I farted and now my gas furnace wont run

Contractor's Assistant: Did you double-check the thermostat? And what about the pilot light?

My friend has a miller propane furnace and the burner is not coming on.The inducer motor comes on,it has a brand new thermocouple.white rogers gas valve.

Contractor's Assistant: Do you plan on doing the work yourself?

Yes I am I`m very good at oil boilers and furnaces but the propane side of it I need a little help.

Contractor's Assistant: Anything else we should know to help you best?

This furnace has a standing pilot which of course is lite,The inducer motor is coming on first,the thermostat is turned up but no ignition.

Submitted: 6 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 5 minutes by:
1/5/2018
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello.

So far it sounds like water in the pressure switch tubing if it has one.

Take close up, exceedingly well focused photo's of the wiring diagram glued inside the furnace/air handler door, and the printed circuit board mounted on the blower, , that shows where the thermostat wires connect, and I will mark them up with trouble shooting instructions.

Use the 'add files' link next to your send button to get the photo(s) to me.

.

We can go from there with training, coaching and diagnosis.... without a time limit, In depth with as much detail as needed .

.

When we finally get the situation solved, please select the 'finish and rate your expert link' near the top of your page and click on it.

.
My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today. If you need more assistance, please use the reply box and let me know.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
It's an older propane furnace and it doesn't have a pressure switch on it.
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago

Thanks, ***** ***** why asked for the wiring diagram. it will show me what you have, and I can mark it up with testing instructions, step by step.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
I'm not at the location of where the furnace is so I will get the wiring diagram and get back to you thanks.
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago

.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Nordyne furnace in my manufacture home that will not
i have a Nordyne furnace in my manufacture home that will not fire. It has a standing pilot that stays lite and i got 24 volts at the gas valve that has a slight buzzing noise until i pull one of the … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
The problem is after replace the control board, I jump R and
the problem is after replace the control board, I jump R and W, still nothing happen, the inducer blower should run… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Furnace will start up as normal, (inducer blows, burners light,
Furnace will start up as normal, (inducer blows, burners light, heat comes out of vents) it will run for about 3 mins then shut down (burner stops, no heat/air coming from vents) and the blower contin… read more
theplumber717
theplumber717
Plumber
Vocational, Technical or Trade Scho
791 satisfied customers
I have a Heil furnace which is approximately three years old
I have a Heil furnace which is approximately three years old (EDD2X30FA2). Before the blower kicks in and the burners are heating up the furnace makes a noise like the fan needs oiling except that the… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
having trouble lighting pilot. not staying lit after turning
having trouble lighting pilot. not staying lit after turning to on.was natural gas and now converted to lp.same problem as before. i think control valve has a piece of dirt in it.sometimes when lever … read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
Tempstar gas furnace Model 867.815014 (outside furnace on slab)
Tempstar gas furnace ModelNNN-NN-NNNN(outside furnace on slab) Heat will not kick on. I have electric current going to the unit. Tried A/C and heat - neither will come on. No blower no burner.… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have a honeywell gas furnace and our power went out last
I have a honeywell gas furnace and our power went out last night. When we awoke, the furnace was off. We got it running again, but the burners won't ignite. Is it broken or is there something we need … read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have a Holland coal burner converted into a natural gas furnace
I have a Holland coal burner converted into a natural gas furnace ... it has a small motor connected to a single fuse box to start it .... on the motor there is a metal tag instructing you to oil once… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
i dial in the temperature on my thermostat and the blower does
i dial in the temperature on my thermostat and the blower does not respond. the fan comes on and theres nothing igniting in the fire box. what could bo the problem?… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
i have a model gck100d20-3a and the small blower kick on but
i have a model gck100d20-3a and the small blower kick on but the pilot wont lite or the gas valve to the pilot will not open… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
my boiler wont stay heating I tried changing the thermo coupler
my boiler wont stay heating I tried changing the thermo coupler and thermostat what else could i try… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
MY lennox central air/heater will not lite the gas the gas
MY lennox central air/heater will not lite the gas the gas is on the thurmo is set but it just buzzes and then the fan starts… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have a miller furnace in a mobile home with an auto iigniter.
I have a miller furnace in a mobile home with an auto iigniter. It stopped working, I replaced the thermacouple and that doesnt seem to do it, so what is my next step Sam… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
We have a Miller model # M1S-066, oil burner series AF10. The
We have a Miller model # XXXXX oil burner series AF10. The points and the nozel are cleaned and we get the pilot lit and then we hit the reset. It gets up to temp than The pilot light goes out . How c… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
hi, just been to a baxi solo pf 3 boiler. the problem is that
hi, just been to a baxi solo pf 3 boiler. the problem is that the boiler is calling so it starts up for a second or so and then cuts out for a second and then starts again for a second then cuts out f… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,349 satisfied customers
My furnace is just blowing cold air and I think its the pilot
My furnace is just blowing cold air and I think its the pilot light. The pilot light is eletronic. Is there anyway I can light it manually?… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
I own a Tempstar Ultra High Efficiency furnace model NTGM 100
I own a Tempstar Ultra High Efficiency furnace model NTGM 100 EHA3. Intermmitently main burner will go out,followed by blower motor,shortly after,although thermostat is still calling for heat.Attempts… read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
my pilot light goes on and wont kick on the boiler. then the
my pilot light goes on and wont kick on the boiler. then the pilot light goes off after 30 seconds… read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x