My thermostat is blank and the breker is tripped at the

Customer Question
My thermostat is blank...

My thermostat is blank and the breker is tripped at the outside unit. I turned the breaker on and hooked the red and green wire from the thermostat together and the fan came on. When I was installing the green wire back to the thermostat ( red wire was not installed) the screen came back on intermittently. when I made the connection it was still blank. The breaker at the unit was not tripped.

Contractor's Assistant: Just to clarify, do you think this is a larger HVAC problem, or something specific to the thermostat?

I do not know.The screen went blank last night and the heat quit working.

Contractor's Assistant: Do you plan on doing the work yourself?

If I can. MY son is experienced in electrical work and he will help me.

Submitted: 6 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 5 minutes by:
1/7/2018
HVAC Technician: HVAC Guru, HVAC TECH replied 6 months ago
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,713
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified

One moment please..Note it takes time to type and add links so please be patient. Also the site will send you a phone call offer, that is not me.

Ask Your Own HVAC Question
HVAC Technician: HVAC Guru, HVAC TECH replied 6 months ago

Do you have a volt meter and can you test from the R to the C terminal at the thermostat for 24-27 volts AC?

Ask Your Own HVAC Question
Customer reply replied 6 months ago
I will have to find meter
HVAC Technician: HVAC Guru, HVAC TECH replied 6 months ago

OK check that and let me know what you find.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
I will have to find meter I will take a while if I can find it at all
Customer reply replied 6 months ago
I will have to find meter I will take a while if I can find it at all are you still there
Customer reply replied 6 months ago
Can I get a case number ***** get back to you. We are renovating and my tools are packed up
HVAC Technician: HVAC Guru, HVAC TECH replied 6 months ago

Yes I am online just post when you got it note I am helping other customers and there is a delay in responses just post here bookmark this URL

Ask Your Own HVAC Question
Customer reply replied 6 months ago
0 reading
HVAC Technician: HVAC Guru, HVAC TECH replied 6 months ago

What likely happened is the low voltage fuse in the furnace or airhandler blew. There typically is a SLOT STYLE 3-5AMP FUSE on the board itself inside the furnace/airhandler like this.

CLICK HERE

If that is burned out all power to the thermostat will be lost. 95% of all units use some sort of SLOT FUSE or inline BUS STYLE FUSE to protect the low voltage circuit. You need to find that and change it out. If you just bump two wires together you could have just popped it without even knowing it. Now if for some reason your unit does not use a fuse often the board will be damaged due to the short. You would need to confirm you have 24 volts to the board inside the furnace/airhandler with a volt meter to make sure though.

Note if you have a condensate pump check the float and make sure the pump is not full of water...as that could cut low voltage power to the unit as well if the pump is not working and full of water.

I hope that I have earned a 5 star rating. We are on the honor system here for payment and will receive nothing unless a rating is given. Please remember to use the RATING LINK ON YOUR PAGE by selecting a star at the top or bottom of the screen before you leave today. If you need anything else, just let me know. You can continue asking follow-up questions at no additional charge after rating my service if you still need assistance.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Is air handler revering to the outside unit or unit in the attic? Is there a fuse in the outside unit?
Customer reply replied 6 months ago
Is air handler reffering to the outside unit or unit in the attic? Is there a fuse in the outside unit?
HVAC Technician: HVAC Guru, HVAC TECH replied 6 months ago

No no fuse on the outside unit the one in the attic

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Thanks. Would that cause the breaker outside to trip? It smells like electrical wires burning when I open the outside panel.
HVAC Technician: HVAC Guru, HVAC TECH replied 6 months ago

It could if something is shorted

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Thanks. Would that cause the breaker outside to trip? It smells like electrical wires burning when I open the outside panel.
I have two units outside ( upstairs and downstairs). The upstairs is working. There are two breakers in the panel outside. Only one was tripped
Customer reply replied 6 months ago
I have two units outside ( upstairs and downstairs). The upstairs is working. There are two breakers in the panel outside. Only one was tripped. Is the air handler in the attic only hooked up to one unit or both?
HVAC Technician: HVAC Guru, HVAC TECH replied 6 months ago

It could be hooked to both or one it just depends on how it was wired. This sounds like you may need an electrician or HVAC tech onsite to see what has failed.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
If it is hooked to both, then could it still be the pump in the airhandler in the attic. The tray is dry. Do you think the failure is in the unit outside. if the short is in the outside unit, would that have caused the thermostat to go blank when the breaker tripped?
Customer reply replied 6 months ago
If it is hooked to both, then could it still be the pump in the airhandler in the attic. The tray is dry. Do you think the failure is in the unit outside. if the short is in the outside unit, would that have caused the thermostat to go blank when the breaker tripped?
Are you still there?
HVAC Technician: HVAC Guru, HVAC TECH replied 6 months ago

I would check the unit in the attic, but a short from the outside unit goes to the insie unit in the attic as well so it could have blown the fuse on the board in the attic unit. Check the board on the airhandler in the attic

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask HVAC Guru Your Own Question
HVAC Guru
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,713
18,713 Satisfied Customers
Experience: 20yrs in the HVAC industry with certificates and degrees.

