HVAC

Have HVAC questions? Ask an HVAC Expert for answers

Ask an Expert,
Get an Answer ASAP!

What is fault code "AIR PR SW/HEX TEMP SW. Just serviced…

Customer Question
What is fault code...

What is fault code "AIR PR SW/HEX TEMP SW

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Yes okay just serviced last month

Contractor's Assistant: Do you plan on doing the work yourself?

Yes yes

Contractor's Assistant: Anything else we should know to help you best?

No just tell me the what that LOCKOUT fault code means or i can look it up in the manual

Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 21 minutes by:
1/6/2018
HVAC Technician: David Bowden, General Contractor replied 7 months ago
David Bowden
David Bowden, General Contractor
Category: HVAC
Satisfied Customers: 1,307
Experience: Owner at Floridaco
Verified

T​he fault code is for " Air pressure switch/ heat exchanger temperature switch" Basically the pressure switches are probably open and not allowing the system to operate due to design safety features. Most likely you will need to have the unit serviced and diagnosed as it may be something fairly simple, however it could be more involved. You might look around for the little reset button on the sensors and see if they tripped, resetting them may resolve the problem however if they trip again you need to get the unit serviced.

Ask Your Own HVAC Question
HVAC Technician: David Bowden, General Contractor replied 7 months ago

Greetings… Just following up to see if you were still needing some help answering your question?

Thanks,

Dave

Ask Your Own HVAC Question
HVAC Technician: David Bowden, General Contractor replied 7 months ago

I was reviewing my open questions list and noticed this one has not been answered or replied to. Did you still need help with it or should it go back to customer service for proper processing?

Ask Your Own HVAC Question
HVAC Technician: David Bowden, General Contractor replied 7 months ago

As of this posting I have not been able to locate any additional information on this specific issue, and since I have not received any reply or feedback from the recommendations I mentioned above, I trust they have been helpful in resolving this problem. However, if you are still needing additional assistance, please let me know by using the reply box below, otherwise I will proceed in closing out this question.

Thank you,

Dave

Ask Your Own HVAC Question
HVAC Technician: David Bowden, General Contractor replied 6 months ago

Hello... I would very much appreciate if you can take a few moments and reply to this email and let me know if you still require assistance, or should I proceed forward to closing out this question since it has been open for so long.

Thank you,

Dave

Ask Your Own HVAC Question
HVAC Technician: David Bowden, General Contractor replied 6 months ago

Hello... As part of our continuous follow up procedures, every open question requires it to be closed out once it has gone past a reasonable time, and that the expert has provided an answer that should have helped resolve your question. This can be done simply by completing the 5 Star Rating once it appears. If you still require assistance or have additional questions, you can let the expert know by replying to this posting that you still need their advice and recommendations.

Thank you,

Dave

Ask Your Own HVAC Question
HVAC Technician: David Bowden, General Contractor replied 5 months ago

Hello, I was reviewing my open questions and noticed this one has not been replied too, however I did respond with an answer back on January 05, 2018 and therefore I am wondering if that has resolved the problem you were experiencing. I would greatly appreciate a reply email, so I can complete this open question, or just let me know if you need further assistance, and I can continue to look for another solution.

Ask Your Own HVAC Question
HVAC Technician: David Bowden, General Contractor replied 5 months ago

Your assistance is needed... A​s of today this question is over 60 days old and based on the nature of the problem along with the recommendation that were provided, I would like for us to close out this question, however to do that it requires a rating by you as explained below.

Please note that the rating is only based on the experts attempt to resolve the problem. If you feel a credit or refund is applicable, please contact customer service directly as the experts are not authorized to handle these matters.

One of the goals here at Just Answer, is to provide each customer with the best experience possible and for the experts to earn a 5 Star Rating based on their responses, recommendations, and professionalism, when answering questions. If I have achieved that goal for this question, please take a few moments to rate my service and select the 5 Stars before logging out.

​Thank you very much for your assistance with this, I sincerely ***** *****

Dave

Ask Your Own HVAC Question
HVAC Technician: David Bowden, General Contractor replied 4 months ago

Hello... As part of our continuous follow up procedures, every open question requires it to be closed out once it has gone past a reasonable time, and that the expert has provided an answer that should have helped resolve your question. This can be done simply by completing the 5 Star Rating once it appears. If you still require assistance or have additional questions, you can let the expert know by replying to this posting that you still need their advice and recommendations.

Thank you,

Dave

Ask Your Own HVAC Question
HVAC Technician: David Bowden, General Contractor replied 3 months ago

Greetings...

I was reviewing my open questions and noticed this one has not been rated yet. If you could take a couple of moments and complete the 5 Star Rating which will close out the question I would appreciate it.

