I have a avptc426014AA air handler with a heat pump primary…

Customer Question
I have a avptc426014AA...

I have a avptc426014AA air handler with a heat pump primary and electric heat backup. It’s -1 outside and for the past few days, seems the floor never comes up to temp the thermostat is set at. It’s set at (higher than usual) 74 and its 63 in here. The blower motor comes on for about three to five minutes then shuts off. It does blow warm air out the vents when it runs. However it doesn’t remain running very long. About 15 minutes go by then comes back on again for another few minutes. The thermostat is a Honeywell and I edited the schedule so it is calling for the same temp all the time. I have tried to just turn on the blower. Is thermostat but it doesn’t come on, but I know it works.

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Filter changed yesterday.

Contractor's Assistant: Do you plan on doing the work yourself?

Sure!

Contractor's Assistant: Anything else we should know to help you best?

Six green flashes. I do not have it communicating via Ethernet or home system. There is one red led that’s on all the time.

Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 13 minutes by:
1/7/2018
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 939
Experience: Owner at Gaztech
Verified

Hi I amCustomer a independent technician, I will assist you with your issue.

Don't forget to rate the 5 star rating AT THE TOP OF PAGE if we are done. this will credit me for assisting you.

TO RECALL THE LAST 6 FAULTS, MOST RECENT TO LEAST RECENT,

Locate diagnostic led and button on furnace control board.

DEPRESS SWITCH FOR MORE THAN 2 SECONDS WHILE IN STANDBY (N

DEPRESS SWITCH FOR MORE THAN 2 SECONDS WHILE IN STANDBY (N

THERMOSTAT INPUTS)

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Ok I’ll head to the attic. Rather cold. How should I put the unit in “standby”
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago

Set t-stat to off

Ask Your Own HVAC Question
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago

The diagnostic led will give flashes, count flashes between pauses.

there might be defferent faults

Fault chart is in your manual or sticker in furnace

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Pressed fault recall button. The flashing green LED went out. The red LED (fault recall) still on. The only green led flashing is the data one. I have no Ethernet cable to this thing. At this point I have no fault code
Customer reply replied 8 months ago
Oh and the tstat was turned off as directed
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago

Then I suspect possible t-stat issue

Ask Your Own HVAC Question
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago

Does blower turn on when you set t-stat to fan on?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Could a bad tstat cause the 6 green flashes on the board? There were the6 flashes prior to hitting the recal button
Customer reply replied 8 months ago
The blower does not come on when I tell it to. Weird thing is it does work and comes on when it wants
Customer reply replied 8 months ago
Let me try to turn it on
Customer reply replied 8 months ago
Stand by
Customer reply replied 8 months ago
Fan set to on. Tstat clicked. Fan not running. System set to off still.
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago

GREEN CFM LED - EACH FLASH REPRESENTS 100CFM (USE FOR AIRFLOWAPPROXIMATION ONLY) - EXAMPLE: 8 FLASHES = 800CFM

Blower speed status LED

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Blower fan did not come on. On the tstat I still have the system “off”.
Customer reply replied 8 months ago
Correction. Blower is running but not strong.
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago

Here is fault chart

https://www.manualslib.com/manual/1289171/Goodman-Avptc42d14-Series.html?page=22#manual

What make and model of t-stat do you have?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Honeywell TH8320u1008
Customer reply replied 8 months ago
Yeah I read a little of the chart but thought the 6 led flashes I was getting was the code. Then read about the blower module and a whole bunch of stuff could be wrong with the 6 flashes.
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago
Ask Your Own HVAC Question
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago

Nothing on segment diagnostic display I assume

Ask Your Own HVAC Question
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago

Are you still there?

Ask Your Own HVAC Question
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago

segment diagnostic display is on furnace control board and will show E? if there is a issue

Pager 24-27

https://www.manualslib.com/manual/1289171/Goodman-Avptc42d14-Series.html?page=24#manual

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Pic of board coming
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago

I dont see E display either, must be diferent model

Ask Your Own HVAC Question
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago

Lets try something else, put panel back on furnace the go to t-stat

Pull t-stat off the wall plate and at wire terminals put a jumper between terminal R and W to see is furnace starts to heat

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Ok give me a little bit
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago

