I have a PAH90AF and it will not Ignite. The Igniter is

Customer Question
I have a PAH90AF...

I have a PAH90AF and it will not Ignite. The Igniter is sparking and to pilot is lit. The flame came on once when i heard a click and then went out. The power vent is running and the big fan is also running. I was thinking pressure switch but it is trying to ignite but seems lack of fuel or valve opening. Nay suggestions ?

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

Well the furnace hasn't run in some time because of this conditio. So yesterday went through and clean and check all fuel lines, exhaust and wire conections

Contractor's Assistant: Did you check the furnace's filters?

Yes except the fuel valve. not sure if there is one in there as there are safety torx on the cover

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Submitted: 6 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 6 minutes by:
1/9/2018
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,693
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, if the burner ignites for a second or two then goes out, the cause is almost always a dirty flame sensor rod. You can clean that off with steel wool.

.

That would be the first step, it has about an 70% chance of working... there is a 30% chance the printed circuit board is bad, I am estimating that based on the main blower running when the burners are not on.

.

If you want up to 24 hours of coaching well above 'Just an Answer' rate positively now, then

Take close up, exceedingly well focused photo's of the wiring diagram glued inside the furnace/air handler door, and the printed circuit board mounted on the blower, , that shows where the thermostat wires connect, and I will mark them up with trouble shooting instructions.

Use the 'add files' link next to your send button to get the photo(s) to me.

.

We can go from there with training, coaching and diagnosis.... without a time limit, In depth with as much detail as needed .

. select the 'finish and rate your expert link' near the top of your page and click on it.

.
My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today. If you need more assistance, please use the reply box and let me know.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Where would i fine the flame sensor rod on this unit?
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago

The flame sensor rod will be poking into the burner flames on one of the burners, about an inch above the burner... all you will see is a small white ceramic piece with ONE wire coming out and running to the printed circuit board... its held in place by a 1/4" hexagonal head screw, remove the screw and pull the flame sensor out to clean it..

.

click here please, this should be close to the model you have, see page 24 for flame sensing circuit

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,693
9,693 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,693 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Dayton Fuel Trimmer Plus Model 4E455A 60,000 BTU
I have a Dayton Fuel Trimmer Plus Model 4E455A 60,000 BTU 80% heater.The heater exhaust fan comes on the ignitor does not ,then the blower motor starts.I manually lite the pilot it burned & burned yet… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have an ancient Magic Chef furnace that wont turn on.
I have an ancient Magic Chef furnace that wont turn on. Pilot lights but it never kicks on to heat the house. Model is EG6A75D-8. … read more
MattR757
MattR757
HVAC Contractor / Owner
Associate Degree
14 satisfied customers
I have a modine pah90af that doesnt lite .when I turn the
I have a modine pah90af that doesn't lite .when I turn the thermostat up the exhaust fan starts then in a short period of time I hear one click and the big fan starts. I used to hear 3 o 4 clicks for … read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a Carrier Carrier Weathermaker SXA080. The thermostat
I have a Carrier Carrier Weathermaker SXA080. The thermostat calls for heat. The burner fan comes on, about 10 seconds later the pilot comes on. It used to take at least a minute, sometimes more befor… read more
Heath.M
Heath.M
Refrigeration Mechanic
Vocational, Technical or Trade School
223 satisfied customers
Hello. New install. Modine hd45 powered exhaust nat gas. No
Hello. New install. Modine hd45 powered exhaust nat gas. No ignition. Thermostat on, exhaust fan on, nothing, short delay, fan off. Green led always. See/hear no spark. 15Vac thru all closed temp swit… read more
V12Tech
V12Tech
252 satisfied customers
I have a Carrier furnace (395BAW048080AABA). The draft inducer
I have a Carrier furnace (395BAW048080AABA). The draft inducer fan will come on (I replaced the cage wheel which had desinigrated from rust), then the ignitor will spark and the pilot will light. The … read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a Lennox Pulse 21 furnace purchased in 1992. This
I have a Lennox Pulse 21 furnace purchased in 1992. This past year it took several tries for the furnace to begin running. at times it ignites on the 5th or 6th try. It often sounds like it backfires,… read more
Wvfan79
Wvfan79
Mecanical Designer & Estimator
High School or GED
775 satisfied customers
Furnace man has spent two hours and it still wont work. F09
Furnace man has spent two hours and it still won't work. F09 error code, good spark, fuel but won't light. What do I do?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hello, Ive got a Heatilator fireplace GC150 E with a Robert
Hello, I've got a Heatilator fireplace GC150 E with a Robert Shaw 832 controller DSI unit. The unit has been slowly failing, I get a good spark, it would sometimes come on and burn for as long as 15 m… read more
Jerry
Jerry
Plumber
High School or GED
1,456 satisfied customers
lennox G20Q5e -150Hard start... when turning the furnace
lennox G20Q5e -150 Hard start... when turning the furnace on, the pilot will light then go out. it will not try and restart. after manually restarting the furnace, it seems that the pilot sensor gets … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I am working a 1992 Reznor model F250. When the thermostat
I am working a 1992 Reznor model F250. When the thermostat closes, the exhaust fan comes on for about 30 seconds, then the main blower fan turns on. However, the spark for ignition or flames are never… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Greetings... I have a BDP (Carrier) 395AAW048070 circa 1983.
Greetings... I have a BDP (Carrier) 395AAW048070 circa 1983. I'm still trying to familiarize myself with all the parts and pieces of this system (with the help of the interweb) so I'm at that point wh… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Lennox furnace ignites pilot but pilot withers and goes out
Lennox furnace ignites pilot but pilot withers and goes out before ingnition sequence finishes… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
The main burner on my Airco 8300 Turbo gas furnace will not
The main burner on my Airco 8300 Turbo gas furnace will not stay lit. When the furnace starts the little fan in the chimney runs, the pilot light ignites and then the main burner fires after 3-5 secon… read more
G Wurtz
G Wurtz
Instructor of HVACR Program
Master's Degree
57 satisfied customers
Rheem Imperial 90 furnace.... exhaust fan cycels and pilot
Rheem Imperial 90 furnace.... exhaust fan cycels and pilot light ignites. Main burners will not ignite, have a ticking sound coming from the gas valve.… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a Comfortmaker N9MP1 furnace, and Im getting a trouble
I have a Comfortmaker N9MP1 furnace, and I'm getting a trouble signal of 6-2. The pilot light starts, then after a few seconds it blows itself out, and starts the process all over again until it times… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
Bard Furnace. Small exhaust fan comes on, igniter starts sparking
Bard Furnace. Small exhaust fan comes on, igniter starts sparking with what looks like a good spark to me, but 70% of the time it won't light the natural gas. Gas flow is then shut off and small exhau… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
I just tried to turn on the heat in my house this morning and
I just tried to turn on the heat in my house this morning and I heard an intermittant humming noise comming from the mechanical room. The noise sounded like it was from the furnace and lasted about 15… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x