Thanks,

Dave

Ask Your Own HVAC Question
HVAC Technician: David Bowden, General Contractor replied 2 months ago

I do apologize for these continuing follow-up messages, however since this question remains open and will only close out once the rating portion has been completed by you. Please assist me by taking a few moments to fulfill the rating requirement and this will satisfy the system.

Thank you so much, I sincerely ***** *****

Best,

Dave

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask David Bowden Your Own Question
David Bowden
David Bowden
David Bowden, General Contractor
Category: HVAC
Satisfied Customers: 1,307
1,307 Satisfied Customers
Experience: Owner at Floridaco

David Bowden is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have an older trane, TDD080C936B0 and got an OPEN HIGH
I have an older trane, TDD080C936B0 and got an OPEN HIGH TEMP LIMIT SW fault. I replaced the sw that is on the front of the unit behind the gas valve. When I cycled power I got the same error code. I … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We have a LOCHINVAR Knight, hot water heater. Service manual
We have a LOCHINVAR Knight, hot water heater. Service manual says WH-55-399. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My central air system is currently working but over the last
my central air system is currently working but over the last several days we have been getting a "Systems Error" message on the thermostat and being locked out for 4hrs … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Trane ComfortLink II, XL 20i unit. I have an error 126 -
Hi. Trane ComfortLink II, XL 20i unit. I have an error 126 - tried cutting power to inside and outside for 5 minutes, it didn't fix. … read more
Webb-Guy
Webb-Guy
Maitenance Supervisor
Associate Degree
3,330 satisfied customers
I have a Honeywell programmable thermostat. In the morning
I have a Honeywell programmable thermostat. In the morning when the temp is programmed to change the setting from 62 to 68 the furnace comes on but then aborts at about 66 degrees. I have to turn the … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Raypack 2100 digital spa/ pool heater. We had a big
I have a Raypack 2100 digital spa/ pool heater. We had a big lightening strike right outside the door and the heater has not worked since. It is showing a code of PR 6. Not sure that is a code but it … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
My Trane xr90 intermittently flashes code 4 (open limit sw)
My Trane xr90 intermittently flashes code 4 (open limit sw) upon call for heat. checked in and out voltage safety circut 25.6v out 25.2 return while flashing 4 board shuts down and then restarts proce… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have an Amana GUI115B35B with a White Rogers ignition module
I have an Amana GUI115B35B with a White Rogers ignition module #50E47-170. with a flashing status lite. What does the code mean. After resetting, unit will cycle normally.… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Hi there. I have a fujitsu air conditioner duct type/art series,
Hi there. I have a fujitsu air conditioner duct type/art series, part no(NNN) NNN-NNNN Our system is less then a year old. We haven't turned on our system for about a month and when we turned it on to… read more
servtech50
servtech50
HVAC/R service tech
216 satisfied customers
We have a Munchkin boiler Model 140MHAR1 Can a surge of power
We have a Munchkin boiler Model 140MHAR1 Can a surge of power effect the comter panel? If so what steps are necessary to reset? Jim… read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
My Bryant furnace is not putting out warm air. I just went
My Bryant furnace is not putting out warm air. I just went and looked at the RED LED status light and it was blinking. After removing both panels and then replacing the top panel, the light remained o… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We put in our Carrier high-efficiency furnace last fall since
We put in our Carrier high-efficiency furnace last fall since then we've had a lot of error msgs, and the alert (since last dec 2009) saying "system malfunction, contact technition" on our infinity th… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Goodman Furnace, 80% efficiency; its about 6 years
I have a Goodman Furnace, 80% efficiency; it's about 6 years old. About once a day for the last several weeks, my digital thermostat will call for heat (Honeywell-it will click and say "Heat On" and n… read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
I have a Ducane Gas heater - about 10 Years old. The model
I have a Ducane Gas heater - about 10 Years old. The model number is XXXXX We used programmable Thermostat (Honeywell). Currently, the heater is signal error code as follow : 4 flash stop for 2 second… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a Trane XL80 that is blowing out cold air, the error
I have a Trane XL80 that is blowing out cold air, the error code (2 short flashes) says "External Lockout (Retries or Recycles exceeded)" What does this mean?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Model UPNE-036JAZ SER 7348 M1506 05913 Code is flashing low
Model UPNE-036JAZ SER 7348 M1506 05913 Code is flashing low pressure lockout. checked all pressures. okay. bypassed low pressure switch. still nothing… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Worcester Bosch 28i junior boiler. Starts up every
I have a Worcester Bosch 28i junior boiler. Starts up every morning and after 10 mins it cuts out. Red light flashes every second. Press reset and boiler relights. Have to run boiler at 50% output as … read more
Dan Linger
Dan Linger
Lead Technician / Energy Consultant
Bachelor's Degree
62 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question