If it makes it easier, remove both wire and twist R and W together

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Ok little update. I changed the batteries on the tstat. They were a littl corroded. Plugged the tstat back on. Turned it to Heat and it is heating. There are 16 flashes now instead of 8. So 1600 cfm got it. I did that about 5 minutes ago and the blower has not shut off yet. I am getting heat (Luke warm). I volt metered the incoming lines. I have two 60 amp feeds going to the furnace. Both breakers check out fine. I have voltage on all heat elements. However what I am missing is amperage on the one double pole breaker. The other is drawing 45 amps and the A coil is warm. I could be wrong but shouldn’t the other breaker have a load on it as well when it’s this cold out. I don’t see how the heat pump would be doing much good. I am getting 23 amps on the one set of elements but the other set is giving me 0.3 amps. Can you assist me in troubleshooting these elements or seeing if one of the relays are bad? After typing this on my phone with frozen hands, blower is still running strong
Customer reply replied 8 months ago
I am completely comfortable working in the furnace while “hot”. I am a journeyman wireman. Just not an HVAC guy.
Customer reply replied 8 months ago
Unless the other two elements are for emergency heat. Which I have not tried
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago

You have a 2 stage furnace, W2 terminal needs to be energised, bypass w1 and w2 at furnace control board to see if other elements energise

Ask Your Own HVAC Question
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago

I am getting ready to go out with kids soon.

Ask Your Own HVAC Question
Customer reply replied 8 months ago
by bypassing W1 and W2, just switch them around?
Customer reply replied 8 months ago
Have fun with the kiddos.
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago

No put jumper wire 18 gauge between the 2 terminals

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Ok gotcha I’ll jump them and see. Hit me up when you get back please
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago

Try what I am saying, will check in 5 minutes, slowly getting ready

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Will do I’m on my way back up there. I have 4 kids the oldest is 9 so I completely understand lol
Customer reply replied 8 months ago
W1 and w2 already jumped together
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago

OK,

element relays are 24 v coil, it may be DC volt. see if there getting 24v

and elements are 10-12 ohms each.

High limit switch to each elements are normaly close

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Ok give me a while. Go do your thing. I’ll check back in with you later. I can’t safely get to the coil wires with all the other wires in the way. Gonna have to move some stuff to check those items.
Customer reply replied 8 months ago
Ok weird
I just closed up the furnace to grab something to eat. That blower ran non stop all that time. Closed the panel and it’s shutting down now. Wonder what the deal is with that?
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago

It may be coincidence? reset unit ( power off 10 sec. ) check if posible error code.

Blower motor is ECM electronic control motor.

For diagnosing element area, I wear new thin spandex work gloves with a light rubber coating on the front side.

just avoid touching ground helps alot

Shut power off to check element Ohms

Power on for relays obviously.

Ask Your Own HVAC Question
Customer reply replied 8 months ago
I’ll have to tear into this after bit. We have other issues at the moment. Thanks for your help today and I’ll hit you up tomorrow evening.
I do believe I have a bad sequencing relay though. Not 100% sure cause I got pulled away. Don’t close the chat please
Customer reply replied 8 months ago
It’s heating once again but the outdoor temp went up to 18-20.
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago

Sequencers do sthe same as relays but often need replacing.

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Not sure what happened but we are at 70 degrees now. Tstat is still set at 72
The outside ambient temp went up to 20F.
Blower working ok, throwing heat. It does cycle on and off but not as much. I honestly believe the other set of elements need looked at and it’s probably that relay. Unless the DIP switches tell it when to come on (if they are even set right). The only thing I actually did was replace the batteries on the Tstat. They were bad corroded. Maybe a combo of that and the outside temp going up enough the heat pump started working. I’m going to dive back into this later in the week when it’s supposed to be in the mid to high 40’s. In the meantime I’m ordering two relays. That why if it is one of those, I have a spare on hand and another spare for future. Outside of that, not sure what else it could be except the tstat itself which seems to be working ok at this point. If one of the elements or limit switches are
Bad, then I’ll deal with that and I cross that bridge. Luckily the weather is supposed to warm up a bit and should give me a window to work with this. My second floor is roughly 2,000 sqft. In your opinion, do you feel that I have the correct unit? 9’ ceilings. Not sure of the size heat pump I have (didn’t go out and look). Regardless even if I have to heat this floor with the heater kit in the air handler, shouldn’t it be sized so that it can help up? I mean if it’s -40 outside, I can see maybe not keeping the entire floor heated efficiently but not -1/-7. Just my opinion. Maybe with the other elements not working or being told to operate, the thing just doesn’t have a chance to catch up. Just curious if the size unit I have is adequate enough in your opinion. Thanks again for your help. Not sure what we did and I don’t think it’s fixed but it’s better than it was. Keep this open if that’s ok with you and if you don’t hear back from me by Friday, close it out or shoot me a message. Thanks again. Stp
Customer reply replied 8 months ago
Sorry about the misplaced words. Spell check changed them for me lol
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago

The heater kit used for your furnace is not identified on the furnace rating plate.

