When I switched my heat pump unit form the AC to the heat…

Customer Question
When I switched my...

When I switched my heat pump unit form the AC to the heat mode the breaker tripped off line. I replaced the start and rum compressor capacitors also noticed the the starting relay was burned and pitted so replaced that. I am still getting high current that is triping the breaker . Is this an indication of a bad starting winding in the compressor or has something gone wrong with the unit when I went from cool to heat mode

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

I have heat running through the restistive coils in the indoor unit that is running ok the temp is set at 70 and the filters are good. it is the condenser unit outside that is tripping off line . Note they are on serperate breakers

Contractor's Assistant: Do you plan on doing the work yourself?

I want to check what is causing the high current flow. and see what I can do. If the comressor is bad I will get me tech here they are all very busy because of the cold here in Florida. What to be able to identify what is wrong

Contractor's Assistant: Anything else we should know to help you best?

What is the best way to check the comprssor windings are the issue

Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 days by:
1/8/2018
HVAC Technician: airheatman, HVAC Technician replied 8 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,545
Experience: Furnace, A/C and heat pump specialist.
Verified

If compressor operates in cool mode, the compressor is not the issue. Will it still come on and run without tripping breaker in cool mode? Also what is model on outdoor unit?

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a 2hp13l30p-18 heat pump high amps on heat cycle and
I have a 2hp13l30p-18 heat pump high amps on heat cycle and trips breaker on cool runs at 12 amps and no problems. serial# ***** ***** unit is about 8 years old. filter is new and a coil is clean as i… read more
airheatman
airheatman
HVAC Technician
9,545 satisfied customers
I have lennox 13hpd-048-2301-1 . Intermittent problem. It cools
I have lennox 13hpd-048-2301-1 . Intermittent problem. It cools fine when working then it will stay running (fan and compressor) and no cooling. Later it will work fine again. It works ok in heat mode… read more
airheatman
airheatman
HVAC Technician
9,545 satisfied customers
RHEEM HVAC HEAT PUMP RUNS PERFECTLY IN AC MODE (BLOWS 40 DEG
RHEEM HVAC HEAT PUMP RUNS PERFECTLY IN AC MODE (BLOWS 40 DEG AIR) & EMERGENCY HEAT MODE (BLOWS 130 DEG AIR). WHEN PUT INTO 1ST STAGE HEAT PUMP POSITION, STARTS TO RUN, INSIDE COILS GET HOT OUTSIDE COM… read more
mranswer
mranswer
TECHNICIAN
Bachelor's Degree
481 satisfied customers
I have a rheem classic plus air handler and a heat pump outside.
I have a rheem classic plus air handler and a heat pump outside. Our local ac guy rewired some stuff during the winter for the heater, and now the ac just trips the breaker when it starts up. I am pre… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
My American standard heat pump ,in cooling mode only, will
My American standard heat pump ,in cooling mode only, will trip the breaker when the compressor try's to startup. This only happens when the outside temp is quite warm, ie,80 and above. Reset the brea… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I was working on a walk-in freezer and notice the breaker is
I was working on a walk-in freezer and notice the breaker is tripping even though the breaker amp is enough for the unit. I check the start and run capacitor and they check out O.K. I also check the s… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Ive got an carrier 38tg model air cooled condensing unit,
Ive got an carrier 38tg model air cooled condensing unit, have full 220 power to the unit. but on the control wiring im get 20 volts on the blue wire and no volts on the brown wire. any sugg. unit is … read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
TRANE XB13 R22 HEAT PUMP (SPLIT SYSTEM) COOLING MODE
TRANE XB13 R22 HEAT PUMP (SPLIT SYSTEM) COOLING MODE LOW SIDE = 66 PSIG HIGH SIDE = 148 PSIG, LINE TEMP 75 AMBIENT TEMP = 70 COMPRESSOR PULLING 7 AMPS HEATING MODE* LOW SIDE = 0VER 120 PSIG (OUT OF GA… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Heat pump is not cutting on. The AC is working fine. The heat
Heat pump is not cutting on. The AC is working fine. The heat pump clicks on for about one half a second then trips the breaker. The back up heat is heat coils.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
why is my evaporator icing up on my heat pump unit,fan is indoor
why is my evaporator icing up on my heat pump unit,fan is indoor fan is operating operating pressures 50psig & 220 psig high side abient temp.80 degrees f.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Lennox 10ACC-036-230-02 that is tripping the 30AMP
I have a Lennox 10ACC-036-230-02 that is tripping the 30AMP circuit. I have replaced the capacitor and the molded plug to the compressor. When i dosconnect the compressor the fan will run just fine. A… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
My Air conditioner compressor will turn on and after about
My Air conditioner compressor will turn on and after about 30 seconds trips the breaker. I dont think the blower is kicking on. Help.… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Ive had my Payne Ac Unit for five years. Recently Ive had
I've had my Payne Ac Unit for five years. Recently I've had issues with it blowing the breaker on start up? We replaced the breaker but it continues to trip - we also replaced the capacitor thinking t… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
goodman gpg13360901a compressor wont engage capasitor is good.have
goodman gpg13360901a compressor wont engage capasitor is good.have 240 between black and red and between black and yellow but not between red and yellow can you help?… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Ducane 2HP13L30P-1A, SN 4606A21730 - outdoor unit is not running.
Ducane 2HP13L30P-1A, SN 4606A21730 - outdoor unit is not running. No fan, no compressor. Green LED is on. AC power is OK. Indoor unit is functioning (heating, fan) OK. Air Filter is new. Air flow to r… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
3 ton Rheem heat pump, R22, manuf. date 1997 Customer complaint
3 ton Rheem heat pump, R22, manuf. date 1997 Customer complaint: Only getting heat from heat-strips as condenser unit will not run in heat-mode. When we (my assistant brother, Ernie) and I arrived thi… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
my trane xb12 unit keeps tripping the breaker. it has acted
my trane xb12 unit keeps tripping the breaker. it has acted very strange for about 2 months and my power bill has jumped almost 70%. I an currently using it ti heat my house and the aux light on the c… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My package unit in my renter house is not working, it keeps
My package unit in my renter house is not working, it keeps triping the breaker every time its turned on. It will try to come on and it kicks the breaker. I think the compressors is bad i checked the … read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x