The yellow light on my Rheem classic 90 plus is out and

Customer Question
The yellow light on...

The yellow light on my Rheem classic 90 plus is out and furnace isn't turning on

Contractor's Assistant: Did you check the furnace's filters?

The regular air filter? What do I need to check with that?

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

I think the flame is out

Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 minute by:
1/5/2018
HVAC Technician: airheatman, HVAC Technician replied 7 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,352
Experience: Furnace, A/C and heat pump specialist.
Verified

Tell me about the middle (OK) gren.Is it flashing? If so count blinks between pauses

Ask Your Own HVAC Question
Customer reply replied 7 months ago
It is flashing and there are 2 blinks between pauses
HVAC Technician: airheatman, HVAC Technician replied 7 months ago

THanks for this information. The 2 blink code indicates a problem with the pressure switch.The small vent inducer has to come on and stay on pulling and holding a vacuum on the pressure switch in order for furnace to operate.
Troubleshooting the cause can be time consuming and may require us to have a volt meter for testing voltage and continuity as well as a manometer to check vacuum on the switch.Without these we are limited to what we can check.

Below are the most common reasons for the error

1.Blocked intake or exhaust vent(This can be a small as a spider web or dirt dauber in vent)

2.Blocked condensate drain (No water should e standing any drain hoses)

3.Loose,restricted or cracked hose from inducer fan ti pressure switch ( Visual inspection will verify if hse is cracked or loose. Hose can be removed and fittings cleaned with a straightened paper clip)

4.Bad pressure switch (we would need a meter and manometer to test)

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 7 months ago

Lets start by verifying that the vent motor is coming on when you call for heat

Ask Your Own HVAC Question
Customer reply replied 7 months ago
How do you check that the vent motor is coming on? It shows on my thermostat that the furnace is on but I don't hear anything from the furnace.
HVAC Technician: airheatman, HVAC Technician replied 7 months ago

Turn thermostat off. Then power off to furnace and then back on.THat will reset board. The call for heat at thermostat and remove panel on furnace .Look and listen to see if the small vent motor comes on.

https://i.imgur.com/xmXZlNf.png

Ask Your Own HVAC Question
Customer reply replied 7 months ago
I didn't hear any motor come back on. And the light didn't start blinking right away. Took about 3 minutes for them to start blinking
HVAC Technician: airheatman, HVAC Technician replied 7 months ago

OK that little motor where vent connects HAS to come on first to close the pressure switch.

Problem is going to be one of 2 things:
1.Motor is stuck or burned up

2.Board is not sending power to little motor.

Can you try to spin the little fan blade using a small screwdriver to see if it will turn? And do you have a volt meter to see if we get power to the little motor?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
I'm not sure which fan blade I'm supposed to spin. Is it in the top panel and part of the black blower?I do not have a volt meter
HVAC Technician: airheatman, HVAC Technician replied 7 months ago

Yes remove top panel and take me a pic and attach here using add file button I will point it out.

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 7 months ago

THanks. Now it appears you can not access the blade on yours to try to spin.

From here,We would need a meter to troubleshoot. If you have a meter let me know .If not you can get an inexpensive one at Walmart for about 15 bucks if you would like to troubleshoot and I would be happy to guide you.

http://www.walmart.com/ip/Innova-3300-Equus-3300-Hands-free-Digital-Multimeter/14644665

