Heat pump Model: GBD080500738. No power to 22vdc heater

Customer Question
Heat pump...

Heat pump Model: GBD080500738

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

No power to 22vdc heater relay from circuit board.

Contractor's Assistant: Do you plan on doing the work yourself?

Yes. The new circuit board is getting 24vac.

Contractor's Assistant: Anything else we should know to help you best?

Too cold for outside unit to work.

Submitted: 6 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 42 minutes by:
1/7/2018
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,702
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello,

Take close up, exceedingly well focused photo's of the wiring diagram glued inside the furnace/air handler door, and the printed circuit board mounted on the blower, , that shows where the thermostat wires connect, and I will mark them up with trouble shooting instructions.

Use the 'add files' link next to your send button to get the photo(s) to me.

.

We can go from there with training, coaching and diagnosis.... without a time limit, In depth with as much detail as needed .

.

When we finally get the situation solved, please select the 'finish and rate your expert link' near the top of your page and click on it.

.
My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today. If you need more assistance, please use the reply box and let me know.

Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago

Hello, I see the 24 volt transformer on that diagram but not any heater relay that you are reporting 22vdc at, I need to see the diagram with that relay on it as well

Ask Your Own HVAC Question
Customer reply replied 6 months ago
I’ll be home in an hour
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago

Great, we can go from there then.

Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago

thanks, ***** ***** are getting 22 vac (not DC) across that contactor coil at the bottom of the diagram and its not closing and putting power to the electric heater strip, then the contactor is bad,

If you are getting 240 volts to the heater strip terminal, and the heating element is not getting hot, then the high temperature safety cut out switch shown to the right of the heating element on the diagram is open... turn power off to the unit, remove the wires from that switch and use an ohm meter to determine if its open or not.... if its open and it has no reset button on it, then its bad and needs to be replaced.

.

Its time to rate my input for the day, that gets me paid, locate the "finish and rate your expert" link near the top of the page and click on it. I will appreciate that very much.

I am in every day from 9 am to 11 pm west coast USA time to do any follow up needed.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
I have done all of that. The contact says 22vdc and no voltage is coming out of the card.
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago

These systems all run on 24volts AC you might have your meter set incorrectly, I cannot tell from here, tell me what the meter reads with a known 24vac source, such as the 24v control transformer.

You have not measured the 230 volt AC on the heavy wire though, did you understand my previous instruction, or do I need to say it another way.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
I said yes I did all of that, everything works fine all the voltages are good there is just no power coming out of the card to the relay. I could jumper the relay and all is well. I just paid $100 for a new card, and it still doesn’t work.
Customer reply replied 6 months ago
Is the circuitboard supposed to change the low-voltage from AC to DC to the relay.
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago

Hello again , you can dismount the relay and look at the side of the 22v coil and it will say if its 24 vac or 24vdc,

I have seen printed circuit boards rectify AC to DC its very rare, and in these cases there is no need for it.

.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Please refund my money, if you cannot identify the problem tomy satisfaction.
Customer reply replied 6 months ago
I believe I already stated The relay says 22 vDC
Customer reply replied 6 months ago
The relay will just buzz, if I put the 28vac to it. There is no voltage of any kind in the wires going to the relay.
Customer reply replied 6 months ago
I meant 24 VAC.
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago

I can never tell if if I am working with a teenager or an experienced old timer in the business....your remarks saying that the coil was putting out 22vdc suggested that you did not understand that the coil does not put out anything it uses any voltage applied to it.

