I have a Centurion 2 not working with the flashing indicator…

Customer Question
I have a Centurion...

I have a Centurion 2 not working with the green flashing indicator 4 time.

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

About 8 hrs

Contractor's Assistant: Do you plan on doing the work yourself?

If it’s easy to do. I read in one of yor articles it could be a clogged tube from a vent or motor.

Contractor's Assistant: Anything else we should know to help you best?

No that’s about it.

Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 22 hours by:
1/8/2018
HVAC Technician: airheatman, HVAC Technician replied 7 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,366
Experience: Furnace, A/C and heat pump specialist.
Verified

The 4 flash code is an open high temp limit error.
There may be
several limits on the furnace.Blow describes locations:
PRI***** *****MIT
The pri***** *****mit control is located on the partition panel and monitors
heat exchanger compartment temperatures. It is a normally closed
(electrically), automatic reset, temperature-activated sensor.
The limit guards against the overheating as a result of insufficient
conditioned air passing over the heat exchanger.
AUXILIARY LIMIT
The auxiliary limit control(s) are located on or near the circulator
blower and monitors heat exchanger compartment temperatures.
They are a normally-closed (electrically), manual-reset, temperature
activated sensors. These limits guard against overheating as a
result of insufficient conditioned air passing over the heat exchanger.
VENT DRAFGAURD
These would be located on the draft hood if you have one on your furnace.
ROLLOUT LIMIT
The rollout limit controls are mounted on the burner/manifold assembly
and monitor the burner flame. They are normally-closed
(electrically), manual-reset, temperature-activated sensors. These
limits guard against burner flames not being properly drawn into the
heat exchanger.
Lets start with the most simple and easy. Look near burners for limits with a little button in center.It will push in to reset.If none are tripped we will go from here. Let me know if you have a multi meter for troubleshooting.
http://i.imgur.com/CGkB9sa.jpg

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a DGAT090BDD furnace and I get a three flash error
I have a Coleman DGAT090BDD furnace and I get a three flash error code that indicates "centrifugal switch stuck open" condition. Am I correct that this switch is part of the furnace booster motor asse… read more
airheatman
airheatman
HVAC Technician
9,366 satisfied customers
I own a Trane XV90. past few weeks I am getting an
I own a Trane XV90. For the past few weeks I am getting an increasingly frequent situation where the 1st stage of the furnace fires 100% of the time but almost every time now the second stage attempts… read more
MattR757
MattR757
HVAC Contractor / Owner
Associate Degree
14 satisfied customers
Hi < I have a Reznor V3 T Core model Udap60. It is on Propane. When I turn it on it
Hi < I have a Reznor V3 T Core model Udap60. It is on Propane. When I turn it on it will not heat. Some motor comes on but the main fan does not. I have tried to restart the motor with no success. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Gibson power vent 90+ propane furnace. The problem
I have a Gibson power vent 90+ propane furnace. The problem is intermittent. The induction fan starts,the surface ignitor glows,the burner comes on for a couple seconda then goes off. The red light fl… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
We have a Lennox ML195UH and it is flashing 3 times
We have a Lennox ML195UH and it is flashing 3 times indicating "pressure switch open with combustion air inducer engergized." What does this mean and is it a simple fix we could do by resetting the ma… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We have a white Rogers thermostat 184960 on our water heater.
We have a white Rogers thermostat 184960 on our water heater. It's locked in vacation mode with the green led lit. We had a power outage yesterday so this may have caused the condition. Two other LEDs… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Ruud Acheiver 90 that is about 10 years old. The
I have a Ruud Acheiver 90 that is about 10 years old. The thermostat is set at 72, but the indoor temp is 63. I turned the thermostat from heat to off, but the supply fan continued to run, even after … read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
Have A question regarding my Trane HVAC that is out. I need
Have A question regarding my Trane HVAC that is out. I need to sign up for a plan first I guess but this site is not user friendly at all.… read more
airheatman
airheatman
HVAC Technician
9,366 satisfied customers
Lennox G43UF Heat isnt turning on...Diagnostic Code LED#1
Lennox G43UF Heat isn't turning on...Diagnostic Code LED#1 Red if off and Led #2 Green is flashing...Could be Pressure prove switch open or blocked inlet/exhaust vent or pressure switth closed prior t… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a three story building in Bronx NY. On the first floor,
I have a three story building in Bronx NY. On the first floor, there are two small stores and there are four apartments on the 2nd and 3rd floors. The apartments have two bedrooms each. Currently, I h… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
My Centurion II will not run up to the temperature that is
My Centurion II will not run up to the temperature that is set on the t-stat. It runs for about 3-4 minutes, flame shuts off, and the furnace does its normal end cycle. As soon as the fan stops, the f… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a RUUD High Efficiency Residential Heating unit in my
I have a RUUD High Efficiency Residential Heating unit in my attic. It was installed in 2004 and is 93.5 per cent efficient. Don't know model #. After replacing the air filters the heating system won'… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Hello. I have a Ruud 90 Plus furnace, installed in about 1995.
Hello. I have a Ruud 90 Plus furnace, installed in about 1995. Series URGA-10EZAJS, Serial #DF50707 F0495 2396. I just replaced the Induced Draft Blower (the squrial cage desinegrated), and now when I… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
luxaire 90 % furnace induced draft limit switch opens , 4 flashes
luxaire 90 % furnace induced draft limit switch opens , 4 flashes , hi limit ok furnace is about 2 yrs old… read more
TimVZ26
TimVZ26
Service Foreman
Vocational, Technical or Trade Scho
157 satisfied customers
I have a Rheem Criterion 2 furnace. the ok light is flashing
I have a Rheem Criterion 2 furnace. the "ok" light is flashing 4 times. If I trip one of the sensors can get furnace to cycle. Sometimes works for a week or two sometimes a cycle. Have had the guy who… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
have a rheem centurion furnace 80 pluse approx 4 years old,
have a rheem centurion furnace 80 pluse approx 4 years old, intermintently furnace will not com on. take off the upper cover to see combustion blower and furnace will start and run for days. furnace w… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
have a rheem gas furnace RGPH have 3 indicator lights one amber(Flame) Green(OK)
have a rheem gas furnace RGPH have 3 indicator lights one amber(Flame) Green(OK) AND Green (power). The green OK Indicator is flashing 4 times meaning presure switch closed. How do i fix this Unit doe… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
my family just moved into a new home with 2 Goodman GKS9 furnaces.
my family just moved into a new home with 2 Goodman GKS9 furnaces. One works perfectly well but the other has the LED light that beeps 3 times...i have tried to flip the breaker. the unit appears to s… read more
DanielC
DanielC
Service manager
High School or GED
95 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x