Hkr 21 being the bigest one available and think that is the one that should have been chosen.

As far as Heat pump its 400 sqFt/ ton as rule of thumb

Ask Your Own HVAC Question
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago

I noticed question is still opened?

Did you resolve problem?

Best regards

Customer/p>
Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Gaztech Your Own Question
Gaztech
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 939
939 Satisfied Customers
Experience: Owner at Gaztech

Gaztech is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Is there a way to reset the schedule for our thermostat? I
Is there a way to reset the schedule for our thermostat? … read more
jhvac
jhvac
2 satisfied customers
The temperature outside is 21 degrees. The Aux heat is on. I
The temperature outside is 21 degrees. The Aux heat is on. I have messed with the outdoor lockout heat pump setting and the outdoor lockout back up heat settings. What should they be set on to bring t… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Replacing Lennox 36G7101 with Honeywell RTH6450. Need help
Replacing Lennox 36G7101 with Honeywell RTH6450. Need help with wire code for Honeywell Wire CODE CONNECTION LENNOX Y-YELLOW M-ORANGE F-GREEN V-RED R-BLUE… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a lennox 4 ton high effiency 16 sear unit installed
I have a lennox 4 ton high effiency 16 sear unit installed 3/2016. my unit on heat not a heat pump has heat strips .the unit thermostat is set at 74 degrees now. the unit starts up and runs 3 min cuts… read more
hvacdave84
hvacdave84
53 satisfied customers
I can't figure out why my furnace won't run sometimes. The
I can't figure out why my furnace won't run sometimes. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
We moved into this house last summer. Heat has been working
We moved into this house last summer. Heat has been working fine so far. Last night, we used the gas fireplace for first time. I don't know if that is a factor, but now the Honeywell thermostat seems … read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a question about programming a Honeywell thermostat; can you assist? New thermosta
I have a question about programming a Honeywell thermostat; can you assist? New thermostat model is RTH6450.… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
My furnace does not shut off automatically. It is an Airease
My furnace does not shut off automatically. It is an Airease BCS2 Air Handler (installed in Aug. 2009) with a Honeywell thermostat (no info can be found on the thermostat itself) which looks to be ver… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Im having issues with my Rheem RHLLHM3821 JA. The issue seems
Im having issues with my Rheem RHLLHM3821 JA. The issue seems to be the air handler as when the unit needs to come on (Thermostat set to 74 and reads 78 inside) I can hear cracking inside the Air Hand… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hello. I just installed a new Honeywell RTHL 2310/RTHL 221
Hello. I just installed a new Honeywell RTHL 2310/RTHL 221 Series thermostat to operate my Trane heat pump. When I turned the AC on, the motor, fan, and blower operate, but it blows ambient temp air, … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
I have an avptc426014AA AIR HANDLER and the blower motor wont
I have an avptc426014AA AIR HANDLER and the blower motor wont come on , I am getting 6red flashes on the control board and 1 green flash , what is the corrective action… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
HI - I have a Trane air handler and heat pump installed at
HI - I have a Trane air handler and heat pump installed at my cabin in SE British Columbia, but no longer have a dealer/service person as they have gone out of business. Just yesterday, the fan on the… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I am installing an HVAC system where the primary heat source
I am installing an HVAC system where the primary heat source is a forced air woodstove attached to a Goodman air handler with a primary and backup electric heat kit in the plenum. What is the best the… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I just hooked up my honeywell rth2300 thermostat.. I have
I just hooked up my honeywell rth2300 thermostat.. I have electric heat with a heat pump. I have 6 wires coming out from the wall - w, g, r, y, o, and brown. I hooked the corresponding colors to the c… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a White-Rodgers IF90-1, installed in 1988. Twice in
I have a White-Rodgers IF90-1, installed in 1988. Twice in recent weeks, when the AC went on, the "current room temp" display starts moving down, for example from 74 (same as the setting) down to 68 i… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We are in a new home this winter. Our Air Handlers heat system
We are in a new home this winter. Our Air Handlers heat system is about 4 y/o. We have our temps set really low due to high electric costs in our area. The problem is as long as the system is turned o… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
why doesnt my air handler blower kick on when my t-stat calls
why doesn't my air handler blower kick on when my t-stat calls for heat and my outside unit is running? if i raise temp on t-stat enough to call for aux heat the blower works fine, also it is not cons… read more
Charles
Charles
HVAC Technician
Associate Degree
91 satisfied customers
can you help with programming we are trying to set to heat,
can you help with programming? we are trying to set to heat, house is cold, and cannot do it. Thank you… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x