.I will opt out however so that other experts here can jump in if they think they can help you.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Let me restate my problem for the next guy. The heat strip relay says on the side 22 vdc, but never recived any voltage from the old or new Circuit board which is getting 24 vac. Fan needs to start before Heat strips.
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,702
9,702 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,702 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Ac fan not working but compressor does put in new fan and
Ac fan not working but compressor does put in new fan and capacitor but fan still not runnimg … read more
Phil
Phil
Mechanical Engineer
9,702 satisfied customers
2shp13le136p-1 heat pump, heat pump will not come on unless
2shp13le136p-1 heat pump, heat pump will not come on unless I manually hold contactor in, how do jump thermostat or test it for voltage? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a heat pump system with electric resistance auxiliary
I have a heat pump system with electric resistance auxiliary for backup. Unit originally installed in 2003. Heating mode works fine when not in AUX HEATING and outside temp is above 25-30. Right now t… read more
Phil
Phil
Mechanical Engineer
9,702 satisfied customers
I have Goodman AC unit and Heat pump system. I am not
I have Goodman AC unit and Heat pump system. I am not getting the contactor for the fan and compressor to run when calling for heat and/or cool air. I've changed the run capacitor and contacter and ne… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,942 satisfied customers
Ihave rthl 3550 it one work on axu heat oney ihave a heat
ihave rthl 3550 it one work on axu heat oney ihave a heat pump it wount come on what rong … read more
Phil
Phil
Mechanical Engineer
9,702 satisfied customers
Equipment: Trane Heat Pump Model TWR036C100A0 S/N G46257905
Equipment: Trane Heat Pump Model TWR036C100A0 S/N G46257905 DOM 11/92 with a Honeywell Chronotherm IV Plus stat. Issue: Cooling mode working fine. When heat is called the outdoor unit fan comes on but… read more
Phil
Phil
Mechanical Engineer
9,702 satisfied customers
I have a Lennox EC10Q3-20-1 furnace with heat pump. Furnace
I have a Lennox EC10Q3-20-1 furnace with heat pump. Furnace is off meaning, room temperature is at desired level and the unit is not operating but there is still heat coming from the warm air plenum, … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
HI, I leave in Québec, and I have the electrical power company
HI, I leave in Québec, and I have the electrical power company (Hydro Quebec) providing us "Bi Energy" signal (24vac, 2 wires, black and white). When it is colder that -12Celsius the signal needs to c… read more
Bill P.
Bill P.
Installer/ Troubleshooter/Technician
286 satisfied customers
I have a Trane heat pump (TWR048C100A3?) that operates normally
I have a Trane heat pump (TWR048C100A3?) that operates normally in the summer and most of the time in the winter. However, occasionally in cold weather the unit will blow cold air inside the house; at… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
while repairing a wire to the defrost circuit board in the
while repairing a wire to the defrost circuit board in the heat pump a wire next to it came off. As I reattached it a low voltage spark occured and now I have no power to the thermostat. Yes I neglect… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Compressor/fan relay control problem. The relay checks good
Compressor/fan relay control problem. The relay checks good (i applied the 24vac for the heat pump sol to the relay and it works. When the thermostat is set to "heat" the freon sol energizes, but how/… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
I have an air-to-air heat pump, with auxillary heat strips
I have an air-to-air heat pump, with "auxillary" heat strips in the air handler, and a "defrost timer board" in the compressor unit. When this "defrost timer board" senses ice on the outside coils, it… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a heat pump that is not working. The air handler just
I have a heat pump that is not working. The air handler just blows cold air and the outside unit does not turn on. I have checked the power with a multimeter and I have 220 coming into the unit. I can… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
Nordyne heat/ac outside unit MDL# GR4GA-060K120C Gas
Nordyne heat/ac outside unit MDL# XXXXX Gas heater not coming on. Getting 120v to new ignitor & motor. Status lite on circuit board flashes twice & repeats. Any help would be greatly appreciated.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I replaced a old skuttle 592 with a new one. After installing
I replaced a old skuttle 592 with a new one. After installing it I tested it and it worked fine but after closing the furnace and retesting it quit working. I can't even get the blower to come on in t… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I have a Lennox E12Q3-20 2P heat pump and for the last few
I have a Lennox E12Q3-20 2P heat pump and for the last few weeks it has been building up ice now 2 inch thick) on outside unit. Seems to run all the time, located in PA so due to cold it heats OK but … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
i have a phf030 heat strips will not energize, defrost board
i have a phf030 heat strips will not energize, defrost board was replaced and still no 22vdc from control board to relays when 24vac is present at w1 and there is no od tstat… read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
I have an Amana BMA Multi Position Airhandler with a EDK07A
I have an Amana BMA Multi Position Airhandler with a EDK07A Electric Heating Kit. The heat went out in it today, and I am looking for simple things to check. I have verified that the thermostat and co… read more
Michael Reush
Michael Reush
Master Technician
High School or GED
2 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x