I have a avptc426014AA air handler with a heat pump primary…

Customer Question
I have a avptc426014AA...

I have a avptc426014AA air handler with a heat pump primary and electric heat backup. It’s -1 outside and for the past few days, seems the floor never comes up to temp the thermostat is set at. It’s set at (higher than usual) 74 and its 63 in here. The blower motor comes on for about three to five minutes then shuts off. It does blow warm air out the vents when it runs. However it doesn’t remain running very long. About 15 minutes go by then comes back on again for another few minutes. The thermostat is a Honeywell and I edited the schedule so it is calling for the same temp all the time. I have tried to just turn on the blower. Is thermostat but it doesn’t come on, but I know it works.

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Filter changed yesterday.

Contractor's Assistant: Do you plan on doing the work yourself?

Sure!

Contractor's Assistant: Anything else we should know to help you best?

Six green flashes. I do not have it communicating via Ethernet or home system. There is one red led that’s on all the time.

Submitted: 3 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 13 minutes by:
1/7/2018
HVAC Technician: Gaztech, HVAC Technician replied 3 months ago
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 803
Experience: Owner at Gaztech
Verified

Hi I amCustomer a independent technician, I will assist you with your issue.

Don't forget to rate the 5 star rating AT THE TOP OF PAGE if we are done. this will credit me for assisting you.

TO RECALL THE LAST 6 FAULTS, MOST RECENT TO LEAST RECENT,

Locate diagnostic led and button on furnace control board.

DEPRESS SWITCH FOR MORE THAN 2 SECONDS WHILE IN STANDBY (N

DEPRESS SWITCH FOR MORE THAN 2 SECONDS WHILE IN STANDBY (N

THERMOSTAT INPUTS)

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Ok I’ll head to the attic. Rather cold. How should I put the unit in “standby”
HVAC Technician: Gaztech, HVAC Technician replied 3 months ago

Set t-stat to off

Ask Your Own HVAC Question
HVAC Technician: Gaztech, HVAC Technician replied 3 months ago

The diagnostic led will give flashes, count flashes between pauses.

there might be defferent faults

Fault chart is in your manual or sticker in furnace

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Pressed fault recall button. The flashing green LED went out. The red LED (fault recall) still on. The only green led flashing is the data one. I have no Ethernet cable to this thing. At this point I have no fault code
Customer reply replied 3 months ago
Oh and the tstat was turned off as directed
HVAC Technician: Gaztech, HVAC Technician replied 3 months ago

Then I suspect possible t-stat issue

Ask Your Own HVAC Question
HVAC Technician: Gaztech, HVAC Technician replied 3 months ago

Does blower turn on when you set t-stat to fan on?

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Could a bad tstat cause the 6 green flashes on the board? There were the6 flashes prior to hitting the recal button
Customer reply replied 3 months ago
The blower does not come on when I tell it to. Weird thing is it does work and comes on when it wants
Customer reply replied 3 months ago
Let me try to turn it on
Customer reply replied 3 months ago
Stand by
Customer reply replied 3 months ago
Fan set to on. Tstat clicked. Fan not running. System set to off still.
HVAC Technician: Gaztech, HVAC Technician replied 3 months ago

GREEN CFM LED - EACH FLASH REPRESENTS 100CFM (USE FOR AIRFLOWAPPROXIMATION ONLY) - EXAMPLE: 8 FLASHES = 800CFM

Blower speed status LED

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Blower fan did not come on. On the tstat I still have the system “off”.
Customer reply replied 3 months ago
Correction. Blower is running but not strong.
HVAC Technician: Gaztech, HVAC Technician replied 3 months ago

Here is fault chart

https://www.manualslib.com/manual/1289171/Goodman-Avptc42d14-Series.html?page=22#manual

What make and model of t-stat do you have?

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Honeywell TH8320u1008
Customer reply replied 3 months ago
Yeah I read a little of the chart but thought the 6 led flashes I was getting was the code. Then read about the blower module and a whole bunch of stuff could be wrong with the 6 flashes.
HVAC Technician: Gaztech, HVAC Technician replied 3 months ago
Ask Your Own HVAC Question
HVAC Technician: Gaztech, HVAC Technician replied 3 months ago

Nothing on segment diagnostic display I assume

Ask Your Own HVAC Question
HVAC Technician: Gaztech, HVAC Technician replied 3 months ago

Are you still there?

