Lennox furnace is showing ‘system is waiting’ on thermostat.

Customer Question
HVAC Company was called and...
Lennox furnace is showing ‘system is waiting’ on thermostat. HVAC Company was called and came out earlier today (this was after I ‘reset’ the furnace via the circuit breaker and everything was working ok) couldn’t locate any issues, ‘cleaned’ the furnace yet an hour later same error message came back on.Could this be an issue with the actual Wi-Fi thermostat?
Submitted: 1 month ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 hour by:
1/9/2018
HVAC Technician: Phil, Mechanical Engineer replied 1 month ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,200
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, we can run some tests.

I think its either a thermostat problem. or more likely a bad printed circuit board in the furnace..

.

test 1. Gently pry the thermostat from the wall, if it does not come off easily it might be a type with a few retainer screws.

When you get the thermostat off the wall, if it has R, W, Y, G and maybe a C terminal, fit a jumper wire between the R and W terminals on the thermostat if the furnace comes on, the problem is with the thermostat.

Test 2. IF the furnace does not come on with test 1, then turn the thermostat OFF, then go stand next to the furnace, listening *intently... the inducer fan should come on, then 2 to 3 seconds later you should hear a faint click (that is the pressure switch closing) .... then 20 to 30 seconds after that two more faint clicks...(those are the igniter and gas valve relays).

Then the burners should ignite. you will hear the whoomp sound... then if the burners go out after 2 to 5 seconds let me know all about that.

Repeat this test several times until you are familiar with the sequence and sounds, tell me how far the furnace gets in the start sequence before it fails (in cases where it fails).

.

We can go from there without any time limits in the morning, I am off to bed shortly tonight.

.

My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today. If you need more assistance, please use the reply box and let me know.

Ask Your Own HVAC Question
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,200
9,200 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,200 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Air Handler # NFCX3600C2 what causes the circuit breaker
Air Handler # NFCX3600C2 what causes the circuit breaker panel to fry? I replaced it once and the heat worked OK but when I tryed to run A C the board fryed again … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
427 satisfied customers
I have a 1982 Lennox furnace. For some reason, the burners
Hello - I have a 1982 Lennox furnace. For some reason, the burners only goes on when the temp is around 68 degrees even though my thermostat that is set for 74 degrees displays " Heat on". Any ideas o… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Lennox furnace model G26Q3-75-5. It shows a status
I have a Lennox furnace model G26Q3-75-5. It shows a status of Primary/Secondary Limit switch open. Once I shut off the power and then turn it back on it will start up and run in normal operating mode… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Lennox furnace that just had a new inducer motor
I have a Lennox furnace that just had a new inducer motor and control board installed. Now the furnace is working but it does not start to heat until the temperature gets below what the thermostat set… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
Trying to add Aprilaire 600M to Lennox furnace with iComfort
Trying to add Aprilaire 600M to Lennox furnace with iComfort tstat. … read more
Phil
Phil
Mechanical Engineer
9,200 satisfied customers
Lennox furnace that "burbs" very load when deicing. New.
Lennox furnace that "burbs" very load when deicing … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Parents g23 lennox furnace is light in front is continuously
parents g23 lennox furnace is green light in front is continuously flashing … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a Lennox furnace that was not turning on. It clicks
I have a Lennox furnace that was not turning on. It clicks twice and then gives the code for "Normal Operation with call for heat". I jumped the R and W terminals to check to see if it was thermostat … read more
Phil
Phil
Mechanical Engineer
9,200 satisfied customers
I have a Lennox furnace (EL296UH070XV36B-05) that is
I have a Lennox furnace (EL296UH070XV36B-05) that is currently wired for their iComfort Thermostat (ive been told its like a propitiatory wiring). Anyways I am wanting to wire it up for a Nest. I am l… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My Lennox furnace is having an issue - the flames are going
Hello, my Lennox furnace is having an issue - the flames are going out within a minute after starting. I see one of the flames "stutter" after 45 seconds and then the whole thing shuts down. … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
427 satisfied customers
We have two identical Lennox furnaces in our building. One
Hi. We have two identical Lennox furnaces in our building. One of them collects water in the inducer fan when it is cold outside, the other does not. I have checked the pvc leading to the drain and it… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a lennox furnace that is not working the furnace
hello i have a lennox furnace that is not working the furnace lights and the burners come on breifly then shut off i have a flash code of 8 flashes … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Having trouble with lennox furnace - it wont stay on. Therm
having trouble with lennox furnace - it wont stay on. Therm set at 72 and house temp is 65. watching the furnace it comes on for about 10 seconds and then goes off, blower runs about 1-1/2 minutes and… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
20 min ago my WiFi system on the lennox furnace gave me an
20 min ago my WiFi system on the lennox furnace gave me an error code of 271? serious issue or can it wait until tomorrow … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Turned off circuit breaker while furnace running ... turned
turned off circuit breaker while furnace running ... turned on circuit breaker ... furnace did not come back on ... got message system malfunction outside sensor error on carrier infinity 96. read you… read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
427 satisfied customers
I have a lennox furnace. the heat will come on for a few
I have a lennox furnace. the heat will come on for a few minutes and the control board shows a red and green light flashing quickly. then, it shuts off and shows a single green light flashing slow. my… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Lennox furnace that's not working. It has a
I have a Lennox furnace that's not working. It has a flashing green light. The label says check flame sensor. Where is this sensor?… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Will a weak capacitor trip the circuit breaker. Today only
well I can tell you I took off a fan motor that had 3 wires and replaced it with one with 4 wires… read more
Phil
Phil
Mechanical Engineer
9,200 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less