HVAC Guru is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have the Honeywell RTH2410B thermostat and I have Blue,,
Second opinion] Hi I have the Honeywell RTH2410B thermostat and I have Blue, Green, Yellow and 1 red wire. Do I hook up all three of them? I did and my compressor is not turning on.… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Split air unit outside. Not working. Tech replaced a trip
Split air unit outside. Not working. Tech replaced a trip switch in the outside unit. He says my nest thermostat is bad because when it calls for cooling, only the fan comes on. All test on the nest a… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We have a Gibson Central Air unit: GB5BM-T25K-A-10. After
We have a Gibson Central Air unit: GB5BM-T25K-A-10. After not having it on all winter, I turned it on and nothing happened. I noticed the battery light flashing in the thermostat and so I replaced the… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
The power went out in my neighborhood an hour last night.
The power went out in my neighborhood for about an hour last night. When it came back on, my Lennox iComfort touchscreen thermostat did not reboot. It's just a blank screen.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I just installed a Honeywell RTH2410 thermostat and my system runs 2 or 3 minute
I just installed a Honeywell RTH2410 thermostat and my system runs for about 2 or 3 minutes and then trips the breaker. This happens for both cooling and heating. It is a gas furnace. Thanks for your … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We just installed this Honeywell CT87N and can only get hot
We just installed this Honeywell CT87N and can only get hot air. We installed the wires the exact way we pulled out of old one and now nothing works...??… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I am replacing a Robertshaw 9520 with a Honeywell RTHL3550.
I am replacing a Robertshaw 9520 with a Honeywell RTHL3550. We are pretty sure we have all the wires in the correct spots but the compressor is not coming on. The fan comes on and runs fine. This is a… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Replacing thermostat with RTH 6350. Old thermostat label was:
Replacing thermostat with RTH 6350. Old thermostat label was: W- blue/brown wire together O- orange G- Green R- Red C- white Y- yellow Here's how I have the new labeling: Aux/E- Blue/Brown together G-… read more
HVAC Guru
HVAC Guru
HVAC TECH
18,713 satisfied customers
We came home last night to find our air off and the thermostat
We came home last night to find our air off and the thermostat blank. Replaced the batteries and the air won't turn on at all. The thermostat clicks as though it is trying to turn the ac on, but nothi… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We have a Robertshaw 9520 thermostat. Got home work today
We have a Robertshaw 9520 thermostat. Got home work today and the house was cold. I checked and the thermostat was blank. It's the kind with no batteries so just to see if it the heat pump was working… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Carrier central AC system with Inifnity thermostat.
I have a Carrier central AC system with Inifnity thermostat. The thermostat screen went dark overnight and the AC is off. Pressing the "Off" button doesn't bring it back on. I don't see any breakers t… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
Yesterday I went and bought a hunter programmable thermostat,
Yesterday I went and bought a hunter programmable thermostat, model #44377. When I left to get it my daughters boyfriend thought he would be useful and disconnected the old thermostat. Now I'm not rea… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
we have a honeywell T8411R 1002 (2) thermostat and we tried
we have a honeywell T8411R 1002 (2) thermostat and we tried to turn on the heat but it would not turn on. when we first looked at the thermostat it was blank, we pulled it out from it's housing and pl… read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
my husband just installed a new Honeywell thermostat. It is
my husband just installed a new Honeywell thermostat. It is working but the fan will not turn off. What to do? Can you help??… read more
Douglas
Douglas
Vocational, Technical or Trade Scho
3,087 satisfied customers
We woke up this morning and the thermostat was blank. I tried
We woke up this morning and the thermostat was blank. I tried reseting the thermostat several time until the display came up. The heat will not come on. I thought it was the thermostat so I went and b… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,349 satisfied customers
I am having a problem with my heat pump AC. The digital thermostat
I am having a problem with my heat pump AC. The digital thermostat went blank. I found a cut in the line running between the inside and outside unit. When I spliced it the thermostat would come on for… read more
ComfortZone
ComfortZone
Associate Degree
515 satisfied customers
when i came home last night my thermostat went blank and the
when i came home last night my thermostat went blank and the air stop working. I checked all the breakers and pulled the front off of my inside furnace. I found the E (purple) fuse was blown. I change… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Furnace working fine.........had a 75 Degree yesterday went
Furnace working fine.........had a 75 Degree yesterday went to thermostat and changed to cooling Digital Thermostat clicked twice as it does when changing over Thermostat went blank........Can't figur… read more
Robert
Robert
Associate Degree
161 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x