Ask Your Own HVAC Question
HVAC Technician: Gaztech, HVAC Technician replied 3 months ago

segment diagnostic display is on furnace control board and will show E? if there is a issue

Pager 24-27

https://www.manualslib.com/manual/1289171/Goodman-Avptc42d14-Series.html?page=24#manual

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Pic of board coming
HVAC Technician: Gaztech, HVAC Technician replied 3 months ago

I dont see E display either, must be diferent model

Ask Your Own HVAC Question
HVAC Technician: Gaztech, HVAC Technician replied 3 months ago

Lets try something else, put panel back on furnace the go to t-stat

Pull t-stat off the wall plate and at wire terminals put a jumper between terminal R and W to see is furnace starts to heat

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Ok give me a little bit
HVAC Technician: Gaztech, HVAC Technician replied 3 months ago

If it makes it easier, remove both wire and twist R and W together

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Ok little update. I changed the batteries on the tstat. They were a littl corroded. Plugged the tstat back on. Turned it to Heat and it is heating. There are 16 flashes now instead of 8. So 1600 cfm got it. I did that about 5 minutes ago and the blower has not shut off yet. I am getting heat (Luke warm). I volt metered the incoming lines. I have two 60 amp feeds going to the furnace. Both breakers check out fine. I have voltage on all heat elements. However what I am missing is amperage on the one double pole breaker. The other is drawing 45 amps and the A coil is warm. I could be wrong but shouldn’t the other breaker have a load on it as well when it’s this cold out. I don’t see how the heat pump would be doing much good. I am getting 23 amps on the one set of elements but the other set is giving me 0.3 amps. Can you assist me in troubleshooting these elements or seeing if one of the relays are bad? After typing this on my phone with frozen hands, blower is still running strong
Customer reply replied 3 months ago
I am completely comfortable working in the furnace while “hot”. I am a journeyman wireman. Just not an HVAC guy.
Customer reply replied 3 months ago
Unless the other two elements are for emergency heat. Which I have not tried
HVAC Technician: Gaztech, HVAC Technician replied 3 months ago

You have a 2 stage furnace, W2 terminal needs to be energised, bypass w1 and w2 at furnace control board to see if other elements energise

Ask Your Own HVAC Question
HVAC Technician: Gaztech, HVAC Technician replied 3 months ago

I am getting ready to go out with kids soon.

Ask Your Own HVAC Question
Customer reply replied 3 months ago
by bypassing W1 and W2, just switch them around?
Customer reply replied 3 months ago
Have fun with the kiddos.
HVAC Technician: Gaztech, HVAC Technician replied 3 months ago

No put jumper wire 18 gauge between the 2 terminals

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Ok gotcha I’ll jump them and see. Hit me up when you get back please
HVAC Technician: Gaztech, HVAC Technician replied 3 months ago

Try what I am saying, will check in 5 minutes, slowly getting ready

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Will do I’m on my way back up there. I have 4 kids the oldest is 9 so I completely understand lol
Customer reply replied 3 months ago
W1 and w2 already jumped together
HVAC Technician: Gaztech, HVAC Technician replied 3 months ago

OK,

element relays are 24 v coil, it may be DC volt. see if there getting 24v

and elements are 10-12 ohms each.

High limit switch to each elements are normaly close

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Ok give me a while. Go do your thing. I’ll check back in with you later. I can’t safely get to the coil wires with all the other wires in the way. Gonna have to move some stuff to check those items.
Customer reply replied 3 months ago
Ok weird
I just closed up the furnace to grab something to eat. That blower ran non stop all that time. Closed the panel and it’s shutting down now. Wonder what the deal is with that?
HVAC Technician: Gaztech, HVAC Technician replied 3 months ago

It may be coincidence? reset unit ( power off 10 sec. ) check if posible error code.

Blower motor is ECM electronic control motor.

For diagnosing element area, I wear new thin spandex work gloves with a light rubber coating on the front side.

just avoid touching ground helps alot

Shut power off to check element Ohms

Power on for relays obviously.

Ask Your Own HVAC Question
Customer reply replied 3 months ago
I’ll have to tear into this after bit. We have other issues at the moment. Thanks for your help today and I’ll hit you up tomorrow evening.
I do believe I have a bad sequencing relay though. Not 100% sure cause I got pulled away. Don’t close the chat please
Customer reply replied 3 months ago
It’s heating once again but the outdoor temp went up to 18-20.
HVAC Technician: Gaztech, HVAC Technician replied 3 months ago

Sequencers do sthe same as relays but often need replacing.

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Not sure what happened but we are at 70 degrees now. Tstat is still set at 72
The outside ambient temp went up to 20F.
Blower working ok, throwing heat. It does cycle on and off but not as much. I honestly believe the other set of elements need looked at and it’s probably that relay. Unless the DIP switches tell it when to come on (if they are even set right). The only thing I actually did was replace the batteries on the Tstat. They were bad corroded. Maybe a combo of that and the outside temp going up enough the heat pump started working. I’m going to dive back into this later in the week when it’s supposed to be in the mid to high 40’s. In the meantime I’m ordering two relays. That why if it is one of those, I have a spare on hand and another spare for future. Outside of that, not sure what else it could be except the tstat itself which seems to be working ok at this point. If one of the elements or limit switches are
Bad, then I’ll deal with that and I cross that bridge. Luckily the weather is supposed to warm up a bit and should give me a window to work with this. My second floor is roughly 2,000 sqft. In your opinion, do you feel that I have the correct unit? 9’ ceilings. Not sure of the size heat pump I have (didn’t go out and look). Regardless even if I have to heat this floor with the heater kit in the air handler, shouldn’t it be sized so that it can help up? I mean if it’s -40 outside, I can see maybe not keeping the entire floor heated efficiently but not -1/-7. Just my opinion. Maybe with the other elements not working or being told to operate, the thing just doesn’t have a chance to catch up. Just curious if the size unit I have is adequate enough in your opinion. Thanks again for your help. Not sure what we did and I don’t think it’s fixed but it’s better than it was. Keep this open if that’s ok with you and if you don’t hear back from me by Friday, close it out or shoot me a message. Thanks again. Stp
Customer reply replied 3 months ago
Sorry about the misplaced words. Spell check changed them for me lol
HVAC Technician: Gaztech, HVAC Technician replied 3 months ago

The heater kit used for your furnace is not identified on the furnace rating plate.