AS stated either this motor is bad or it is not getting power

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,352
9,352 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a rheem classic 90 plus that has no heat, no fan
I have a rheem classic 90 plus that has no heat, no fan blowing for heat or air. The diagnostic leds are as follows flame=not lit, the next one=constant green, the next one=constant green. I have chan… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Same unit rheem classic 90 plus. When I restart the furnace
Same unit rheem classic 90 plus. When I restart the furnace it goes thru start up fine including the ignition but when the blower kicks in the flame goes out and the ok light blinks.… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
I have a Rheem Classic Plus Super Quiet 80 two -stage furnace.
I have a Rheem Classic Plus Super Quiet 80 two -stage furnace. It blows out cold air 90% of the time. I cut it off for 30 minutes and it worked for one heating cycle then back to cold air. I opened th… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hi, I have a Rheem 90 Classic Plus furnace. I am not seeing
Hi, I have a Rheem 90 Classic Plus furnace. I am not seeing any ignition, partial or temporary, when I turn on heat. Blower turns on, and at times will remain on for an extended period of time blowing… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Hi, I have a Rheem classic 90 Plus furnace which is not turning
Hi, I have a Rheem classic 90 Plus furnace which is not turning on to blow air and has 2 red indicator lights #6 and #8 blinking. What may I do about the problem since we would like to use our AC. Kat… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
What is the best way to clean the permanent air filter(s) on
What is the best way to clean the permanent air filter(s) on a Rheem Classic 90 Plus furnace? On my updraft model there are two small woven steel mesh filters in the same enclosure that houses the ele… read more
Wvfan79
Wvfan79
Mecanical Designer & Estimator
High School or GED
775 satisfied customers
Rheem Classic 90 Plus Furnace Blower kicks on. Burner is
Rheem Classic 90 Plus Furnace Blower kicks on. Burner is ignited. Runs for a minute then kicks off. Blower kicks back on but flame on burner is no longer appearing. Turn it off then on again. I have a… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Rheem classic 90 plus model number RGRA 09EZAJS, igniter
I have a Rheem classic 90 plus model number RGRA 09EZAJS, igniter isnt lighting and the OK led blinks 3 times, whats going on?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Rheem Classic Series 90 Plus 95% AFUE Upflow Gas Furnace
Rheem Classic® Series 90 Plus® 95% AFUE Upflow Gas Furnace will not fire. Power LED is ON OK LED blinks 5Xs FLAME LED is out This is the first time this unit is being started.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We have a rheem classic 90 plus. AC stopped working last night
We have a rheem classic 90 plus. AC stopped working last night - getting an error code on unit that reads "supply air sensor out of range". What does this mean?… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
My Rheem AC sounds like it is working but no air is coming
My Rheem AC sounds like it is working but no air is coming out of the vents. any suggestions?… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
We have a Rheem Classic 90 Plus, model RCBA 3765GGZ1XI. There
We have a Rheem Classic 90 Plus, model RCBA 3765GGZ1XI. There is a green light on, the air is coming through the vents, it sounds like it's on, but only cold air is coming out. It's getting colder and… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My Rheem classic 90 Plus wont ignite. Both LED lights are
My Rheem classic 90 Plus won't ignite. Both LED lights are solid green and there is not water backed up in the drain lines. The clear one shows condensation and the black one coming from the vent pipe… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
i have a rheem classic 90 plus and the furnace status indicator
i have a rheem classic 90 plus and the furnace status indicator is flashing 5 7. it looks like that means something needs to be done to the high pressure switch. Can anyone help me?… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Rheem Classic 90 Plus furnace that is 4 years old.
I have a Rheem Classic 90 Plus furnace that is 4 years old. it has 24V to the IFC but there are no LED lights on. When you tap the 24V relays the LED comes on and furnace will start for a few seconds … read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Rheem Classic 90 plus furnace/air not working this morning
Rheem Classic 90 plus furnace/air not working this morning - no heat. Thermostat seems ok (24vac at both red and white wire. After pushing in the filter interlock switch, on the control board the pwr … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I am in Colorado, 20 deg outside. Furnace is apparently not
I am in Colorado, 20 deg outside. Furnace is apparently not working. I have turned it off now, and before I call repair people, I want to check the filter. Can I just open the filter access door, and … read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
Good Evening, I have a Rheem Classic 90 Plus furnace that is
Good Evening, I have a Rheem Classic 90 Plus furnace that is 10 years old. It started shutting off today however will turn back on when turned off and then restarted. It will remain on for approximate… read more
Mario
Mario
Owner Of At Your Service Plumbing & Heat
High School or GED
672 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x