Customer Question
What does flashing yellow...

What does flashing yellow light in damper module mean?

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

Just bought the house, bryant system has been here for about 10 years

Contractor's Assistant: Do you plan on doing the work yourself?

Depends

Contractor's Assistant: Anything else we should know to help you best?

We installed a nest system today, blew a fuse, and now can't get heat to work. power is working with new fast, but yellow flashing light on the damper module

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Haven't looked at filters...will double check

Submitted: 6 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 12 minutes by:
1/7/2018
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, I need a photo of the zone damper box with the cover open that shows the yellow flashing light to coach you on a diagnosis... either there is no power to the damper, due to a bad thermostat or zone controller or the damper motor is bad.

.

Use the 'add files' link next to your send button to get the photo me, photo must be well focused and include ALL of the wire connections at the zone controller.

IF you do not have such a zone controller I need to know what the flashing yellow light is on, a photo will help.

.

My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today. If you need more assistance, please use the reply box and let me know.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
It is on a Bryant damper module.. we added nest thermostats and now furnace won’t kick on. The only thing we see is flashing 7x) on damper module
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago

Bryant makes a lot of different damper controls, tell me about how big that module is, if its larger than 10 inches square I need a photo of the inside of it showing all wire connections.

.

If the system worked however before you installed the NEST you have wired it incorrectly... tell me which color of wire attached to the old thermostat and the letters for each terminal. and the same for the NEST

We can go from there

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a model 340m340mav036080 furnace and it's not staying
hi I have a Bryant model 340m340mav036080 furnace and it's not staying on or giving much heat … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,942 satisfied customers
I'm getting an error on my Nest Thermostat, No Power to RH
I'm getting an error on my Nest Thermostat, No Power to RH wire, E24. The heat will not turn on and now the fan is running and I cannot shut it off. Wondering how to get it to shut off. … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
454 satisfied customers
My forced air heater has worked fine for 10 years, but this
My forced air heater has worked fine for 10 years, but this morning when I turned up the thermostat, the fan came on but no heat. I took off the front panel on the heater and saw a yellow flashing lig… read more
Phil
Phil
Mechanical Engineer
7,426 satisfied customers
Will a nest series 3 thermostat work with my evolution heat
will a nest series 3 thermostat work with my bryant evolution heat pump … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I bought a nest e Thermostat today and have trouble
I bought a nest e Thermostat today and have trouble installing it due to not knowing about if my system has heat pump and auxillary power... … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
454 satisfied customers
E24 reading on nest report system, at turned off main
e24 reading on nest report system, at turned off main breaker no heat … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have two Trane XE80's (side by side) in a new house I
I have two Trane XE80's (side by side) in a new house I moved into this summer. About two weeks ago, I opened them up to check the filters; all burners in both units were on. A couple days later, I ch… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Disconnected and reconnected honeywell basic thermostat (new
Disconnected and reconnected honeywell basic thermostat (new - 3 mo.) to do some drywall repair. On reconnect, "Cool" just flashes, LCD reads "In Recovery" and no air blows. Removed batteries, turned … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have Evolution thermostat that has a blank screen. The
I have Bryant Evolution thermostat that has a blank screen. The unit has been off for about a week. We had a power outage 2 days ago but I thought the thermostat still had power. I checked the A/c bre… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Need working asst on unit. I need to know what wires to put
I need to know what wires to put where just bought unit today from Costco … read more
Phil
Phil
Mechanical Engineer
7,426 satisfied customers
Yes. I have a Honeywell 8900 perfect climate comfort center
yes. I have a Honeywell 8900 perfect climate comfort center system. I want to put in a Nest thermostat. I've read quite a bit on this, it doesn't seem like it is 100% compatible due to things like the… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,019 satisfied customers
, I have a Bryant 90t with Zone Perfect Plus ZONEBB8KIT-.
Hi, I have a Bryant 90t with Zone Perfect Plus ZONEBB8KIT-B. I'm trying to remove my old thermostat and install a Nest. Is this even possible? The Nest error report I get it "e30". Any Help Appreciate… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I have a Trane XL80 that keeps blowing the 5A fuse on the circuit
I have a Trane XL80 that keeps blowing the 5A fuse on the circuit board. Changed to a Nest thermostat 3 weeks ago and it was working fine. Blew a couple of days ago and now consistently blows when I r… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My Bryant Zone Perfect Plus thermostat won't pump heat
I recently bought a house with a Bryant zone perfect plus thermostat. This is the first time I needed to use it and it won't pump heat. There are 2 zones. Both are programmed identically. The Therm is… read more
Phil
Phil
Mechanical Engineer
7,426 satisfied customers
Carrier Infinity System thermostat #SYSTXCCUIZ01-B has no LCD
Carrier Infinity System thermostat #SYSTXCCUIZ01-B has no LCD display and cannot be programmed.… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
we have a bryant 90i 355mav furnace the inducer motor starts
we have a bryant 90i 355mav furnace the inducer motor starts the igniter lights the burners gas comes on the burners light stays lit for about 1 min then the gas shuts off lights flash gren red then y… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
I tried installing a NEST thermostat but it says that my Rc
I tried installing a NEST thermostat but it says that my Rc wire had no power. So I tried putting my old thermostat back in and now I can't get that one to power up. I've checked the fuse box to see i… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
In 2008 we had a Bryant 286ANA048 2 speed 16 seer heat pump
In 2008 we had a Bryant 286ANA048 2 speed 16 seer heat pump installed and provides three zones in our home. Came home last night to error message on thermostate pad "System Malfunction Call Technican"… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x