Hkr 21 being the bigest one available and think that is the one that should have been chosen.

As far as Heat pump its 400 sqFt/ ton as rule of thumb

Ask Your Own HVAC Question
HVAC Technician: Gaztech, HVAC Technician replied 3 months ago

I noticed question is still opened?

Did you resolve problem?

Best regards

Customer/p>
Ask Your Own HVAC Question
Was this answer helpful?
Ask Gaztech Your Own Question
Gaztech
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 803
803 Satisfied Customers
Experience: Owner at Gaztech

Gaztech is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
display backlite not working on honeywell thermostat #TH6220D.
display backlite not working on honeywell thermostat #TH6220D. can this be fixed?… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
My furnace (Rheem Classic 90 Plus) runs only if the panel is
My furnace (Rheem Classic 90 Plus) runs only if the panel is off. When the panel is replaced, the flame on the burners goes out and the system cycles every few minutes. when I re-set the system and op… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have a frigidaire furnace FG6RC 060C-12A that blows air,
i have a frigidaire furnace FG6RC 060C-12A that blows air, but no heat. the burners come on, but then shut off after a couple of minutes. Thermostat is good and a new filter was just installed within … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My 1 year old furnace refuses to operate. Both the red and
My 1 year old furnace refuses to operate. Both the red and green LEDs are on solid and the yellow LED flashes 3 times. No power to the thermostat. … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
My goodman furnace ignites and shuts off after a couple of
Hi, my goodman furnace ignites and shuts off after a couple of seconds (problably 3t o 5 seconds). … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
I have a Lennox G51MP gas furnace that will not operate
I have a Lennox G51MP gas furnace that will not operate properly on a 6800 Watt portable generator. I have a manual transfer switch and everything in my house including TV, computers, internet are run… read more
Gaztech
Gaztech
HVAC Technician
803 satisfied customers
I, I installed a furnace control Board part # 62-24084-82.
I, I installed a furnace control Board part # 62-24084-82. It cycled once and will will not cycle again. all the controls are ok after checking them. any Ideas? … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Xrv95 trane furnace. Power to unit, fuse ok, transformer ok,
xrv95 trane furnace. Power to unit, fuse ok, transformer ok, Circuit breaker ok. Power to furnace. Changed thermostat batteries. Problem is fan will not run even in on position. No heat. No codes, no … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I wanted to replace a T8112D Thermostat with an RTH 111B and
I wanted to replace a T8112D Thermostat with an RTH 111B and in removing the T8112D, I accidentally touched the red and white wires. The system went on. I relaced the thermostat and the Air Cond came … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
How can I tell I my York furnace control board is the cause
How can I tell I my York furnace control board is the cause of the furnace not completing the heat cycle. It shuts down and give me the pressure sensor/switch code but two tech's have been out and ver… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
This is the same guy with the Goodman furnace control board
Hi, this is the same guy with the Goodman furnace control board / transformer. My plumber said what caused the board to fail was a short in the blower motor from water from AC unit backing up into blo… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Goodman GMNTE120-5 It has a furnace/control board
I have a Goodman GMNTE120-5 It has a furnace/control board with this part number B1809925two of the wires have come off two connectors, and the wires are the same color - trying to determine if it mat… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I recently replaced my furnace control board. The furnace is
I recently replaced my furnace control board. The furnace is a Lennox G40-OUH and the control board was a White Rodgers 50-A65-121-07. The only replacement was a White Rodgers 50A65-843 Universal Boar… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have an amana furnace control board with an led flashing 3
I have an amana furnace control board with an led flashing 3 times … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I need help with my -Rodgers furnace control board 50e47-060
I need help with my White-Rodgers furnace control board 50e47-060 on a Trane furnace. It has a blinking red light. On the unit it says " steady red light- replace control, blinking red light-referred … read more
type2technician
type2technician
253 satisfied customers
I have a nordyne KG7TC-080D, with a furnace control board
I have a nordyne KG7TC-080D, with a furnace control board #624790/920916. this is a 2-stage upflow unit. Furnace ignites but goes out wihin seconds. flame sensor replaced, still the same issue. Has in… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I think that I may have a bad furnace control board. Trouble
Hello I think that I may have a bad furnace control board. Trouble shooting so far. Two different thermostats with the same behavior. Direct connection of the R&W&G wires make the furnace run continuo… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My furnace control board light is not coming on. Yes, the
My furnace control board light is not coming on. JA: Did you check the furnace's filters? Customer: Yes, the furnace filter is new. JA: Do you plan on doing the work yourself? Customer: Yes. JA: Anyth… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x