I'm having a issue with my boiler. I get heat on the bottom…

Customer Question
Hi I'm having a...

Hi I'm having a issue with my boiler. I get heat on the bottom floor but can't get heat upstairs. I changed the thermostat for the upstairs and the pump for the upstairs zone but the pipe from the boiler with the faucet on it is still cold, while the 1st level zone pipe is hot. Every pipe off the boiler is hot except the pipe going to the 2nd floor

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

I double cked triple cked the thermostat settings. And I didn't know there were filters. Are u talking about the main boiler filter??

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

Yes this all started when I had no heat in the whole house. Cuz both the upstairs and down stairs thermostats would click on even if I turned them right to 80 degrees, that's when I bout new ones. The new ones clicked on but still minimal heat so I found at the boiler one of the pump motors wasn't working so changed it. Now I get heat on the 1st floor but the 2nd floor is speratic. It will work and then not work.

Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 minute by:
1/6/2018
HVAC Technician: Rick, HVAC Supervisor replied 8 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,850
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. First I’ll need some more info so I have a more complete picture of your situation.

Did you purge the air out of the system after you replaced the pump?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
By opening the faucet valves ? If so yes
HVAC Technician: Rick, HVAC Supervisor replied 8 months ago

It's a lot more involved than that. I suspect you have air in the zone and it's stopping circulation. If you can post pics of the piping around the boiler I can walk you through how to properly purge the system on a phone call

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
How do I reset or insure that an 1f80 361 for hydronic heat
How do I reset or insure that an 1f80 361 for hydronic heat is set correctly? … read more
Rick
Rick
HVAC Supervisor
24,850 satisfied customers
I set my central ac on 75. The basement is freezing cold.
I set my central ac on 75. The basement is freezing cold. The 1st floor is 75. The 2nd floor is 84. Seems like wasted cold air in basement and too hot upstairs. Only 1200 sq ft house.… read more
Ricky Main
Ricky Main
8 satisfied customers
I have heat down stairs but not upstairs. Baseboard heat
Baseboard heat from a boiler in the basement. Checked the thermostats. I even replaced the one upstairs. … read more
Rick
Rick
HVAC Supervisor
24,850 satisfied customers
The heat is ON on the 2nd floor zone, but the temperature
The heat is ON on the 2nd floor zone, but the temperature doesn't go up... Went to the boiler - it's hot alright, but the pump isn't working. The switch for the 2nd floor zone is in ON position. To ma… read more
Rick
Rick
HVAC Supervisor
24,850 satisfied customers
I have a Weil-McLain wm97+ running on propane. Needed to add
I have a Weil-McLain wm97+ running on propane. Needed to add a 2nd (Taco 0010-F3 Single Phase Circulating Pump 00 Series) circulator for 2nd floor. Water was not traveling up stairs efficiently. Just … read more
Rick
Rick
HVAC Supervisor
24,850 satisfied customers
I have a 3400 ft cape . 900 sqft 2nd floor, 1250'sqft 1st
I have a 3400 ft cape cod. 900 sqft 2nd floor, 1250'sqft 1st floor and 1250'sqft basement. Furnace is Carrier 2 cycle 100000 btu (old furnace just went out 80000 btu) with central air. Plus adding an … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Hope someone can help....have a 2 zone heating system....2
Hope someone can help....have a 2 zone heating system....2 taco 007 circulating pumps sit atop the boiler with a taco 220 flowcheck valve connected atop each pump. right pump circulates water to 2nd f… read more
Rick
Rick
HVAC Supervisor
24,850 satisfied customers
i have a 1988 gas boiler,it heats 3 floors. not getting heat
i have a 1988 gas boiler,it heats 3 floors. not getting heat on 2nd floor, what could be the problem be.susan… read more
Rick
Rick
HVAC Supervisor
24,850 satisfied customers
my heat stop wrking on the first floor of my house. i have
my heat stop wrking on the first floor of my house. i have base board heating and the second floor works great. my circular pump is hot on both ends of the pipes coming out of it. i replaced the therm… read more
Rick
Rick
HVAC Supervisor
24,850 satisfied customers
Weil-mclain hot water heater system, thermostat is downstairs,
Weil-mclain hot water heater system, thermostat is downstairs, do not get much heat upstairs in bedrooms?… read more
Rick
Rick
HVAC Supervisor
24,850 satisfied customers
I have 3 zone heat(boiler gas) with a thermostat in the basement,
I have 3 zone heat(boiler gas) with a thermostat in the basement, 1st floor and 2nd floor. I noticed yesterday that my 2nd floor was freezing and I had the thermostat on the normal 68 degrees. There i… read more
Rick
Rick
HVAC Supervisor
24,850 satisfied customers
I have a HZ311 truzone panel and (trolatemp Automatic dampers
I have a HZ311 truzone panel and (trolatemp Automatic dampers opposed dampers) 3 dampers attached the upstairs zone gets all the heat in the middle of the night and the 1st floor zone is cold.Thermost… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Hi Tim, A new question based on the previous one. You have
Hi Tim, A new question based on the previous one. You have fully answered the question of how to wire the honeywell h365 humidifer into a system comprising the first company air handler and hai omnist… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have baseboard heat. I have 3 zones (basement/main floor/2nd
I have baseboard heat. I have 3 zones (basement/main floor/2nd floor). I currently have basement heat set to 65 and main floor turned off as well as 2nd floor. I am still getting heat on the 2nd floor… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We have an oil heater and we have heat downstairs but the baseboars
We have an oil heater and we have heat downstairs but the baseboars heat upstairs when turned on does not warm up...I hear no water being pushed through the pipes like I normally do when the heat is t… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I live on the 2nd floor of a 2 story with a basement. We have
I live on the 2nd floor of a 2 story with a basement. We have a hot water heating system with radiators, one furnance( in the basement) supplies heat to the entire building. I have the thermostat cont… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Why am I getting heat only downstairs but not upstairs?
I have a 2 zone (upstairs & downstairs) hot water base board heating system. The boiler is working and I am getting heat downstairs but no heat upstairs?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Basement boiler heats water. Baseboards are not getting it
Basement boiler provides hot water. Circulation pump is running and I can hear water flowing in the pipe when it's on. Pump pipe very hot up to T which divides hot water between two zones. 1st floor a… read more
Ken Anderson III
Ken Anderson III
Vocational, Technical or Trade Scho
14 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x