its ok... Its 50 degrees F outside today but still only up to 61 in my garage. doesnt seem right to … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Have a 15-20 yr old trane RTU unit will run about 10 -15 min
have a 15-20 yr old trane RTU unit will run about 10 -15 min then the compressor fan stops running. The circulating fan run fine … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have a 10 years old home. From day 1, this house has
I have a 10 years old home. From day 1, this house has always been rented out. Now that the tenant has moved out and I am ready to sell the house. I called a company to clean the vent return only, ins… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a trane XR 80..need to open door to replace filter
I have a trane XR 80..need to open door to replace filter but apparently I am not getting the two black knobs in the right position to open … read more
Gaztech
Gaztech
HVAC Technician
799 satisfied customers
Have a power vent hot water heater. replaced gas valve.
have a power vent hot water heater. replaced gas valve. worked for several hot and then went into lock out with . … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a 80% arco furnace and after a power failure the
I have a 80% arco furnace and after a power failure the furnace will not come on al all. The LED on the gas valve is on steady … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Crown wall hung boiler with a Wilocirculator that
I have a Crown wall hung boiler with a Wilo(###) ###-####circulator that has failed. would like to buy just motor cartridge if possible. is there a part number for that , or what other model pump woul… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.